Need more consistent domestic hot water
I currently have a WM SGO-3 oil fired steamer with a tankless hot water coil, installed in 2007.
The coil is rated at 5GPM and is plumbed to a Honeywell mixing valve to regulate domestic hot to a max of 120F.
I have thermometers plumbed in line with the direct hot water out of the coil as well as the domestic hot feed to the home.
At this point, even with the boiler firing, it can’t maintain 120F from the direct out of the coil. I have dropped the flow rate from my shower to less than 2GPM, and it still has trouble maintaining temp.
Some years ago, I purchased a new tankless coil (same spec and mfg) for the boiler which is still sitting in a box, along with a new mixing valve, as the old one is seized internally.
Since I never mess with the boiler during the winter months, my thoughts were to replace the coil and rework the control setup for the domestic hot come springtime.
The existing coil could be covered in sludge or have internal mineral buildup preventing heat transfer, or could have been improperly installed by the knuckleheads that installed the boiler before I knew about steam (Thank you Dan Hollihan) so that would be the first thing to do.
I was considering adding a flow switch to the cold water input and an aquastat to the hot water output, wired in series. This would fire the boiler only when the flow was detected and the temp was below the setpoint. It would shutdown the boiler if either one was satisfied.
Does this make sense to anyone, or am I overthinking this?
«1
    ethicalpaul Member Posts: 7,755
    edited January 15
    Separate your domestic hot water from your heating system and let your boiler sleep during the summer.
    A boiler is a horrible way to make domestic hot water. I think someone about 100 years ago thought "hey I have all this heat, why not use it to heat my domestic hot water?" and then no one ever thought since then if it was a good idea.
    Buy an electric water heater (traditional or heat pump as you wish) and enjoy the simple life.
    An indirect tank would be better than a tankless, but the cost and complexity of that is something that only a plumber with a boat payment due could love. $$$ tank, $$$ fittings, circulators, and $$$ installation, $$$ running your boiler all summer to heat a few gallons of water per day.
    Larry Weingartenhot_rodGGrossbjohnhy
    EBEBRATT-Ed Member Posts: 18,209
    edited January 15
    Could be the mixing valve.
    That being said a tankless coil is only good for 2 people or so if you have more than that I would look at different options.
    I am not thrilled with an indirect tank on a steamer. The cost of the indirect and a bronze pump will cost $$$.
    If you change the mix valve and coil and are still dissatisfied I would look at a 40-50 gallon electric. You could use the tankless to preheat the electric when the boiler is on for heat.
    Unless gas is available.
    Also some are not aware of this but tankless coils only put out their rated capacity with 200 deg boiler water and you don't want to go that high
    What water temp are you running for DHW in the boiler.
    I see no purpose to your flow switch idea as the low limit and the flow switch would have to call for the boiler to run.
    What you could do if you had a spare tapping in the boiler and put an additional low limit control in that tapping set for a higher temp say 190. You could wire that control in series with the flow switch and the to the boiler.
    So when the flow switch calls it puts the new LL in the circuit to the boiler at a higher temp but only while the flow switch is calling.
    But we are beating a dead horse. I would go electric if the new tankless doesn't work.
  • Jon Held_2
    Jon Held_2 Member Posts: 26
    Thank you all for the thoughts and comments.
    I have NG available, it's just not plumbed to that side of the house. Not a big deal.
    I'm not liking the idea of a standard hot water heater, as I've been down that road in my old house and still reminded of the flood.
    I was looking into a Bradford-White on demand NG fired unit, but I have no experience with these types of devices. The specs look good along with the warrantee, and the cost isn't too terrible.
    Has anyone had real world experience with these units?
  • GGross
    GGross Member Posts: 1,556
    If you like the way your current tankless works you will like a standalone tankless. They need to be cleaned at least once a year, multiple times if your water is real bad. Still flow limited, and will give the same symptoms your current setup does when they start to scale up.
  • Jon Held_2
    Well, I maintain my boiler every fall, so periodic maintenance doesn't bother me. I'll have to read up on the maintenance procedures for the various units out there. B-W seems to be a decent unit. Are there better/more reliable units on the market?
    edited January 16
    Sounds great!! Can't maintain temp, requires lots of maintenance, low flow, and prone to scale! Who wouldn't want that?
    @Jon Held_2 I think your fear of standalone water heaters is being too heavily biased by one bad event. If you put one in you won't even have to think about it for 10 years, how is that not attractive?
    Larry WeingartenLRCCBJPC7060
  • GGross
    Look at the models that come with 15 year warranty, they are usually more expensive but generally have some way to mitigate scaling. I think BW has one and I know the AO smith family of brands released one. I don't know as much about the BW one, the AO model has a water tube heat exchanger like you might find in a condensing boiler which I like. If your current system does not have a recirc pump and you like how it works (when its working anyway!) then I would go for a model without a pump in it, one less part that can break.
    Sizing for 5 GPM will generally mean you need a 199,000 BTU/hr model (depends on groundwater temp, and desired supply temp), so you will need to take into account sizing the gas for this unit, don't undersize it.
    https://forthepro.bradfordwhite.com/our-products/usa-residential-tankless-gas/infiniti-k-series-tankless-condensing-gas-water-heater-indoor/
    https://www.americanwaterheater.com/residential/tankless/mthr-199x3/
  • GGross
    Paul I think you meant that directed elsewhere. I dislike tankless water heaters and am a tank fan 😁
    edited January 16
    Sorry about that, I apologize for the confusion. I did quote your post to reference the information that you listed there but I was talking to @Jon Held_2 (I edited the post just now to improve clarity)
  • Intplm.
    Intplm. Member Posts: 2,670
    From what you are saying, and asking, "Needing more consistent hot water" . It can help to know how many folks you would like the hot water to accommodate? Your current heating of hot water coil isn't doing what you want.
    I would size a stand alone water heater (Conventional, hybrid, condensing.) to help with the needs of your home.Sized to the amount of people using the hot water. At this point in time you do not have that. Steam boilers are great but are not always a good option when heating a domestic hot water coil.
    hot_rod Member Posts: 25,323
    the key to combi or tankless performance is jeeping the HX descaled. Using the service valves make this an easy task
    Its the quality and amount of water that leads to scaling and performance issues. Don’t blame that on the equipment
    Phosphate dosers are used in Europe to help eliminate some scaling problems. Various treatment options for hard water are available .
    delcrossv
    I don't blame the equipment, but I'd never buy equipment that required all that work and expense when there is other equipment that doesn't.
  • Jon Held_2
    Well, we are about to be empty nesters. Both kids have moved/about to move out, so it's just myself and my wife in about another month.
    Right now I'm just looking into options if the replacement parts I have in boxes don't work for our needs.
    There seems to be some blowback on NG tankless units in favor of a conventional tank, either electric or NG. Again, I have no experience with the tankless on-demand units. They look pretty good on paper to me.
    I suppose I'll have to wait and see when the weather breaks around here (Jersey) and the parts get replaced.
  • ChrisJ
    ChrisJ Member Posts: 16,838
    edited January 16
    Get a 50 gallon tank heater and put a pan under it piped to a drain or outside.
    The pan is required in many areas under code now anyway. That solves your concern and gets you the hot water you want.
    ethicalpaulPC7060
    one mans opinion. That’s the beauty of HH, real life experiences from a variety of posters.
  • Jon Held_2
    Are you saying that a standard tank system doesn't require maintenance? I'm reading that the new NG units require yearly cleanings as well. Is that incorrect?
    edited January 16
    I'm saying that millions of tank water heaters get installed and see zero maintenance their whole lives. Some of them get some maintenance like draining out some water, or replacing the anode, but there is no hard evidence that I've seen that it even affects the life.
    Please link to the reading about NG tank units needing yearly cleanings…I'm not sure what that means and I'm curious now.
  • ChrisJ
    I changed the anode rod in my previous heater once and that's all I ever did to it in 9 years and we use a ton of hot water.
    My current NG heater I've done absolutely nothing to so far, it's about 3 years old.
    I'm not a pro.
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,895
    Hi, Tank type heaters that are glass-lined want to have the anode changed every two to five years and the relief valve should be checked yearly. Flushing out sediment is nice, but usually not too important.
    Yours, Larry
    LRCCBJ
  • delcrossv
    delcrossv Member Posts: 2,183
    edited January 17
    Others comments aside, after going through 2 tanked water heaters in too short a time, one with the associated flood, I installed a Rheem branded (Rinnai) tankless heater. Has kept up with the water demands of 4 teenage girls plus the rest of us without issue. 4gpm for as long as you want it.
    Annual maintenance is overblown. A cheap pump, a 5 gallon bucket and some vinegar is all that's required. Do get the service valve kit. Makes it a snap.
    The only repair I've had to do was clean the proving electrodes once in 12 years.
    Install was straightforward, did it in half a day. I think getting the copper HX rather than the stainless one was a good call with our water.
    Happy camper, I'll never go back to a tank heater.
    I have never heard of anyone with a tankless water heater that was happy
    HVACNUT Member Posts: 6,851
    I've only seen one Bradford White tankless, and now it's a Navien. IDK the model but it had a self adjusting gas valve. It was 2 years old when I first saw it. This particular model was converted to LPG and kept getting a code for incorrect fuel. You could put it through a setup that took like 18 minutes of self checks and it would run. After a phone call with BW Tech Support to verify all was correct, the board was replaced under warranty. I can't remember the specifics, if anything else was replaced, but the issue continued. Spot on combustion numbers when it ran, but it still lockout on the fuel code again and again. BW recommended another board, so a Navi went in and all is good. Maybe it was just that one heater. IDK.
    Bradford White does however manufacture decent stand alone atmospheric water heaters. There's companies that make all sorts of things to alert you if theres a leak and can even automatically shut off the water supply. Technology is cool… if you don't count the beginning of my post.
    If the oil tank is buried or old, have you thought about converting the boiler to a gas power burner? What's hooked up to Nat gas now? What size is the meter?
  • delcrossv
    mattmia2 Member Posts: 13,436
    That sounds more like an issue with support not knowing how the product works or brining in an engineer when then needed it than an issue with technology or the product.(or having access to the engineer because they bought it from someone else and put their name on it.)
    hot_rod
  • ChrisJ
    My boss loves his tankless and has been using them for a long time.
    I think his current one is a Takagi from about 6 years ago.
    delcrossv
    The ones that keep a little tank of hot water are probably ok if you have a large enough gas supply or live somewhere with relatively warm municipal water.
  • ChrisJ
    He has a family of 5 and most of them love long hot showers and he's on a well.
    His water is good and cold in the winter like right now and he's never complained about not having plenty of hot water. I also think he runs it at 140F.
    This is the exact one he's using
    https://www.supplyhouse.com/Takagi-T-K4-IN-NG-TK-4-IN-Takagi-Tankless-Indoor-Water-Heater-Natural-Gas
    delcrossv
    edited January 17
    At 190,000 btu/hr that is also most of the capacity of a standard 250 ft^3/hr gas meter depending on how you design for pressure drop.
  • Larry Weingarten
    Yesterday I replaced the thermocouple on a 43 year old Paloma tankless that's acting as backup for a solar thermal system. I installed both originally. It's the first time this tankless has needed any out of the ordinary service. It's simple and durable. My point (if I have one) is that I have proof that tankless heaters don't have to be problematic. 😇
    Yours, Larry
    hot_rodmattmia2delcrossv
    I think Paloma entered US market in the early 1970’s
    That newfangled water heating technology will never workout!
    EdTheHeaterMandelcrossvLRCCBJ
  • ChrisJ
    I'm not sure what your point is. Either you run higher pressure or you get a bigger meter.
    The heater does the job it says it does. It takes what it takes.
    delcrossv
    Gas suppliers are usually more that happy to increase the potential for you to use more gas. Whether they have it or not.
    EdTheHeaterMan Member Posts: 10,745
    I am of the opinion that a tankless coil in a boiler (Water or Steam) is a bad idea.  The reason for the tankless coil was so that the coal boiler owner could get free hot water in the winter when they added "Indoor Plumbing". When the oil dealers started to convert those old boilers to Fuel Oil, the price of fuel oil may have been as little as 8 cents a gallon, and by heating the hot water with the oil burner, the oil dealer would sell more oil to the customer.
     Levitt installed the package oil fired boiler with a tankless coil because it was less expensive than using 2 different oil burning appliances for heat and hot water separately, and it took up less room.   The cost of oil had gone up to 25 cents a gallon by the time Levitt was building those homes.  The cost of operating those boilers was not a concern to the builder.  Saving space was.
    As time went on, the average homeowner would embrace the tankless coil as “the way it was done” for oil heaters and you would get a Gas Heater and a separate Gas Water Heater if you heated with Gas. .  If you don't have room to have 2 gas burning appliances connected to the chimney, and you wanted to switch from Oil to Gas, then boiler manufacturer offered at least one Gas fired boiler with a tankless coil for those customers.
     Now with the price of filling an oil tank creeping near $1000.00 It has become known that an indirect tank that is not vented to the outside, is more efficient than a boiler with a tankless coil.  The indirect and the other parts to get it to work may be more expensive, but it is lower cost in the long run when compared to an electric tank water heater.  And the fact that those water heaters seem to fail about every 10 years on average and the indirect tanks have limited lifetime warranties in some cases.  Yea the indirect lasts much longer.  And the burner that is making the hot water is much larger than the electric elements or gas burners in those other tanks, so the recovery rate is really really fast.
    So any high efficiency boiler + an indirect water heater = economical, efficient, constant, never run out, hot water for your home. You just need the correct size for your needs.
    Just an opinion of an old fart with an oil burner license.
    LRCCBJ
    that’s quite a convincing pitch, Larry! 😅
    Larry WeingartenEdTheHeaterMan
    They are more than happy to charge you enough to buy several conventional water heaters for it in many cases too. Changing a meter is like one conventional water heater but if they decide the service is too small then it is not likely to be cost effective. Plus adding larger piping in the house. That is my point, that many times it is very costly to be able to supply that load.
    how many people actually need a. 199k tankless?
    I lived with a 110 combi and a 133, plenty of dhw even when we’re were a 3 household.
    The learning curve with a tankless is you never run out of hot water at the designed flow rate.
    With a tank type you always run out at the designed capacity.
    delcrossv
    peoples HW needs very widely.
    What 1 person thinks is plenty of HW would be 20% of another persons needs.
    LRCCBJ
    The recovery rate isn't so great with a mod con because the indirect's coil is sized for 180 degree water from a conventional boiler and mod cons aren't really made to make 180 degree water. the can do it but not so well so if you're using a mod con you should make the indirect bigger.
  • Larry Weingarten
    Hi @hot_rod , I like to think of it as the plumbing training the people. Tank-type heaters with modest reheat capability teach us that back to back to back showers while washing the dishes will give somebody a cool/cold shower, so we adjust. A tankless unit, sized for multiple uses just delivers, more or less endless hot water. This is the plumbing training us that we can be wasteful. I see endless hot water as needed only in some commercial or industrial applications… It's sorta fun. I'm beginning to sound like one of those old guys, yep!
    Yours, Larry
    hot_rodIntplm.
