Baxi Luna 310Fi

CamoZeroDay
CamoZeroDay Member Posts: 3

Replaced my PCB last night and the unit was working, woke up this morning and it’s not kicking over. No error codes, but I don’t hear the gas pumping in and there’s no clicks for it to try and light.

When I restart the system all the lights come on and stay on for about a minute. When I turn the water on the water light turns green.

I’m so burnt out with this unit, it’s always something.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,600

    Much more likely to be a bad switch, problem connector, problem wire, bad ground than the board — particularly if you already replaced the board.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    CamoZeroDay
  • Yes, they can be extremely frustrating. Surprised that you could find a part as they no longer support that model. eBay?

    Baxi support is pretty good. Give them a call on Monday. Hopefully, you can shower at a friend’s.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    CamoZeroDayPC7060
  • Ironman
    Ironman Member Posts: 7,516

    It could be that it’s not sensing flow. Have you checked the inlet filter. When was the last time that the heat exchanger was cleaned?

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    CamoZeroDay
  • CamoZeroDay
    CamoZeroDay Member Posts: 3

    I actually found an almost new unit from a house that was being torn down, I have spares of everything now.

    I might just find a professional to install this second unit.

  • CamoZeroDay
    CamoZeroDay Member Posts: 3

    Not sure, I moved in here 3 years ago.

  • Not recommended. Buy one of their newer boilers or some other reliable brand. Save yourself a lot of grief.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    SuperTechIronman