Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Temp DHW Solution.. tell me if this is a stupid idea

Hi all. My oil-fired boiler has died and I'm looking at probably a month before I can have a replacement in and running.

I currently have an indirect hot water tank that is usually heated by the boiler. Without boiler, I have no hot water to heat the indirect.

Here is my potentially stupid idea. As a temporary solution, could I disconnect the indirect coil connections and plumb them to a small electric "point of use" water heater, with an inline circulation pump to heat the water through the coils, and theoretically heat the water in the indirect tank? I realize recycle time would be terrible, but once up to temp, I should have a 40 gal buffer. I also realize this would be creating a closed loop system, which isn't the intended usage for these heaters and I'd have to get the air out of the loop somehow.

Dumb idea? Thanks.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,556

    Not really, and recovery times may not be as bad as you might think. Not a setting for a long time usage, but you aren't planning that. You can probably use the same aquastat on the indirect tank to trigger the circulation pump, which in turn will turn on the point of use heater. Select the circulation pump so that you get close to the maximum flow through the point of use heater; you may find that a somewhat too large pump with a globe valve in line to control the flow will allow you to fiddle with that to get the best results. The size of the point of use heater selected will determine the recovery time; for a whole lot of reasons I'd be inclined to go smaller — mostly because if this is to be electric it's going to be a lot easier to wire it in.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • mattmia2
    mattmia2 Member Posts: 10,754

    the electric water heater will be the limiting factor in the flow, the indirect will probably be 1" and the electric will be 3/4" or 1/2" depending on the model, i might be inclined to forget about trying to slow the flow down, you might eventually have flow erosion in the electric water heater but that won't be in a month. Use a circulator with a flow check and the controls on the water heater control it, the aquastat just turns the circulator on and off.

    a small office restroom tank type water heater might be the least expensive way to get the package vs a tankless, the wattage of the element, the ampacity of the feeder, and the load available in your panelboard is really the only important part here.

  • Ironman
    Ironman Member Posts: 7,514

    Why not just get a 40-50 gallon electric water heater and connect it directly to the potable lines?

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    ethicalpaulhot_rod
  • bladeofanduril
    bladeofanduril Member Posts: 2

    I considered it, but I'm looking for a relatively inexpensive temporary solution, rather than just switching over to electric DHW.

  • mattmia2
    mattmia2 Member Posts: 10,754

    you'll have to look closely at the cost of the circulator and the fittings to connect and be able to fill and purge and an expansion tank and a relief valve and a relay for the circulator if you need it to figure out which is the better option.

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,563

    Hi, I had a look at home despot and see less than $75 difference between a six gallon heater and a forty gallon unit. I like simple, and the bigger one certainly comes with 4500 watt elements. Input on point of use heaters is usually much less also 🫤
    Yours, Larry

    PC7060DCContrarianIronman
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,283

    Just get a regular tank type electric wh and tie it in. The size depends on how much HW you can live without. A 30 gallon would be enough to get by but you can usually get a 40 at the same price.

    The price of piping and circulators and it would probably cost more than a simple electric tank.

    IronmanLRCCBJethicalpaul
  • DCContrarian
    DCContrarian Member Posts: 628

    I suspect you'll find that using a full-size heater as a temporary solution is cheaper that what you're proposing, once you price all the bits and pieces. When the emergency is over you can sell it on Craigslist.

    Ironmanbladeofanduril
  • ethicalpaul
    ethicalpaul Member Posts: 6,433

    This is another reason why indirects are a bad idea—something so simple as hot water is dead if your boiler is out. And of course, why would anyone want to have to run a boiler all summer to heat a few gallons of water per day?

    Switch to a resistive electric heater, or if you want to take advantage of incentives and pay a lot less per hot gallon, get a heat pump water heater.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • hot_rod
    hot_rod Member Posts: 23,108

    you can still get solar tanks, basically an indirect with a 4500 element installed mid point in the tank. So you have a bit of DHW should the boiler fail.

    A typical electric tank, 4500w is around 15,000btu/hr. You indirect could be 50, 80, 100,000 btu/hr. So recovery will be faster, typically 15- 20 minutes to recover a properly installed indirect.

    Without knowing your fuel costs, operating costs are hard to predict. I pay around 13 cents per kWh, I think Jamie pays 30 cents or more?


    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ethicalpaul
    ethicalpaul Member Posts: 6,433

    Hot water is hard to save money with, and I say this as a heat pump water heater fan.

    Even a resistive water heater uses only like $600 per year. Any savings (if there are any) from an indirect are used up on all the extra piping, circulator, heat exchanger, special tank, and labor to install and maintain it. But now I'm repeating myself!

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • hot_rod
    hot_rod Member Posts: 23,108

    sounds like he already has an indirect, he is only looking for a temporary until the boiler is fixed.

    Buying a 40 gallon electric and use it to pre heat for the indirect, when the boiler is fixed. Don’t run the elements just let it warm incoming water to room temperature.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream