Hoffman 75 failing?
Chasing water loss on my mother-in-law's one pipe system. Two mains, one with big mouths and the other with a Hoffman 75. During a long cycle, the big mouths will close and stay closed but the Hoffman will Cycle open and closed throughout the cycle.
I suspect the element is going bad because the vent will not stay closed. Any suggestions as to what other Main vent has a similar capacity to a 75?
Kind of a bummer as the Hoffman is only a few years old.
Comments
-
Hoffman radiator vents do the same thing. It's normal. Look for leaks elsewhere, such as radiator valve packings.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Hello delcrossv,
I find different vents seem to have different characteristics depending on their design. The big mouth has a lot of thermal mass. If you like the big mouth's performance and you think the Hoffman is defective you can easily make an orifice to slow down the vent rate of the big mouth, since its exhaust port is threaded.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
-
@Steamhead Been around the whole building with a mirror. Fixed a couple of stems and non closing vents. If it's not the hoffman, I'm running out of suspects.
I do have a couple of flange connections with old looking stains. Hmm.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
How much water is it using?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
About 2" om the glass this week. I don't have it calibrated to gallons but somewhere between half a gallon and a gallon. Easy enough to calibrate that.
What concerning is this is new behavior. No steam coming out the chimney so we're good there.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
Hmmm. 🤔 That may be an issue. The boiler room is a lot cooler since I recaulked the HE. The 75 didn't use to cycle open and closed.
Note it's open a lot more than it's closed even at 8oz of pressure (a lot with this system)
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
If its open its either steam or air leaving or air coming back in.
0 -
Air and or vapor coming out.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
@delcrossv said "Note it's open a lot more than it's closed even at 8oz of pressure (a lot with this system)".
If the vent is operating normally, it should only open momentarily after steam first reaches it. In your case I'd replace it. We've seen a lot of Hoffman vents coming from Taiwan lately- I'd use a Gorton #1 which has the same capacity and is made in America.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
Gorton #1 should be arriving today.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
Hello delcrossv,
So far I like my Big Mouth, however I did three things to it before I installed it. Upon receiving it the 'O' ring was not seated in the groove correctly (it never would have sealed), you could see it through the inlet port so I took it apart and corrected it (I have the sockets that size). It has to roll into the grove to sit in there correctly, just pushing it in did not seem to work.
Also since the Big Mouth is orientated vertically (as compared to a regular radiator trap) I did not like the floppiness of the brass disk attached to the capsule, since it has to rub across the 'O' ring every time the valve closed. So I cut about a 3/16" length of maybe 5/8" silicone tubing and tucked it under the brass disk. The brass disk is much less floppy and is almost parallel to the 'O' ring now. I think I have a picture but the camera battery is dead.
Put a small bit of silicone grease on the 'O' ring of the cover.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
Every manufacturer has this happen once in a while. Gorton will make it good.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Dunno @Steamhead ,unless supplyhouse.com is getting seconds. This isn't the first OOB failure for me with Gortons from them.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
Hello delcrossv,
Here are the pictures. Basically an experiment, so far so good. The dime was just for size reference, it was not left inside. I never took a picture of the improperly seated 'O' ring, but that was why I took it apart in the first place.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
Even I have had 2 Gortons be failed on arrival and I've only ever bought 4. But supplyhouse will replace it no problem. It can happen to any manufacturer, but it does seem to happen to Gorton a lot, don't know why.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
-
+1 for supply house. Credited and I can just pitch the bad vent. 👍
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements