DIY Boiler Installation -- Peerless 63-03
  • JakeCK
    JakeCK Member Posts: 1,495
    For thermostats I recommend z-wave. But then you'll need a z-wave hub to connect it to the wifi network. But if you want 100% local control with no cloud than z-wave with something like home assistant is the answer.
    With all that said steam is a set it and forget it system. Set backs are discouraged, which limits a connected t-stats utility. If you want this just for monitoring thats about the only good use case.
  • mattmich
    mattmich Member Posts: 173
    » a #4 is not too fast , ever
    Weeell…
    I think my problem is that the boiler is sized right for the remaining radiation, but the main is now too big. It's a good eight minutes from the first downstairs radiator becoming warm to the last upstairs one coming to life.
    » Two #2 on one main is an awful lot of venting in a residence
    To my mind, so long as the main vents close when warm, they can't really be too big.
  • mattmich
    edited November 2024
    » With all that said steam is a set it and forget it system. Set backs are discouraged, which limits a connected t-stats utility.
    I came to that conclusion years ago also. Setback produced an awful lot of banging and ticking at oh dark thirty. The one thing I'm considering is going down 1 F over night — or half a degree, if that's a thing — just to time it so the heat is on when I get up. I love it on a cold morning when the bathroom radiator is hot, not least because my towel is on it :)
    » If you want this just for monitoring thats about the only good use case.
    Yeah… that. I'll look into z-wave, thanks. Maybe I'll stay primitive, though. We don't travel a lot in winter.
    mattmia2 Member Posts: 13,270
    Insulating the mains will help them heat faster too if they aren't currently. they have to get hot before the steam can progress past that point.
    ethicalpaul Member Posts: 7,720
    Why do you think the size of the main has something to do with how much faster one radiator heats than another one? If the upstairs is heating too slowly, gently increase the size of its vent.
    But NOTE: It doesn't really matter when the radiators get warm, what matters is how comfortable a room is. My upstairs radiators could stay cold all day and it would be warm enough up there most days due to heat going up there. Don't obsess on the radiator, obsess on the comfort of the room.
    Then why stop at 2? Why not 5? Or 10? 🙂 My point is not that it would every harm you (although you do amplify the chance of failure), my point is there is no sense in venting more than is needed.
    well it won’t help them heat much faster but it will help them hold heat longer between cycles
  • mattmich
    @ethicalpaul
    » Why do you think the size of the main has something to do with how much faster one radiator heats than another one?
    Because the main has to get hot all the way around before the upstairs bedroom radiator gets any steam. Like I said, it's 80 ft of main, and 60 ft betweent he first and the last radiator. That's a lot of iron to heat, with a relatively small boiler.
    I'm not worried about waiting an extra 8 minutes, I'm thinking of the 34 kW (equivalent; I don't really do BTU) input power that's running an extra eight minutes just to get the first temperature increase in that radiator. It takes a long time to get the main up to temperature and for the main vents to stop puffing.
    » what matters is how comfortable a room is.
    That is certainly correct and has been fine, but it hasn't been cold for any length of time yet. So I'm just watching and slowly modifying the venting — which appears to have been pretty well balanced already, though with ancient and painted-over vents — so that I'm ready to address any deficiencies when it gets really cold.
    Regarding insulating the main, which I plan to do shortly:
    » it won’t help them heat much faster but it will help them hold heat longer between cycles
    Any heat that doesn't radiate into the basement is heat I don't have to pump in to get the steam to transport.
    » Then why stop at 2? Why not 5? Or 10? 🙂
    Who says I'm stopping? 😎
    It's two because @Steamhead said so, and when we have a weekend with cold and steady days, I'm going to time it with two vents and then with one of them blocked — which is easy to do with the MoM. I really like those things. And obsessing over this stuff seems like a harmless hobby. Wait until the end of the heating period when I downfire to a 63-03L :)
    cheers -m
    But the main has to get hot all the way around before ANY radiator gets any steam (ideally)
    If the main is taking too long, more venting can surely be added, but I like to make sure that more venting is going to actually make it heat faster—it may not.
    Surely, but my point is if the pipes are cool, the pipes are cool, regardless of insulation they must be heated.
    Sounds good to me! But steamhead said two #2, and I see a #2 and a #1, I wonder if there would even be any time difference with the #1 (D) blocked.
    You can probably downsize to a 63-03L in the dead of winter and do fine with all the extra pickup factor.
    Carry on!
  • mattmich
    » But the main has to get hot all the way around before ANY radiator gets any steam (ideally)
    I agree with the "ideally" — the best way to run the system would be to heat the main first and then the radiators, all at once.
    But in my system, the first radiator in the loop takes steam almost ten minutes before the last one. It also gets hot long before the end of the main gets any wamrth. The system works well in practice, as the radiator closest to the thermostat is one of the last ones to get hot, so we're not shutting off prematurely. But the burner always runs at least 25 minutes. If we did this electrically, it'd be 15 kWh.
    I'm pretty sure, and I will time it when I get the chance, that with the main insulated and an outside temperature of zero degrees, the main will have much less time to cool between cycles, will therefore heat up much quicker, and the heating will be much more even from one radiator to the other.
    What I'm having trouble with in my head is how this affects efficiency.
    My thinking is that the boiler and the main always get to the same state during a heat cycle. That's kind of obvious, and it takes a lot of energy. And on a warm day, the radiators heat only a little ways across before the thermostat registers the increase in temperature and shuts off — or they heat more evenly, and much longer, if it's super cold outside. So on a cold day, a larger fraction of the energy used goes to the radiators, where we want it, rather than the system stuff in the basement, where it's a necessarcy load that does not heat the house well.
    If we assume all that heat in the basement drifts upstairs and heats the house, it makes no difference. If we assume that the basement heat is lost, then we have lousy efficiency when it's 50 F outside. It's probably somewhere in between, and I believe a steam system works most efficiently when it's really cold.
    "efficiency" is a difficult word. It has a specific meaning in terms of converting one form of energy to another, and it is used much more commonly in the way you describe above.
    I agree with you that in the shoulder seasons, a lot of fuel is burned to get the steam distribution system hot relative to the amount of fuel putting heat into our living rooms, compared with winter. Not much to do about that except put on a sweater or run your mini-split in heat mode when it's moderate out.
    This is an indication that some of your radiators have too much venting or your main doesn't have enough—they are "stealing" steam from the main.
    A friend of mine has a D vent on each of her radiators in her house (it came that way when she bought it). Her main vent is completely optional and doesn't even get hot during a call for heat sometimes. She is lucky, though, and has good balance and no complaints, so I haven't advised her to change anything.
    If your balance is also fine, or you can make it work with minimal adjustments, that is all to the good. But a good general starting point is for the main to be the easiest thing to fill with steam.
  • mattmich
    » they are "stealing" steam from the main.
    Exactly.
    » This is an indication that some of your radiators have too much venting
    Untrue because
    and that's what I got on all the downstairs radiators — not counting the ones I disconnected.
    That is why I want to go even slower, which will be technically challenging.
    » [..] radiators have too much venting or your main doesn't have enough
    Doubtful because my boiler can only make steam so fast, and the gas gets "eaten up" by turning back into liquid as it goes along the main. But I will test by plugging one of my two main vents to see if it even has an effect.
    » run your mini-split in heat mode when it's moderate out.
    Installing one of those is on the list, to make summers more pleasant. So far it's been OK with two window ACs but it's not great for sleeping when it's muggy.
    I will daresay that if you have #4 on a radiator, there is no way it is stealing from the main unless there is something very wrong somewhere.
    Such as your main vent is failed closed.
  • mattmich
    Learned Friends:
    So I'm a little mad. After calling Oswald Supply — who sold me the Peerless near-boiler piping kit, great job — and describing the flue reducer piece I've misplaced, down to emailing a picture of said part, they sent me the wrong stuff. Only took nine days to get here, whereas the piping kit, all eighty lbs of it, took two. Go figure.
    Y'all may remember that @EdTheHeaterMan graciously helped me out on page 1 of this thread, part number and everything.
    So this is what showed up today, instead — the 6" to 5" vent reducer. I already have one of those installed, thank you. So this stuff is going back.
    Time to get creative.
    I'll still try to get the piece from the manufacturer, but meanwhile, I figured I'd make my own.
    Are we not men? We are men.
    With a pair of tin snips, some clamps, a bench vise, and a leftover piece of five inch vent pipe, I made this:
    The height of the opening in the flue collector is 110 mm — who knew these guys were metric??? — and from the lone picture I took back in August, I counted pixels to get the height of the baffle piece.. which was 77 mm. Wanting a little safety margin, I aimed for 72 mm and mostly got it.
    Since I didn't get started on this until I got home from work, I violated a basic tenet of experimentation and changed more than one parameter:
    - I installed the flue reducer
    and
    - I blocked all radiator vents to concentrate the steam down the main.
    In prior tests, the fastest I'd gotten heat to the end of the main had been ten minutes.
    With the baffle installed, it was four minutes for warmth, and six minutes before the main got too hot to touch. At that time, the puffing noise from the main vents changed, so I'm guessing that's when the steam reached them.
    Another before/after "measurement":
    Since I don't have a thermometer for high temperatures, I used my hand and tried to rest it on the vent close to the chimney. I could maybe leave it on the pipe for five seconds before it got painfully hot.
    With the homemade baffle installed, I can now place my hand on the same spot indefinitely. Clearly, there's less heat going up the chimney, which is a good thing.
    I'm still planning to do more quantitative tests, but for now, I consider this progress.
    Also, I would consider it a favor it @ethicalpaul would measure the height of the original baffle. Per the Peerless parts list, it's the same height for the 63-03 and 63-03L models.
    cheers -m
    MikeAmann
    I can't access it from outside…it's deep inside there, right?
  • mattmich
    Nah, you can touch it by reaching in from below, where the temperature/blocked-vent safety sensor is.
    It's easy to reach but not easy to measure.
    I took part of my vent piping off then it's right there.
    No worries if you're not feeling it; I'm pretty confident I got the size right.
    If you're so inclined — it might be easy to get a size with a piece of manila folder held against the top of the baffle, and a pencil mark made at the bottom.
    cheers -m
    You don't want the stack temp too low or the vent won't draft well.
  • PRR
    PRR Member Posts: 224
    Does your browser have a 'status bar' at bottom? It may be optional. Mine shows Day/Date on mouseover, but also a Post# down in status bar.
  • mattmich
    I did a couple things this past Saturday.
    (i) I installed a ball valve at the lowest point of the wet return, so I can get the sludge out periodically without losing a lot of water. In order to do this I skimmed again — I keep store with a marker on the boiler, so I know I've done it EIGHT times by now, and I mean long sessions, several gallons gone.
    And of course this meant that I had to drain all the water from the system. It looks like the surging has finally stopped. So far, after every skimming session, it'd come back within three or four cycles. I'm starting to be a believer.
    And (ii) I did what I had threatened some days ago and plugged all the radiator vents to see how quickly I could fill the main. That part of the experiment was inconclusive, inasmuch as on Friday night, I got the far end of the main "warm" four minutes after the steam came up at the near end…. and "too hot to touch" two minutes later. That was after being off for a good 3 hours, and much faster than before I installed the baffle.
    But on Saturday, with the main vent removed for maximum venting, it took two minutes longer for the main to get warm. I attribute this to the fact that I kept the heat off much longer as I skimmed and then replaced the water and installed the new valve. By the time everything was done — and lunch was cooked — more than 5 hours had passed since the last cycle.
    I think I learned that my boiler is too small to require more than one Gorton #2; it can make steam a lot faster than the main vent can take, but it can't send it down the pipe fast enough.. and by the time "steam" gets to the vent, it shuts off anyway. The main vent needs to be sized to the boiler, not the main.
    The other thing I learned, by keeping the boiler running with the vents blocked, is that my system will never short cycle. I don't have a good gauge — where do I buy a 0-3 PSI gauge? Supplyhouse only sells 0-5 PSI — so I didn't measure, but with just a little pressure in the system, the old vents I had taped shut let just a little air out, and the heat sloooowly started coming up on a few radiators. The needle never moved on the 0-30 PSI gauge, of course, and the few times I cracked the skim valve a little, there was no oomf behind hit.
    I just ordered Maidomist #4s for the remaining radiators and might repeat the test once I have a better pressure gauge. But I'm convinced that my boiler will never short-cycle in routine operation.
    cheers -m
    Many of the low pressure gauges are calibrated in oz/in^2 rather than psi so that is what you need to look for on supplyhouse.com.
    the worst case for the main vents will be when the system has only been off for a few minutes and the mains are still hot when heating the main will be much less of a factor in ow fast the steam can progress. of course there is the question of how much this matters on a one pipe system. it could be more important on a vapor system.
    dabrakeman
  • delcrossv
    delcrossv Member Posts: 2,183
    This is the one I got from supplyhouse.
    https://www.supplyhouse.com/Winters-Instruments-PLP301-2-1-2-PLP-Steel-Low-Pressure-Gauge-1-4-Bottom-NPT-w-Brass-Internals-0-32WC
    0-18 Ounces. And it's on a JB-5 running a 4 flat.
  • Marc_18
    Marc_18 Member Posts: 16
    Are you serious? How about simply a piece of tape over the vent orifice?
    EdTheHeaterMan Member Posts: 10,677
    It appears that you have the oil burner operating now. That wasn't too hard was it? Did you have someone test the combustion numbers yet? I didn't look at your other posts yet today.
    OOPS. I got you confused with another poster. Seized123 Who is putting an oil boiler. Sorry
    Anyway, I have been following you also and are happy that you are up an running also. You never found that baffle in the mess of boxes and parts, so you made one. Good for you!
    I am completely serious. This way my wife can open and close the radiator easily whenever she wants.
    delcrossv
  • mattmich
    I hope everyone had a good Thanksgiving.
    After the festivities, I sat down to order some fiberglass pipe insulation for the newly installed piping and to replace the old insulation I'd removed.
    Searching threads on this site, I found products and some helpful hints. Prices are OK, too, but I am choking on the ~$100 shipping costs. Come again? $150 dollars worth of inert fiberglass, the same stuff I can buy for cheap at my local Home Depot, and it costs a hundred bucks to ship?
    I guess I'll order extra and measure three times instead of twice, but can someone please explain this to me?
    cheers -m
  • mattmich
    Been reading some more, and searching using google's "site:heatinghelp.com insulation+shipping" which told me that the issue is the parcels are "oversized" per UPS. So that's why shipping is so expensive. I guess I'll carefully go over it again tomorrow and then bite the bullet.
    it’s not the same stuff you can buy at Home Depot, it’s much better
  • mattmich
    I get that, Paul, but I meant in terms of risk, hazardous material, or whatever. I didn't think of size as a reason for high cost.
    That should have occurred to me, I guess, having shipped bicycle frames before. That gets spendy in a hurry, too, and it's not from weight.
  • bburd
    bburd Member Posts: 1,170
    Can you get it from a local plumbing and heating supply house and lug it home yourself?
    Bburd
    mattmia2delcrossv
  • pedmec
    pedmec Member Posts: 1,224
    Couple of questions
    1. Your local inspector allowed you to do the gas and water installation? without a plumbing or gas fitter license?
    2. How did you come to the conclusion that with your "vents plugged that you will never short cycle"? You have that backwards. if you cant get the air out you will increase system pressure build up. Air has mass and takes up space.
    I am just going to state one thing that i don't like. Other than that i think you did a good job of following following good near boiler piping. I think you have extreme patience. My issue is with the domestic water tie-in. that is the worse location to tie the cold water into. By tying that directly into the boiler you risk the chance of cracking that boiler by shocking the boiler with cold water. You should have tied it into the return. You open that valve with it running and you're gonna slam cold water directly at that connection to the cast iron. Goodbye boiler.
    clammy
    what lengths are you buying? it could be a whole lot cheaper to ship lengths under 8' or wherever the ups oversize surcharge kicks in.
  • mattmich
    » Can you get it from a local plumbing and heating supply house and lug it home yourself?
    Not likely. I went to a couple of them to get names of contractors and they were pretty hesitant to engage with a civilian on any level.
    » Your local inspector allowed you to do the gas and water installation? without a plumbing or gas fitter license?
    State law does that, as @ethicalpaul kindly dug up for me — see the last page of my earlier thread.
    » How did you come to the conclusion that with your "vents plugged that you will never short cycle"?
    I didn't. The vents were plugged but incompletely; three older radiators started taking steam during my test. My guess is a tiny bit of pressure caused air to leak out past the tape I'd used.
    Seeing how little venting it took to keep the boiler running at full song without cutting out on pressure, I concluded it would never short-cycle "during normal operation." Meaning on the coldest day of the year, bumping the thermostat up a few degrees, I'm convinced it still won't. It's the second-smallest unit Peerless makes.
    I did learn that even a little bit of pressure matters. If I plug one or three radiators with a toothpick shoved in the Maidomist #4 orifice, those radiators stay stone cold. If I plug all of them, steam somehow forces its way in. I have a low-pressure gauge on the way, so I'll be playing with it a little.
    » My issue is with the domestic water tie-in.
    I get that 'best practice' is to do it it differently, and I would have if I had known. But that location is labeled "Tank Supply" in the manufacturer's literature, so that's what I did, and I'm not worried enough to change it now. If I wind up piping and automatic feed, I'll redo the supply plumbing, which is an ancient mess. For now, it works fine, and water doesn't really get used up.
    » what lengths are you buying?
    Three-foot sections. Doesn't seem like that should cost $85 to ship, and slighly over $100 from a competitor. On the other hand, this whole adventure hasn't exactly been cheap — but it was certainly worthwhile if it lasts as long as I hope it will. So no worries here. I'll just measure extra carefully.
    cheers -m
  • mattmich
    It's been a little over a week since the last skimming, and slowly the surging returned.
    First the water level drops by an inch or so, then two …and today it was almost three inches gone mid-cycle.
    I skimmed off a nearly full Home Depot bucket full of water, and now we're back to a one inch drop, or about a gallon.
    I keep track of it; this was skimming #9. I would not have guessed it would take this long, or this many times.
    cheers -m
    I can’t remember, did you do the tsp/washing soda? That dramatically cuts the necessary skimming
    I’m helping a friend who is in your shoes. The problem is when it surges it vomits the oils into all the mains, then you skim whatever remains in the boiler, then it takes days for the oils to return
    Air will compress and allow some steam in especially in a large radiator even if the air can't get out.
    I looked up some fiberglass insulation I ordered about 5 years ago and the shipping was like 415 but it was 1.25' ips and smaller for hot water(and most of it is still sitting in the box which i feel defeats the purpose)
    Some supplyhouses will sell to me and others will not. i think it mainly has to do with if they have a tax license. just like contractors there are a lot of not so great supplyhouses and I suspect those are the ones that get annoyed that you even asked. it seems that johnstone supply has bought up most of the supplyhouses in michigan and they don't sell to the public.
    Did you keep it hot by cycling the burner to keep it just below boiling while you were skimming?
  • mattmich
    » when it surges it vomits the oils into all the mains, then you skim whatever remains in the boiler, then it takes days for the oils to return
    That is what I think, too. It certainly fits with the observation. It's rather like "changing" your transmission fluid with a drain-and-fill, except there is a small amount of something nasty that has be almost completely removed. So that's a lot of operations.
    It also means there is no fast way to do it, and replacing the boiler water doesn't help. Overall it's slowing down, though, and I'm happy with the performance. We've had 25 to 30 degrees pretty steady for a few days, and the system runs 35 minutes then shuts down for two hours or so. I hope to shorten the run time a bit by insulating the main.
    » I can’t remember, did you do the tsp/washing soda?
    I did. But that does nothing to wash out the piping, since the soda water is removed after skimming, per the manufacturer's instruction.
    » Did you keep it hot by cycling the burner to keep it just below boiling while you were skimming?
    I did not. For one thing it was plenty hot, for another, I learned in chemistry class that the hotter a liquid is, the more material dissolves in it. The oil will sit on top, whether the water is hot or cold.
    The soda, on the other hand, will bind the oil and suspend it in the liquid, which is why there is a full water exchange afterward.
    Once the surging is completely gone, I'll think about treating the water and controlling the pH.
    cheers -m
    this video is long but it might indicate that the Squick product might help you
    I would never recommend it to the exclusion of skimming but it could definitely help in an annoying situation like you are facing
    The oils are more fluid when they are hot and will bond less to the metal when they are hot. They won't dissolve in the water without detergent so making the water hotter doesn't change how much dissolves in the water but it does help the oil flow out more easily and makes it bond less to the cast ion. Also the solubility of some things increases with temp, it decreases with others and i don't know the chemistry of why, but the minerals in the water tend to precipitate in water heaters and boilers when you heat the water.
    delcrossv