Quite a few oddities on this 'build'. I'm bothered by the wiring too.
0 -
i'm not saying it might. i'm saying it will. How much is going to be the 64 million dollar question. This is something that will rear its ugly head as the weather gets colder and colder. Will it be a problem? I dont know. there are a lot of factors at play here. What looks like a good idea, a full size bypass, is really not.
Look at it this way. if you were traveling on a trip and the radiators were your vacation spot, would you go thru the tee branch or take the road thru the boiler to get to the radiator? Depending on how much is going thru the boiler your logic in the boiler is going to stay in a lower fire to keep the temp rise down due to the low flow thru the boiler. The PID programming is always monitoring incoming and discharge temperatures and trying to maintain a target temperature. Sure you might have real hot water coming out of the boiler but that could be due to the low flow. this is when you have to think in BTU's, not temperature. You need to get the BTU's out of the boiler.
0 -
oh, and you can spray paint an area of the pipe that you want to test black to make the infrared gun work
0 -
well it cant really go 2 different directions through the T it would not really be possible
0 -
probably a good portion of the flow is going across the bypass. Strap a thermistor type temperature probe on that bypass to see what it runs.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I can tell its not that hot in that location, or not as hot as the supply right below it anyways
0 -
that boiler has a pump and low loss header inside it. All that needs to be done is connect the two green pumps to the return, the other vertical line to the supply.
No extra pump, no cross over, no primary loop needed?
The manual has examples of the correct piping and the explanation of how the boilers “insides” work? This drawing from the manual is close to what you need. You don’t have a mix down zone, so just the two pumps that were there need to connect to the boiler.
How did the piping get so convoluted?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
no, i don’t think this model has a low loss header inside or pump. It’s a different model from that manual
0 -
if it is a wall mount model , that also shows a direct pipe in the manual
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yeah it is the 301 both mountable or floor
hm. Yeah. Im suspicious that some of the noise isn’t all particles or air but turbulence or cavitation forming
But its heating the house, good and fast? So it would have to be coming from the HX? I also have the variable speed pump on a low speed which i believe is slightly lower then the speed of the 2 taco pumps.
0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements