I bought an existing home with an oversized cast iron, non-condensate, non-modulating boiler. It was poor design as the boiler kicks on for less than 2 minutes before going off. This start stop is inefficient use of energy. The boiler managed to live 40+ years because it was cast iron, which is virtually indestructible. Oversizing a boiler was a typical mistake contractors made when installing heating systems. Now that I am staring at a $600+/month heating bill, I need to look at my options to make the system more efficient.
I found 3 options.
1. Safely reduce the output of my boiler by plugging orifices of the burners and readjust air flow accordingly. The net result is like having half the burners. I surmise that cast iron manifold will tolerate the temperature gradients. This solution poses the cheapest, quickest fix, but highest risk since nobody else seems to have tried it. I scoured the internet, and did not find a single engineering oriented discussion on the subject.
2. If I kept the same oversized boiler, I can increase the heat dissipation by Increasing the lengths of my existing finned baseboard emitters. After checking on the price of finned baseboards, and the cost of plumbing new baseboards to existing ones, I decided this is not something economically viable (baseboards and A/C contractors are not cheap)
3. Convert to a Weil McLain AquaBalance with a 10 to 1 turndown ratio.
Regardless of how big a boiler is, the max amount of heating is determined by the amount of radiant baseboard you have in your home It is easy to find out what heat dissipation you system has, as engineers has decided that a finned baseboard radiator can dissipate 600 BTU @ 180 F and 200 @ 120F). Just walk around your house, measure all the baseboard registers, add them up, and multiple the total length with those dissipation numbers. Assuming you are not going to add more baseboard or replace them all with low temperature baseboards, it is obvious that the boiler output should not exceed the maximum heat dissipation ability of your emitters. Anything bigger contributes only to constant start stopping. Something slightly smaller will actually be more efficient in a multi-zone house as not all zones will be “on" at all times. If you leave some rooms colder than others, those zones will be closed more often than zones where you want maximum warmth. Therefore a slightly UNDERSIZED boiler will be most energy efficient if you are replacing your existing boiler with a non modulating new boiler (cast iron or otherwise).
With a boiler that has some level of modulation (up to 5 to 1) , it is still wise NOT to oversize a boiler in order to get the maximum benefit of the modulation. I’ll give an example: If you doubled the size of a modulated boiler with a 5 to 1 turndown ratio, you will only be running at 2 or 3 at the coldest days. At best, you are left with only 2 levels to modulate. It will be ruining at Modulation Level 1 on an average cold day when it should be running at ¼ or less.
But, with the advent of Weil McLain’s AquaBalance that has a game changing turndown ratio of 10 to 1, you can OVERSIZE the modulating boiler by 25-30%. Why 25%? With the AquaBalance you can set the water set point to 135 F instead of a normal 145 degrees. That way the boiler can run at 70% capacity even on the coldest days. The lower temperature will lengthen the life of the boiler since the boiler is subjected to less heat. The other factor which increases the life span of the boiler is that it can run with less start-stop to fulfill the maximum heating demand. Since you are modulating at Level 7 (out of 10), you have 6 levels left on milder days. On each of the 6 levels, the system is working the heat exchanger less hard than on a perfectly sized system. With 6 levels left, this system is MORE EFFICIENT than a perfectly sized modulating boiler that only has 5 levels of turndown. Assume you have 6 Zones, and only 1 Zone is open. The AquaBalance can run at 10% (Level 1). Ideally, the pumps will run more and burners will cycle less. Depending on how well insulated or air tight your house is, you can adjust the OTR (Outdoor Temperature Reset), to further tune the system.
With a lower water temperature set point, the return water can be closer to the ideal 110 degrees or lower for maximum energy efficiency.
But what if you messed up on the heat requirements of your home and the boiler is too small? All a DIY homeowner has to do is to crank up water temperature set point in small increments until a comfortable level is reached.