  • mattmich
    mattmich Member Posts: 91

    The guy I'm dealing with has a good way of communicating. When I told him the same thing — reducer shipped with the boiler; manual says it's OK — he accepted it and in a nice way told me he needed to verify it. So I did a cut-and-paste from the PDF:

    and got the response

    » That works (RE vent), thanks.

    Similarly, with the union inside the cabinet,

    » The union thingy is based on the understanding that it is among the most common leak points and being with in the cabinet makes it more likely that a leak could build up and being in proximity to the burners...

    Which is a great way to say, I can't force you to move the union, but you'd be an idiot not to — without actually using those words.

    That leaves the hard-piped water feed as the remaining issue. Whatever the verdict is, I'll deal with it.

    I'm just kinda all piped out and my day job s ramping up pretty good, so I hope I'll get a pass on that. It's not like we're going to Florida for a month.

    cheers -m

    ethicalpaul
  • ChrisJ
    ChrisJ Member Posts: 16,156

    It is kinda funny.

    To put a 6" even though a 5" is apparently big enough.

    Did they have any kind of notes about wanting a chimney of a minimum height to use the 5" ?

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ethicalpaul
    ethicalpaul Member Posts: 6,130

    No, they don't get specific like that. They just say basically "must be adequate to do the job":

    Chimney/Vent Operation: The vent system must be sized and installed to provide the draft needed to remove all combustion products.

    I'm glad it came with that reducer since that was the size of my SS liner 😂

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    mattmich
  • ChrisJ
    ChrisJ Member Posts: 16,156

    Yeah,

    But liners are sized based on the what the manufacturer of the liner says it can do at a given height, I believe.

    So a 5" in a 30' chimney isn't the same as a 5" in a 10' chimney.

    The code about not being allowed to reduce the appliance's connector is strange based on that, if what I said is correct. @Bob Harper

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • mattmia2
    mattmia2 Member Posts: 10,458

    The code is trying to summarize complicated engineering in to something that usually works.

    I suspect the reducer is just so they don't have to make a different collector box for smaller boilers with that number of sections. Maybe they should put a sticker on the boiler.

    Sometimes the code tables will tell you that you need to increase the vent after it leaves the appliance.

    Boilers running glycol are frequently filled with a pump cart and have no source of automatic fill. sometimes they are installed with a feed pump or a pressurized tank and prv but they don't have to be so I don't think you need an automatic source of makeup water.

  • mattmich
    mattmich Member Posts: 91

    One step at a time…

    ethicalpaul
  • Steamhead
    Steamhead Member Posts: 17,245

    Teflon tape on gas? Do your inspectors allow that? Ours don't……………..

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mattmich
    mattmich Member Posts: 91

    That's what it says on the Teflon tape container.. beyond that I dunno. There's plenty of tape on the prior version, and the inspector didn't comment on that.

    Of course, I don't know this stuff, which is why I posted this image earlier, inviting comment. And the comment I got was, correctly, that I shouldn't have the union inside the cabinet.
    Time will tell.

  • mattmia2
    mattmia2 Member Posts: 10,458

    I don't see anything in the fuel gas section 2015 michigan residential code that prohibits teflon tape or even that requires dope or tape, the only mention is that is says the dope has to be compatible with the gas.

    Make sure you don't wrap the tape all the way to the end of the threads, leave 2 or 3 threads exposed so it doesn't get inside the pipe when using it with gas (or fuel oil). Not sure if we mentioned that or not.

    ethicalpaul
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 8,771

    I'd be surprised if the local plumbing inspector has a clue about steam boilers. The job you did looks GREAT. If your inspector has any questions about the way it is piped, pleas ask them nicely, to site the code violation from his code book including the exact section chapter and verse of the code that they are using to fail the inspection. Post that info here so we can help resolve the issue.

    I love it when inspectors make mistakes that you can question them on. As long as you ask nicely for the reason, you may get the approval because they really don't know and don't want to look thing up. I remember a plumbing code official that told me that I can't install a gas pipe because I needed a state plumbing license. He sited an article that was on the first page of a journal to code inspectors that stated "All piping in the State of New Jersey MUST be installed by a licensed plumber. The following types of piping are excluded from this code: and it went on to list about 4 different piping systems like Hydronic Heating Systems, Fuel piping, Oxygen piping systems, Etc. and the article ended on page one of the journal with the line "continued on page 23."

    So I asked the inspector for page 23, so I could read the full article. It turns out there were over 30 other piping systems that were excluded from the "ALL PIPING" and you will never guess what was one of the "Exceptions". That's right NATURAL GAS AND LP GAS. You know what his reply was to that? "Well I guess I'll let you go this time."

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ethicalpaulCLamb
  • mattmich
    mattmich Member Posts: 91

    I'd be surprised if I had to play games with this gentleman. When I talked to him in the summer he said a couple things that made me ask if he'd read the Holohan book, and lo and behold, he had.. and went on to say, "if you've read Lost Art book, I don't think you'll have a problem."

    We've been doing the picture thing back and forth, and he's fine with the re-done gas plumbing, he's OK'd the 5" inch vent, and he strongly suggested I'd hard pipe the water supply, which I did yesterday. Not my best work, to put it mildly, and it took a few tries to get it all leak tight. It's all in a straight line so I can take it out trivially with the unions on the backflow preventer; if I ever go the automatic-water-feed route, I'll start further upstream and redo everything in copper. There are some ancient galvanized pipes that I just didn't feel like dealing with, esp since they don't feed anything else.

    I hate hate hate soldering valves and the like where some of the parts just can't get arbitrarily hot. Regular copper doesn't bother me, except for working close to the framing. It'd be awkward to catch the house on fire.

    And by Thu morning it'll be a chilly 44 degrees (7 degrees socialist), so I guess that's when the heating season starts…

    cheers -m

    EdTheHeaterManethicalpaulmattmia2
  • mattmia2
    mattmia2 Member Posts: 10,458

    even very old galvanized pipe, especially cold water where it corrodes much more slowly, usually comes apart and you can adapt to copper if you're careful to get a good 3 point grip on it with the wrench so you don't collapse it.

    I usually buy npt valves and use copper adapters so i'm only out an adapter if something goes awry.

  • ChrisJ
    ChrisJ Member Posts: 16,156

    The copper adapters I've used over the past 5 years, including male NPT have absolutely stunk.

    The thread quality is absolutely terrible.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • mattmich
    mattmich Member Posts: 91

    » I usually buy npt valves and use copper adapters so i'm only out an adapter if something goes awry.

    Yep. I did that for the ball valve after mangling an old one I had lying around. MUCH better to have the threads. The backflow preventer acts as a union, so that was easy.

    Apparently I have to add a pipe to the backflow preventer that's just like the pressure relief valve. My old BP didn't have anything like that.. but then not much else was done right in the installation.

    Regarding the old galvanized pipe; it's a remnant. From my water main, I've got 3/4" PVC, so all I have to do is replace the iron pipe with whatever I want. The only iron pipe left anywhere is inside the walls, going to the upstairs bathroom. That's on the list to replace also, but it'll be a job.

    cheers -m

  • mattmia2
    mattmia2 Member Posts: 10,458

    That is sort of the description of all modern threaded stuff, it seems especially brass. The last time I adapted to galvanized I used a brass nipple with wicking and dope(and probably tape) on the part that went in to the galvanized and then I think it went to an NPT valve from the brass nipple.

  • mattmich
    mattmich Member Posts: 91

    Progress report.

    We just had a wee stress test — went on a ten-day vacation with near-freezing night temperatures in the offing, so the heat was left on, with the thermostat set to 55 F.

    I have no idea how often the boiler actually ran — at a guess, around half a dozen times, or ten, or two. But there wasn't a drop of water missing per the sight glass, which is good.

    I started raising the thermostat a few degrees at a time, and there was serious surging going on. As in, a good 3 gallons going missing for 30 seconds or so, and then coming back into the glass. So I skimmed again, but in reality, over an hour or so, I emptied about half the boiler's water this way. That's not skimming, that's replacement.

    It's the 3rd or 4th time I've skimmed, and I'd like to know when I can expect this to stop. Every time I skim, the water level movement goes down to about a gallon peak-to-peak, but then it gets worse over time. I'd like to think that at some point this will stop, as all the oil has washed out. How much longer?

    Nothing much else to report. I still need to put in the dielectric union and the drip leg for the backflow preventer, which will never ever see water, but it's code.

    Overall, I'm relieved.

    cheers -m

  • delcrossv
    delcrossv Member Posts: 967

    Nicely done! How are you supplying water?

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • mattmich
    mattmich Member Posts: 91

    I plumbed in a manual feed line at the suggestion of the city inspector.
    It's got a shut-off valve + a gate valve in-line to regulate flow better.

    The one thing I don't like about the Peerless boilers is that the skim port is a good 1.5 gallons above the waterline, which adds a lot of unnecessary fresh, oxygen-rich water every time you skim.

  • ethicalpaul
    ethicalpaul Member Posts: 6,130
    edited 2:27AM

    So I skimmed again, but in reality, over an hour or so, I emptied about half the boiler's water this way. That's not skimming, that's replacement.

    no, that's skimming!

    Did you wash it out with TSP (or washing powder as peerless says) after you installed it, as the manual suggests (if I recall correctly). That really reduces the amount of skimming you have to do (since the tsp breaks down so much oil).

    I don't know if doing so now will help, but regardless, don't worry about fresh water at this point. Worry about it for the mid to long term, not now.

    I think the skim port location is good. If it was nearer the water line it would take that much longer because the upper part of the boiler would sort of hold oil on it that much longer.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    delcrossv
  • trivetman
    trivetman Member Posts: 188

    Mine was skimmed probably 5 (maybe 6?). times over the first couple months of operation. As the oil accumulated it surged so bad it created enough localized pressure to trigger the vaporstat and short cycled before it even got steaming.

    After that last skim….troublefree.

    Skimming It does add a fair bit of new water. I don’t think it’s avoidable. One time I did so much skimming I figured I might as well drain it after and get any sludge out as the water was all new anyways.

    delcrossv
  • mattmich
    mattmich Member Posts: 91

    Thanks, guys, that helps with context.

    No I did not use the 'washing soda' but I might. It's been a month, not a week, but the boiler has not run much since it's still warm during the day. Which makes the "more effective if the boiler operates 24 to 48 hours" a little problematic. It's basically, run once at four or five in the morning, and then again the next morning, or the next week.

    I'm learning that my house is better insulated than I thought, plus the brick veneer is thick and heavy and holds a ton of heat. I'm not complaining about that, except in the middle of summer.


    At the moment, I've got everything turned off since it'll be warm again today and I've opened the windows. When it gets cold I'll run it again and watch the sight glass. If it bounces more than an inch peak-to-peak, it gets the soda. No more Mr. Nice Guy.

    cheers -m

    ethicalpaul
  • ChrisJ
    ChrisJ Member Posts: 16,156

    I skimmed my boiler, I think 6 times before washing it out with a wand and skimming back in 2011-2012. Each time I think I removed something like 10 gallons.

    When will skimming be over? When you're finished.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    delcrossv
  • mattmia2
    mattmia2 Member Posts: 10,458

    The skim port has to be above where the sections connect together so that the oil can float on top of the water from each of the sections and out the port. Heat the boiler to just boiling after you fill it to that level to make the oil more fluid.

    Adding detergent and nearly flooding the boiler and and getting it to boiling then maybe completely flooding it and letting it sit for half an hour or so with detergent in it then draining and flushing is likely to still get rid of a lot of oil at this point but you will still have oil coming down from the system that you will have to remove after the system runs some more.

    The vent from the double check will squirt/dribble water out the vent if the pressure on the boiler side is ever higher than on the supply side like if you lose domestic water pressure with pressure on the boiler.

    Washing soda is sodium carbonate. TSP is trisodium phosphate. Washing soda is what is largely used in place of TSP where TSP is not allowed to be sold where consumers normally buy detergents. I would only do the detergent the first time and maybe after a couple weeks, I would just float the oil off out the skim port a couple times in between.

    As the system runs it is going to bring more of the oils on the new pipe and joint compound down in to the boiler with the condensate. If it was surging it will throw the oil from the boiler up in to the system with the water and the steam and condensate will have to bring that back down in to the boiler before you can remove it.

    I doubt the house got below 55 much with nights in the 30's and it is unlikely anything would have frozen.

    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 6,130

    That's all very well said, @mattmia2

    I used TSP (or TSP-substitute possibly, they are marketing them weirdly around here) just once and that removed almost all the oil.

    After that I skimmed a few more times just for good measure but I never had any surging after that first run (except when I did it on purpose later).

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el