New Boiler/Size & Pipework
Patrick1
Patrick1 Member Posts: 28
edited December 2024 in Gas Heating
Hello everyone,
i have to get a new boiler, current boiler (damaged) is an HTP Elite 301. It’s a 299 Btu i believe. Water tubed high efficiency.
It has to be replaced.
We are looking at a 199btu Bradford White and are unsure if its powerful enough since the old boiler is 300k.
House is almost 4000 sq *edit *(5300)foot 3 story Colonial Garrison with a basement.
The plumbing on the hot water boiler pipes are original early 1900’s. Has many cast iron radiators and a couple baseboards. People think it used to be a steam system. But i don’t know because all the radiators have been replaced or messed with so some i can tell are from steam systems some not and i dont know which ones are the originals.
Measuring out the radiators and baseboard i am calculating i need about 165k btu. 175k btu if i replace 2 short baseboards back to a cast iron radiator.
Many suggest Bosch, lochvar, Bradford, etc.
Many also suggest 2 smaller boilers instead of 1 big commerical size boiler etc.
Why was a 300k btu boiler installed in the first place and is that even needed?
Im looking at a firetube instead of a water tube. One tech advised a firetube high mass boiler… but the ones im looking at i assume are low mass boilers.
is there any benefit of using a firetube with a cast iron system instead of a water tube.
Will a firetube be inefficient?
Another issue i am wondering is the plumbing going to and from the boiler.
The current circulation pumps i wonder why they were installed this way.
is it okay to have the pumps before the pressure tank?
I know that the system is unbalanced because some radiators have alot more pressure then others when the system is hot.
I have also been trying to get all the air out of the system and proper psi.
When the system reaches temp the 15 psi rises to about 20 psi or more when the boiler was shutting off. Is that normal or okay?
There is 3 lines with isolation valves coming off the primary for the return.
hvac guy would like to install a loop with a circulation pump off the send to help add warm water into the boiler as to not shock it. That may be all. Mentioned about completing the primary but i don’t know what or if that would be altered.
A different hvac guy suggested something that sounded like cutting everything off at the primary and installing a new secondary loop, reinstalling feeder, adding a 2” header and adding a low temp sensor on the return to keep boiler water above 130 degrees.
«1
    hot_rod Member Posts: 27,329
    a boiler like that should be piped primary secondary. It looks like the used high head circs to overcome the pressure drop. The y strainer on old pipe systems should be checked yearly, use a separator instead on the new piping.
    Two boilers give you twice the turn down, so 20-1. Also redundancy.
    I would suggest a hydraulic sep in an old iron pipe system. Air, dirt, mag, and hydraulic separation would protect the boiler and pumps.
    GGross
  • Patrick1
    So what you are saying i have not a complete primary? Because there is a large primary that everything T off of but returns with its own run.
    I had no idea that was a Y screen.
    yes on the new installation we are talking about adding a new screen.
    So everyone wants to do Copper, i personally want iron because i dont like to mix metals for multiple reasons. But would copper be surly okay? Im mainly wondering about heat loss from a copper run.
    also that bottom pipe along the trap door is a return from other heaters, its hard to tell from the picture with the angle.
    here are piping options that are generally in the installation manual for high efficiency mod con boilers
    Patrick1
    EBEBRATT-Ed Member Posts: 20,085
    Copper is fine mixed with black pipe. No issues on a closed loop system.
    SuperTech
    Jamie Hall Member Posts: 27,237
    Ah… before you do anything, someone needs to do a heat loss calculation on the structure. Otherwise, you have — quite literally — no clue what size boiler to install.
    The old one may or may not be the right size. I may be much too big. It's unlikely it was too small…
    Then, and only then, can you start worrying about which boiler and how it might be piped.
    Patrick1
  • Patrick1
    not really to sure how to do a heat loss calculation.
    if I were a betting man I would guess a load of around 100- 120,000
    4000 sq ft x 25 btu/ sq ft 100,000 btu/hr
    So a 150,000 mod con boiler may be adequate
    Look at @RenovationWontEnd post in Radiant Heating, he just did a heatloss with a spread sheet
  • Patrick1
  • Patrick1
    The expansion tank is for 12 psi, the auto feeder may be broken so i have been manual feeding it when i need to. Which blocks off the air trap….I had to work on a couple radiators earlier this year and drain. So it seems to need around 15 psi to get the radiators on the top floor to bleed. On first call for heat the pressure gauge in return when the circulation runs drops to around 5-10 psi then as the system heats it slowly creeps its way up to around 15-18 psi. And the top floor radiator starts to get hot Then if i shut the boiler down it instantly spikes to around 20 psi or more.
    is this normal? Its been tricky because I don’t want to over pressurize any part in the system. I imagine there was just an airlock in there somewhere
    after the water gets up to higher temp the HTP was reducing the fire rate to keep the water maintained. I cant remember at what percent maybe around 70% and i want to say set point was 180 but water temp seemed to be struggling to get above 165 for supply like it was maxing out almost.
    If the 300k btu boiler still modulates down to a lower fire rate when reaching optimal temp wouldnt that be a good sign its the right size? Also the outdoor temp sensor was disconnected.
    1 of the installers recommended not installing the outdoor temp sensor that they are unreliable and not needed. Also stated i dont really have a primary or secondary and should have a primary configured. And that a low temp sensor on a return isnt needed.
    1 installer recommended installing an outdoor temp sensor and then installing a low temp sensor on the return to keep boiler water continuously circulating on a primary at no less then 130 degrees to boiler health? And that a secondary loop needs constructed to maintain that.
  • Patrick1
    i keep calculating anywhere from 50-75kbtu/h heat loss. Does that sound normal or is my math wrong? Thats not really taking into account the refrigerated third floor walls from the balloon frame.
    This is for a 3 story Colonial Garrison, uninsulated, gabled roof. With a basement 1/2 below grade
    What im not understanding is the concept of calculating heat loss. I have X amount of cast iron radiators that could potentially put out X amount of BTU. If i have 175btu or radiant heat wouldn’t i want at least 175k btu of power and a little extra?
    it is possible if there have been upgrades to the building that it has more radiator capacity than you need. That would be a good thing as you could run at a lower boiler temperature.
    You could calculate all the radiator output and match the boiler to that.
    Better to know the actual heat load as it stands today. A wild approx but 20- 25 btu/ sq ft is not unreasonable 5300x 25 btu is 132,500btu/hr. 1/2 the size of the current boiler
  • Patrick1
    yes there has been a couple radiators replaced with larger ones, replaced with fin tube, and possibly 1 added. But for the most part its the same. The house was built in 1913-1925. Everyone in this part of the city ran coal. Alot of people here still have the original coal boilers and use them!
    ill have to calculate the radiator output again but the last time i got 165k btu. And if i reinstall 2 more radiators on the 3rd floor to the original pipes that makes it over 175k btu total.
    I think that 150k btu boiler would be to small.
    On a setback it takes the 300k btu about 45 minutes to reach temperature from room temp water. And the radiator on the 3rd floor is the last to start warming up and then the whole system shuts down not heating the floor. The only control is the thermostat in the center of the house.
    A big difference between "thinking" and calculating :)
    175,000 divided by 5300 square feet is 33 btu/ sq ft. That is a pretty big number, unless some windows are missing?
    A few hours, to do a load calc, or send the house plan off to have a load calc done. Maybe have a heat and cooling load calc done, if AC an option.
    With a lot mass, in the radiators and the volume of water, setback might not be a good idea. It's like getting a long freight train up to speed.
    An outdoor reset control to modulate water supply temperature and keep water flow constantly is a much better control strategy. Put heat energy into the building at the rate it is loosing heat is ideal.
  • Patrick1
    when calculating btu output of cast iron radiators should i use the old standard of 240 BTU or the new standard of 130 for an old house old engineering
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    The standard of 240 BTU/square foot of radiation has not changed. Steam at 212F is a constant. So is the 240 value.
    There is no "NEW" standard.
  • Patrick1
    Oh okay i wasn't sure. the engineering standard from the american radiator company lists 240 btu. I thought that has since changed to 130 btu standard.
    This catalog is from 1937 but I imagine wasn’t much different from 1913-1925
    This is all a new area of study for me
  • Patrick1
    is it typical to oversize with a safety margin of for example 1.2?
  • Patrick1
  • GGross
    GGross Member Posts: 1,843
    Looks like that boiler has a built in low loss header and pump, so your boiler loop is all internal and then you direct pipe to the system, primary/secondary is built in by default.
  • Patrick1
  • Patrick1
    edited January 2025
    Got the new one put in
  • pedmec
    pedmec Member Posts: 1,306
    A boiler sitting on wood, a combustible material. That's all i'm going say. i know where i stand on this install.
  • Patrick1
    yeah im not excited about the wood blocks either. When things warm back up this year im going to mortar in blocks under it.
    On the BTUh per square foot EDR. There is no new standard. And it is incorrect to call the 240 BTUh per square foot at a surface temperature of 212 F a "standard". That's a real live experimentally determined constant. Not, perhaps, as well researched as, say, the acceleration due to gravity, but nonetheless a physical constant. You can't fight it — or change it.
    However. Note that it was determined at a surface temperature of 212 F in a space with a temperature of 72 F. Change either of those numbers and the output will change in an entirely predictable way. The change isn't quite linear, but close enough: output per square foot EDR, measured in BTUh is equal to 1.71 times the difference between the emitter temperature and the space temperature in degrees F, measured in BTUh.
    edited January 2025
    Why the crossover pipe above the boiler? Is there a pump inside the boiler and that is a primary loop attempt? Are there pumps in series?
    Check that Y strainer occasionally on iron pipe systems they tend to accumulate rust and sludge.
  • Patrick1
    edited January 2025
    the cross over pipe is a small loop that mixes with the return. I guess as opposed to a mixer valve or hydraulic mixer. There is no internal pump that i know. There is a new 3 speed pump on the supply. we left the 2 old circulator pumps on the return side alone for now.
    yes the strainer.
    also working out all the air.
    system seems to be heating very evenly. Im suspicious of my old psi guage on the return pipe because at 12 psi i was getting no pressure to the third floor, and at 15 barely. The psi guage was removed and there is a psi guage on the boiler i get good pressure at what seems to be 15 psi cold. The old guage was on the return and the new one is built in on the supply
  • Patrick1
    ….still trying to get rid of the sloshing sounds after it start getting hot. Been successfullinbleeding air out several times already….
  • pedmec
    What kind of heat exchanger is in that boiler? You should have put a ball valve in that bypass line. Depending on the pressure drop thru the boiler I think you might be short cycling that boiler. Or at minimum the boiler is going to remain at low fire. Due to the large mains of the heating system and no internal circulator there is no reason why your flow is going to go thru the highest restricted path, which is the heat exchanger.
  • Patrick1
    I dont understand:
    it is a firetube, kitirami stainless steel with copper fins.
    Is there more information i can provide? I am very new to boiler systems.
  • Patrick1
    at 140 degrees set the supply burns the hello out of my hand and the return is more ok to grab
    it’s a rather unusual piping. One pump on the supply, two on the return?
    Water will take the path of least resistance, I suspect you have a bit of bypass?.
    An air separator up on the supply piping would help a lot to scrub air,and noise away.
    The expansion tank to pump relationship is not ideal, and will make it tougher to get air out.
  • pedmec
    The path of least resistance would be between the 2 tee's. Although the tee's are not a directional flow fitting like a 90 it is still easier for the flow path to be between the two tee's than trying to flow thru the heat exchanger. A fire tube boiler offers less of a pressure drop than a water tube there is still some pressure drop. The question becomes how much bypasses the boiler compared to thru the boiler. By having a ball valve or something similar between the two tee's you would be able to have some sort of control over the flow. Your new circulator location is going to act as a boiler bypass due to its location in the system
    If you pay attention to the boiler and its is not getting proper flow the boiler will modulate downward to keep the the outlet temperature within parameters. you can check your temp rise to see if it is an issue.
  • Patrick1
    edited January 2025
    it all is seeming to heat up well, seems to run smoother with the supply pump set at a low speed instead of medium. There is definitely alot of debris in the water and air bubbles. I need to flush the system out but being so cold out right now is a bad idea to me.
    A device like this above the boiler would be a nice addition. It will grab air, and also small ferrous particles that the strainer cannot catch.
    I'm not sure you could get a valve in between the tees where the crossover is?
    The largem Taco zone pumps may be what is allowing this to work, with that unregulated bypass?
    Maybe Mr. Webstone is trying to tell you something?
    pecmsg Member Posts: 7,024
    The strainer should be pointed down.
    Patrick1
  • Patrick1
    hm. Well im going to figure out taking surface temperatures here and try to see how much of a difference is going on.
  • Patrick1
    but other then that the radiators seem to be heating up nice and keeping the house warm
  • Patrick1
    edited January 2025
    this is how i believe the bypass loop is operating.
  • Patrick1
    edited January 2025
    …looking around for tape to put on the copper, the IR thermometer dosent like to read surface temp off copper well but it definitely is hot from the boilers supply to the variable speed pump
    and the return from the T down seems to be the very last thing to really heat up but it does eventually get hotter
  • Patrick1
    Are you saying that it could just be grabbing off of the already hot supply like this?