Hoffman 75 failing?
Chasing water loss on my mother-in-law's one pipe system. Two mains, one with big mouths and the other with a Hoffman 75. During a long cycle, the big mouths will close and stay closed but the Hoffman will Cycle open and closed throughout the cycle.
I suspect the element is going bad because the vent will not stay closed. Any suggestions as to what other Main vent has a similar capacity to a 75?
Kind of a bummer as the Hoffman is only a few years old.
Hoffman radiator vents do the same thing. It's normal. Look for leaks elsewhere, such as radiator valve packings.
Hello delcrossv,
I find different vents seem to have different characteristics depending on their design. The big mouth has a lot of thermal mass. If you like the big mouth's performance and you think the Hoffman is defective you can easily make an orifice to slow down the vent rate of the big mouth, since its exhaust port is threaded.
One Pipe System1 -
@Steamhead Been around the whole building with a mirror. Fixed a couple of stems and non closing vents. If it's not the hoffman, I'm running out of suspects.
I do have a couple of flange connections with old looking stains. Hmm.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
About 2" om the glass this week. I don't have it calibrated to gallons but somewhere between half a gallon and a gallon. Easy enough to calibrate that.
What concerning is this is new behavior. No steam coming out the chimney so we're good there.
Hmmm. 🤔 That may be an issue. The boiler room is a lot cooler since I recaulked the HE. The 75 didn't use to cycle open and closed.
Note it's open a lot more than it's closed even at 8oz of pressure (a lot with this system)
If its open its either steam or air leaving or air coming back in.
Air and or vapor coming out.
@delcrossv said "Note it's open a lot more than it's closed even at 8oz of pressure (a lot with this system)".
If the vent is operating normally, it should only open momentarily after steam first reaches it. In your case I'd replace it. We've seen a lot of Hoffman vents coming from Taiwan lately- I'd use a Gorton #1 which has the same capacity and is made in America.
2 -
Gorton #1 should be arriving today.
Hello delcrossv,
So far I like my Big Mouth, however I did three things to it before I installed it. Upon receiving it the 'O' ring was not seated in the groove correctly (it never would have sealed), you could see it through the inlet port so I took it apart and corrected it (I have the sockets that size). It has to roll into the grove to sit in there correctly, just pushing it in did not seem to work.
Also since the Big Mouth is orientated vertically (as compared to a regular radiator trap) I did not like the floppiness of the brass disk attached to the capsule, since it has to rub across the 'O' ring every time the valve closed. So I cut about a 3/16" length of maybe 5/8" silicone tubing and tucked it under the brass disk. The brass disk is much less floppy and is almost parallel to the 'O' ring now. I think I have a picture but the camera battery is dead.
Put a small bit of silicone grease on the 'O' ring of the cover.
One Pipe System2 -
Every manufacturer has this happen once in a while. Gorton will make it good.
Dunno @Steamhead ,unless supplyhouse.com is getting seconds. This isn't the first OOB failure for me with Gortons from them.
Hello delcrossv,
Here are the pictures. Basically an experiment, so far so good. The dime was just for size reference, it was not left inside. I never took a picture of the improperly seated 'O' ring, but that was why I took it apart in the first place.
One Pipe System2 -
Even I have had 2 Gortons be failed on arrival and I've only ever bought 4. But supplyhouse will replace it no problem. It can happen to any manufacturer, but it does seem to happen to Gorton a lot, don't know why.
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
+1 for supply house. Credited and I can just pitch the bad vent. 👍
Matched the drill size to the internal outlet on the 75. Drilled it at an upward angle so it doesn't drip.
And when the steam hits it, it closes and stays closed. Yay!
I like it ! Since the Big Mouth has a lot of venting capacity there is room for experimentation. Maybe more venting would benefit your system, however maybe not all the Big Mouth has to give, did you try it without the plug orifice ?
Oh, yeah, I think you mentioned you had two mains so maybe things are fairly well balanced with that orifice size.
I see pipe wrench type jaw marks, I used a 5/8 inch hex bit socket driver to install the male pipe thread part. A 5/8 inch hex key (Allen wrench) and a 5/8 inch box wrench would work too.
One Pipe System0 -
Yeah, 9pm and I forgot my Allen keys. 😉
The mains balanced with 3BMs on one main, and a 75 on the other, so i replicated that.
Stopped by today. Looks like all the condensate is making it back to the boiler.
New BM+orifice blows air vigorously, then a little steam, then stays closed for the whole cycle. 😁
I'll stop by tomorrow, but it looks like it's a wrap.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.1
