Main vent recommendation?

My main is 65 ft long and about 1.5 cf volume. I have a single Gorton #2 on it now. Is adding another #2 worthwhile?

Homeowner in Middletown, PA

1936 house with 1996 Burnham V74 oil-fired 1-pipe system

Comments

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,637

    Try running it with the vent removed. If the main heats much faster than with the single #2, then another addition may be indicated.

    ethicalpaul
  • dabrakeman
    dabrakeman Member Posts: 723
    edited January 20

    Make sure this test is run with the system well warmed up both times. Typically one Gorton #2 would be considered enough for that volume though.

    Long Beach Ed
  • Big Ed_4
    Big Ed_4 Member Posts: 3,122

    What is the problem as to ask ?

    There was an error rendering this rich post.

  • danmayer175
    danmayer175 Member Posts: 48

    I ran two tests with the header already hot. Open 1/2" bushing saw steam in 2 minutes. With the #2 it was more like 3:30.

    Homeowner in Middletown, PA

    1936 house with 1996 Burnham V74 oil-fired 1-pipe system

  • danmayer175
    danmayer175 Member Posts: 48

    Homeowner in Middletown, PA

    1936 house with 1996 Burnham V74 oil-fired 1-pipe system

  • delcrossv
    delcrossv Member Posts: 1,916

    What's on that runout? What vent on the rad? Riser to second floor?

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Steamhead
    Steamhead Member Posts: 17,619
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • danmayer175
    danmayer175 Member Posts: 48

    There are 2 radiators, both have varivalves on middle setting. The second floor rad is slowest (and farthest from boiler). Every other runout is in the first half of the main, this one is the end of the line, just before the main vent.

    Homeowner in Middletown, PA

    1936 house with 1996 Burnham V74 oil-fired 1-pipe system

  • dabrakeman
    dabrakeman Member Posts: 723

    Obviously you can try slowing down some of the quicker radiators to help the balance. Adding the second #2 may help a bit as well. I would raise the main vents up on a nipple and antler. Looks like you have plenty of room.

  • delcrossv
    delcrossv Member Posts: 1,916

    What @dabrakeman said. You can also try a riser vent at the top of that runout and insulate as much of it as you can.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • danmayer175
    danmayer175 Member Posts: 48
    edited January 21

    I'm adding an antler tonight. I have the Gorton #1 that was on the main when I moved in, so I'll add that first and see if it helps. And then tune the Varivalves I have all over the house. I'm planning to replace them all, but it's a pricy proposition and this #1 is free to me!

    Homeowner in Middletown, PA

    1936 house with 1996 Burnham V74 oil-fired 1-pipe system

  • danmayer175
    danmayer175 Member Posts: 48

    I added the antler and the #1 last night. I think it's about 30 seconds faster. The last radiator vents a little quieter and seems to be heating up faster.

    Homeowner in Middletown, PA

    1936 house with 1996 Burnham V74 oil-fired 1-pipe system

    Waher
  • Steamhead
    Steamhead Member Posts: 17,619

    Those street elbows don't have full-size 1/2" passageways. This can slow the venting rate. I'd change them to regular elbows and short nipples.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    delcrossvWaher
  • SteamingatMohawk
    SteamingatMohawk Member Posts: 1,040
    edited January 23

    Be aware that the varivalves do not shut completely. At the minimum setting they are equavalent to a #4. See the chart.

    https://www.heatinghelp.com/assets/documents/Vent-Valve-Comparison.pdf

  • dabrakeman
    dabrakeman Member Posts: 723

    If you replace the street 90 I would also give it a longer nipple to raise the whole thing a bit more…

    Waher
  • danmayer175
    danmayer175 Member Posts: 48

    Dang it. I thought I was being smart getting fewer fittings.

    Homeowner in Middletown, PA

    1936 house with 1996 Burnham V74 oil-fired 1-pipe system

  • ethicalpaul
    ethicalpaul Member Posts: 7,305

    i woudn't sweat it

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • danmayer175
    danmayer175 Member Posts: 48

    If I put a gauge on the end of this antler, and compare to gauge in boiler will I get an accurate measure of pressure drop in the main? After the vents have closed of course. There isn't some strange pressure zone in there, right? I can't see why there would, but I've been humbled by steam before.

    Homeowner in Middletown, PA

    1936 house with 1996 Burnham V74 oil-fired 1-pipe system

  • delcrossv
    delcrossv Member Posts: 1,916

    Once the vents close, the pressure will be the same as the boiler pressure (assuming the rad vents are closed too). You may get a peek at the pressure drop in the interval between when the main vents close and the rad vents close. You can look it up. Jake Myron's book has that info.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • ethicalpaul
    ethicalpaul Member Posts: 7,305

    You aren't likely to ever see any pressure difference between the boiler and the end of the main, not in a house anyway.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el