Good Protocol For Keeping Water Clean in Boiler
I have an oil fired boiler. I know it's a good idea to keep the water clean. Clean water is easier to boil. However, I also know it's bad to constantly fill your boiler with fresh oxygenated water. What is a good routine to keep the water clean in the boiler? Thank you in advance.
Comments
-
It's a bit of a catch-22
Normally you'd have to constantly be draining and replacing the muddy water, but that action itself creates more muddy water.
the solution is to use a boiler treatment product such as 8-Way to raise the pH of your boiler water to around 10. This will dramatically DRAMATICALLY reduce corrosion and creation of brown water. Use less than the product instructions recommend, like 1/4 of what they call for.
Then drain as little as possible as rarely as possible. You are posting in Strictly Steam so I am assuming this is a steam boiler. So you must also stay vigilant about any steam or liquid water leaks in your system. You should aim for a maximum of like 1 gallon of replacement water every month during the heating season.
Here is my video about this topic:
Finally I'm not sure about your statement that clean water is easier to boil. Is this just your belief or are there facts behind it?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
The best advice for residential boilers is to put in as little water as possible. Float type low water cutoffs do need to be blown down perhaps twice a month to once a week. Ideally, other than that, you add no water at all. That said, most systems do require a little makeup water now and then — perhaps a gallon a month.
There is something to be said for blowing down the boiler itself from the mud leg/bottom drains once a year, to get any accumulated goop out — but if you are not adding much water, there won't be all that much (though it may be remarkably hard!).
Some people advocate adding a small amount of buffer to drive the pH up into the alkaline range; others don't feel it is necessary.
That said on an initial install or if significant work has been done on piping, it is absolutely necessary to thoroughly skim the boiler to get rid of any oil. This is time consuming, but critical. It doesn't use much water, though.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
I heard about the dirty water part from a YouTuber. He runs a plumbing and HVAC business. He does the occasional informational video. I think his name was Tony (or Tommy) Pipes?? I've also heard that the heating process actually "burns away" the oxygen in the water. I actually read that on this message board. The wonderful thing about the internet is anyone can post and give info. The worst part of the internet is that anyone can post and give info :) Thank you for the replies.
2 -
You saw Mikey Pipes. He is not too bad but one strong disagreement I have with him is that he is constantly draining all the water out of boilers and replacing it. He sees muddy water as the enemy without understanding that he is creating that enemy.
I currently believe that the idea that you can remove the damage of fresh water in a boiler by boiling the water quickly after adding it, is a myth.
Of course you are going to boil all the new water in a boiler, it is a boiler. In fact I would say that almost all the new water added to a boiler is pretty much immediately boiled (think about an auto-feed—it activates when a boiler is getting a call for heat and so it gets boiled right away).
But regardless of when that fresh water is boiled, the oxygen within it is released into the boiler cavity and I think the damage is done. The evidence of this is shown by production of rusty water.
That's why for all of last year as described in the video above I pre-boiled all my replacement water or used distilled water (along with my increased pH level). The video is there for all to judge.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Yes! Mikey Pipes! I was a little uneasy with his advice on draining once a month to the point the low water shut off activates. He argues it cleans the water and you get a safety check all-in-one. What's the deal with Burnham steam boilers. I've seen people say they were trash on the message boards. Yet, I have also seen people say they were the best residential boilers?! Go figure. Do they make a great ones and crap ones depending on the model? Again… anyone can post anything. Hard to discern good from bad. Thank you for taking the time to reply.
1 -
I rather agree with @ethicalpaul here — we often do! — on his comments on oxygen in water: it does pretty well vanish on the first boil. Whether it is useful to preboil the water or not… well, he's fussier than I am!
I would completely disagree with the YouTube chap. Any chemical reactions — including corrosion — with the water will occur very quickly after addition — and then stop when the chemical environment has stabilised.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
-
Reddit can be good, but moderation is always a challenge everywhere on the internet. Here we are lucky to have Erin.
the Burnham Independence line seems to not be lasting as long as it once did decades ago and lots of people around here including me would be hesitant to install or recommend one today. I haven't seen a conclusive reason but my favorite theory is that they have changed the boiler castings perhaps to make them better at transferring heat in the name of increased efficiency, and their lifetime has been greatly shortened.
They also make what I think is called a "three-pass" design called the MegaSteam that is highly regarded (but is sold only as an oil-burning boiler). I have no direct experience with either product.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
I have a MegaSteam. Someone on the board told me it was the best. I was little confused when someone else told me Burnham were trash. He went on to imply some unscrupulous firms used them knowing they would crap out and need replacing sooner rather than later.
0 -
I think several knowledgable people on this forum would say that you are OK with your MegaSteam, congrats!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
My burnham crapped out after 16 years.. Im surrounded neighbors all who had boiler replacements within a year or two of mine - still have their boilers.. 2 weil mclains and one other brand im not sure..
row houses, all look the same, same edr, same piping.. same water, same radiator type and locations,,,
i can tell you this, none of them give 2 sh*ts about blow downs, water loss, maintenance, treatments, heatinghelp, one was at install repiped in copper and still going strong 20 years now…
so yeah I would say its a burnham problem.
one neighbor has a couple of valve's that have been hissing for years, i can only imagine the fresh water it must take on.. but yet it outlasted my independence, that one is 20 years old now , still hissing away every steam cycle and im worried about my 2 gallons used in a month
2 -
Adding in some questions here as it ties in to a situation I have. Appears I've finally located most if not all leaks in my one pipe system. Make up water has been reduced to very little (about a quart over 2 weeks of pretty cold weather here). So I'm in the situation where my boiler water is pretty dirty, likely from the make up water added in the past. Is there any option on getting the water cleaner without draining and flushing the system? Doesn't appear so, my plan once the heating season is over was to flush out the entire system including the inside of the boiler and return lines.
Would adding 8 Way be something done at the same time I replenish the system after flushing it down? BTW Peerless boiler replaced in late 2011.
1 -
The Mega Steam & Steam Max MAY be fine. It could be the best dam boiler ever made. It may last forever.
But after what Burnham has done to countless owners, the sheer quantity of their boilers that failed is awful.
But my biggest problem is that their CI HOT WATER boilers failed just as miserably.
That is why I don't trust ANYTHING Burnham.
And that is why I don't trust their "flue gas and water chlorides caused it" discussion.
Once you get burned why go back?
If you bought a car which turned into a lemon, would you buy another one with so many other choices?
And its not an installation issue. All these boilers were installed by many different contractors. We all know of various steam boilers that have failed and steam will fail sooner than water especially if neglected.
But many of the jobs I am talking about were hot water boilers in schools with regular maintenance and they didn't last. Some were leaking after 10-15 years.
2 -
Since this thread got reanimated, I will take this opportunity to share a video I made the other day about this topic. It shows my current practice to keep my boiler water clean and to minimize corrosion
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
To All, As I have stated before, The best way to maintain your boiler, is to follow the manufacturer's instructions. Do not put anything into the boiler water other that what the manufacturer tells you. Only clean the boiler water with the chemicals the manufacturer tells you to use and in the concentration they give. I remember an article by Ray Wohlfarth [I hope spelled it right] about how he was called to a job and was in "hot water" because a boiler that he had installed had started leaking. The boiler had a aluminum heat exchanger that did not allow higher PH of cast iron and fire tube boilers and the boiler it replaced had a cast iron heat exchanger that allowed a PH of 10. He discovered that persons maintaining it treated the new boiler the same way they did with the old unit.
0 -
Since I replaced the return piping below the witer line with copper, I'm just not seeing a lot of dirt and sediment in my boiler. I see a little when I drain it for the summer, but in the heating season I only add a little water. I never need to drain it. I haven't used my handy-dandy gauge glass blow-down valve in a couple of years.
Does dirty water make it harder to boil? I think sedimentation might impede heat transfer to some exteent, sending more heat up the flue, but I don't think it raises the boiling point. Dissolved solids (e.g. minerals) can elevate the boiling point, but not suspended particles or colloids if I remember my chemistry.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-242 -
Industrial & commercial sometimes treat water (both condensate & make up) before it goes into boiler.
0 -
When bought my apt building 5 years ago, one of the tenants was getting paid to completely drain and fill the boiler on a monthly basis (as per instructions from local plumbing co). It wasn't until a year or two later i found this forum and learned how bad that was.
All I do now is open up the lwco weekly during season. Water is crystal clear, never have used additives. Not bad for a 75 year old boiler. Consider myself extremely lucky.
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
2 -
it’s possible at that age the boiler has thicker castings than newer ones. You could be set for life
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements