Main vent recommendation?
My main is 65 ft long and about 1.5 cf volume. I have a single Gorton #2 on it now. Is adding another #2 worthwhile?
Homeowner in Middletown, PA
1936 house with 1996 Burnham V74 oil-fired 1-pipe system
What is the problem as to ask ?
I ran two tests with the header already hot. Open 1/2" bushing saw steam in 2 minutes. With the #2 it was more like 3:30.
Last runout is slow to heat up.
What's on that runout? What vent on the rad? Riser to second floor?
Add the second #2. This will get steam to that last riser much more quickly.
Consulting0 -
There are 2 radiators, both have varivalves on middle setting. The second floor rad is slowest (and farthest from boiler). Every other runout is in the first half of the main, this one is the end of the line, just before the main vent.
Obviously you can try slowing down some of the quicker radiators to help the balance. Adding the second #2 may help a bit as well. I would raise the main vents up on a nipple and antler. Looks like you have plenty of room.
What @dabrakeman said. You can also try a riser vent at the top of that runout and insulate as much of it as you can.
I'm adding an antler tonight. I have the Gorton #1 that was on the main when I moved in, so I'll add that first and see if it helps. And then tune the Varivalves I have all over the house. I'm planning to replace them all, but it's a pricy proposition and this #1 is free to me!
Those street elbows don't have full-size 1/2" passageways. This can slow the venting rate. I'd change them to regular elbows and short nipples.
Consulting2 -
Be aware that the varivalves do not shut completely. At the minimum setting they are equavalent to a #4. See the chart.
Dang it. I thought I was being smart getting fewer fittings.
i woudn't sweat it
If I put a gauge on the end of this antler, and compare to gauge in boiler will I get an accurate measure of pressure drop in the main? After the vents have closed of course. There isn't some strange pressure zone in there, right? I can't see why there would, but I've been humbled by steam before.
Once the vents close, the pressure will be the same as the boiler pressure (assuming the rad vents are closed too). You may get a peek at the pressure drop in the interval between when the main vents close and the rad vents close. You can look it up. Jake Myron's book has that info.
You aren't likely to ever see any pressure difference between the boiler and the end of the main, not in a house anyway.
See my sight glass boiler videos: https://bit.ly/3sZW1el1