Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

New Boiler Short-cycling on Pressure Cut-out

dgn
dgn Member Posts: 40

5 weeks ago had a broken Burnham IN-7 boiler (EDR: 542) replaced by a Burnham (U.S. Boiler Co.) SteamMax STMX175 (EDR: 450)

The radiators in the house have an EDR of 418 so it made sense to go with a less oversized replacement. The same Vaporstat and 0-3 psi pressure gauge for measuring ounces coming off a pigtail were transferred from the old to new boiler. The Vaporstat is set to cut-out at 8 oz. with a cut-in at 2 oz.

Once the boiler is hot it starts short-cycling just about every minute. The 1-3 psi gauge shows an increase of pressure to 8 oz. at which point the vaporstat shuts down the boiler. The pressure goes down quickly, boiler starts up again, and after a minute the pressure is back to 8 oz. and the short cycles start again and again.

There are essentially 3 mains all of which get hot yet the radiators coming off 2 of them stay cold. 

Near boiler piping is pretty much the same as the old. Even though there’s a bull nose T pretty much all rads heated well previously.

One new difference is that there is a new condensate pipe coming off the header which seems to drain back to a wet return.

The new auto water feed also goes to the same wet return whereas the previous boiler’s auto water feed went right into the boiler.

The plumber - who was chosen for his supposed experience with steam heat - is coming tomorrow for a follow-up skimming. I told him that the short-cycling needs attention. He said it “could be the water”. This seems like an odd response given that it doesn’t seem to fit typical reasons for short-cycling. Could more skimming really fix this?

For comparison I've added some old boiler photos along with the new.
Any clues to pass along to the plumber are most welcome. Thanks!

new boiler - take off and bull nose tee

new boiler - header condensate to wet return

new boiler - header condensate and auto water feed to wet return

new boiler - vaporstat and 0-3 psi gauge

new boiler - header, equalizer, condensate return

new boiler - hartford loop

old boiler - header and equalizer

old boiler - near boiler piping

old boiler - risers to same side of header

«1

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,433

    The radiators in the house have an EDR of 418 so it made sense to go with a less oversized replacement.

    But still oversized. But based on your description it could be triggering the vaporstat due to surging/carryover because of oil on the water (from the new piping and boiler). Did he skim it at all yet? Skimming a new install take a couple/few sessions especially if he didn't put in some washing powder and let that boil for awhile, then skim and drain.

    The near boiler piping is confusing to me, perhaps he is trying to help a counterflow situation near the boiler, not sure.

    But one thing I see that is not great is the horizontal nipple at the hartford loop is supposed to be a short nipple or even a wye and he has about an 8" one there it appears.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    IronmanLong Beach Ed
  • Ironman
    Ironman Member Posts: 7,514

    Is this a one or two pipe system?

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • dgn
    dgn Member Posts: 40

    Yes, still a bit oversized but the next size down is too small.

    Unfortunately I had to be out of town during the installation. I would have watched it had I been home. I'm assuming it was skimmed on install and will ask tomorrow when they come for what I expect to be a second skimming. So are you suggesting more oil and residue in the system could be part of the cause of the short cycling?

    Also, what do you see as the downside to that horizontal nipple at the hartford loop?

  • ethicalpaul
    ethicalpaul Member Posts: 6,433
    edited October 28

    Yes, still a bit oversized but the next size down is too small.

    Not in my opinion. I'd greatly prefer 388 vs 450 for a 418 EDR (30 under vs 32 over). For those following along at home, all these ratings are boosted by 33% to make up for pipe losses, which is dramatically too much for those losses. But anyway, that ship has sailed.

    For the hartford loop nipple, I believe it can cause hammer. And I was wrong about the length, it's a lot longer than that, I didn't notice the part before the elbow…it's gotta be 18"-24". This issue might not manifest as any problem, but it's good to be aware of it.

    Here is an answer

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,283

    Have him check the burner specs and see if the firing rate can be reduced slightly. It is possible he did not skim the boiler or skim it enough. He also needs to find out why some rads do not heat that is exacerbating the short cycling. If the water line is surging while skimming that is a clue that it needs skimming.

    Water surging and getting into the mains could cause some rads not to heat.

    mattmia2ethicalpaulLRCCBJ
  • Ironman
    Ironman Member Posts: 7,514

    It appears that there’s definitely some piping errors.

    A close up pic of the sight glass would help to see if it needs skimming.

    Short cycling and faulty venting may be the cause of some rads not heating.

    The vaporstat setting of 2-8oz is more in the range of a two pipe vapor system. I’d make sure that the other issues are corrected first, but a one pipe system may need slightly higher pressure, but not above 2 psi.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Long Beach Ed
  • dgn
    dgn Member Posts: 40

    Curious if you have any thoughts on the new piping of the header condensate and auto water feed now going to the wet return?

  • Ironman
    Ironman Member Posts: 7,514

    This is proper near boiler piping. The optional drop header is preferred, but not required.

    IDK why there’s a drip off of the middle of the header unless it doesn’t have proper slope towards the equalizer.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 10,754
    edited October 28

    There is a random drip in the middle of the header, it shouldn't hurt anything I don't think but it is unnecessary. The old near boiler piping is wrong. The risers from the boiler should both connect to the header before the riser to the system then the equalizer should connect after that and it should have some pitch toward the equalizer. You should check the pipe sizes against the manual.

    If there is liquid water being thrown in to the mains from oil still on the water in the boiler or from the risers and header being undersized the water could be keeping part of the system from heating as @EBEBRATT-Ed said.

    and as you pointed out, each main should connect to the header separately.

  • dgn
    dgn Member Posts: 40

    @mattmia2 the 2 risers from the boiler do connect to the header on the same side as the riser to the system with the equalizer on the other side. It's just difficult to see in the old boiler photos due to the insulation. And yes, the mains should all be coming separately out of the header which is not the case. Luckily, in the old setup this wasn't a problem.

  • mattmia2
    mattmia2 Member Posts: 10,754

    I figured out what they are doing, it isn't correct but I know why they did it.

    There is a horizontal reducing ell between the header and the equalizer which will keep condensate from being able to drain from the header, the drip is to try to correct for that instead of just putting the reducing ell vertical on the equalizer connection.

    LRCCBJ
  • Ironman
    Ironman Member Posts: 7,514
    edited October 28

    I now see it in the picture. That’s a huge mistake as now the header would have to be pitched backwards to drain.

    I’d make them correct that properly and skim the boiler.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2LRCCBJ
  • ethicalpaul
    ethicalpaul Member Posts: 6,433

    The vaporstat setting of 2-8oz is more in the range of a two pipe vapor system. I’d make sure that the other issues are corrected first, but a one pipe system may need slightly higher pressure, but not above 2 psi.

    Respectfully, but definitely not. No one pipe system should need any more pressure than 1 oz/square inch (about 2 inches of water column). And even then, "need" is too strong a word.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 10,754

    But if the boiler is oversized it may need more differential to make the cycle length reasonable.

    ethicalpaulLRCCBJCLamb
  • ethicalpaul
    ethicalpaul Member Posts: 6,433
    edited October 28

    I define reasonable as "make fire when I need steam". I don't care if my atmospheric boiler cycles 100 times per day (it doesn't of course). I don't want it burning fuel for no reason, so I prefer it cycles on pressure rather than building pressure that doesn't help me.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 10,754

    That might be more efficient in a standing pilot boiler with no vent damper but the losses up the flue when the vent damper is open but the ignition is still working on starting a cycle and the post purge at the end of a cycle are going to eat up any miniscule gain you get by not building a small amount of pressure. Though a small amount of that energy is not transferred to the water because the water is a slightly higher temp, most of that energy is stored in the water and released as steam as the pressure is reduced as the system cools.

    LRCCBJethicalpaul
  • Jamie Hall
    Jamie Hall Member Posts: 24,558

    Whoa guys. First let me say that I agree with @Ironman on the pressure. There is a reason why one pipe systems tend to need higher pressures: the pressure drop through the vents on the radiators. However, that is not likely to be the reason for some radiators which did heat not heating — and whatever is causing that is also causing the too short run phase of the short cycling. (with that oversize on the boiler, I would expect a cycle on the order of 3 minutes on to 1 minute off; if the run phase is less than about three quarters of the total cycle length, there is a problem). Do the main and risers to those radiators get hot?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2ethicalpaul
  • LRCCBJ
    LRCCBJ Member Posts: 291

     There is a reason why one pipe systems tend to need higher pressures: the pressure drop through the vents on the radiators. 

    If this were the true situation, NO one pipe system could ever run below………say………..10 ounces. There is more than enough data on this site to prove that is not accurate. Several folks with drop headers run with pressure so low that a 3 oz. gauge is necessary just to read it accurately. The pressure drop though the vents is negligible.

    Furthermore, they can run FOREVER at this pressure and never get to a point of tripping a vaporstat. The radiation distributes ALL the energy that the boiler provides.

    delcrossvethicalpaul
  • Jamie Hall
    Jamie Hall Member Posts: 24,558

    I'm going to put this in two current threads on short cycling.

    And be blunt. It is impossible to design and build a system with a fixed firing rate at the boiler and a fixed load area which will reach full capacity of the load under all conditions, but no more (and thus, if modulated by cycling, never cycle).

    You can get close. Sometimes very close.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • LRCCBJ
    LRCCBJ Member Posts: 291

    And be blunt. It is impossible to design and build a system with a fixed firing rate at the boiler and a fixed load area which will reach full capacity of the load under all conditions, but no more (and thus, if modulated by cycling, never cycle).

    And to be blunt…………..at least five members of this forum…………other than myself…………have done exactly that.

    I tried to explain that the output of a system is variable depending on water content of the steam……….and those with very little water in the steam ALWAYS result in a boiler that is not capable of overfilling the distribution system UNDER ANY CONDITIONS……………and each of these systems were designed with a boiler that was proper for the EDR available.

    You are free to believe whatever………………….

  • Jamie Hall
    Jamie Hall Member Posts: 24,558

    OK. You have the following variables which affect the condensation rate of the system (the load): space air temperature. Space enclosure temperature. Space convection velocity. Internal pressure in radiation. There may be others I haven't thought of at the moment.

    You have the following variables which affect the power output of the boiler: fuel BTU content. Burner air flow. Intake combustion air temperature. Intake combustion air moisture content. Intake combustion air pressure. Exhaust draught. Steam pressure in the boiler. For starters.

    And given all those variables, you say it is possible to design a system which will always exactly match the load to the power output at all times? Really?

    Note that I am not saying that it's not possible to get a very close match in average conditions. Very close indeed sometimes, either by good luck or by careful design and careful adjustment, and I applaud those who take the time or are otherwise fortunate to do so. I'm one of them, though I don't think you counted me in the five. Nor am I saying that a two pipe system should cycle on pressure; most of the time, it shouldn't (a one pipe system may or may not need to cycle; if it has TRVs it must cycle to obtain control). But it is neither surprising nor indicative of poor design if, in some conditions, it does.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • LRCCBJ
    LRCCBJ Member Posts: 291

    First, let's get the FACTS down:

    In each of the cited cases, the designer utilized a boiler with a relatively small pickup factor…………15% to 25%…………..with a very carefully calculated EDR.

    In each of the cited cases the designer utilized a drop header with ample size to keep the steam velocity below 15 ft/sec.

    In each of the cited cases, the designer utilized two risers that extended at least 30" above the waterline.

    And, in each of the cited cases, the boiler NEVER developed anything close to 8 oz. of pressure no matter how long the boiler ran.

    So, we must conclude one of two things:

    1. Each of the cited cases had a designer that was erroneous in their EDR calculation
    2. The design of the drop header and risers resulted in very dry steam and the radiation had an output GREATER than the calculated EDR because of the dry steam.

    Clearly, there is no exact match to the radiation. The net output is LESS than what the radiators can condense even when run for an infinite time. It is not a requirement to precisely MATCH the radiation with the boiler output. What the evidence shows is that you can have a beautiful system when the boiler output is LOWER than what the radiation can deliver without compromising the capability to heat the building.

    Do realize that these boilers have fully insulated piping in the basement and around the NBP thereby further reducing the piping factor and potentially provide MORE energy to the radiators than would otherwise be calculated in the pickup factor.

    There is a fundamental fallacy in the generally accepted design of residential steam systems whereby one needs to fully fill every radiator in the building, and obtain the calculated output each time the boiler starts. You would be hard pressed to find a building where the heatloss is not significantly less than the the calculated EDR. Therefore, why install a boiler LARGER than what the radiation can deliver? The old standby of "you don't want to get caught short" given by all the clueless contractors really rings hollow when presented with the FACTS.

    Most steam boilers should be installed with not more than a 10% pickup factor together with a a generous drop header and 30" risers. That boiler WILL NOT CYCLE ON PRESSURE.

  • Jamie Hall
    Jamie Hall Member Posts: 24,558

    I give up. I'm just a knuckle dragging engineer and physicist.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    LRCCBJbburdmattmia2ScottSecor
  • delcrossv
    delcrossv Member Posts: 1,241

    Had a similar discussion with @The Steam Whisperer a couple of years ago, for different reasons.

    Modulating burner controlled by a pressure transducer and a PLC groups those variables into a nice, controllable package.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • LRCCBJ
    LRCCBJ Member Posts: 291

    He has made multiple arguments for running a system with NO pickup factor. Even the expected balancing problems on single pipe systems have not been an issue.

    Apparently some engineers simply cannot grasp what he has been saying.

  • trivetman
    trivetman Member Posts: 202

    Back to the OP’s question….I had similar short cycling behavior when my steammax was installed a couple years ago. It was localized pressure due to dirty water and surging. It took a number of skims to get it cleaned out and running properly. Hopefully your problem is as simple as that.

    ethicalpaul
  • Jamie Hall
    Jamie Hall Member Posts: 24,558
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    LRCCBJCLamb
  • dgn
    dgn Member Posts: 40

    @trivetman thanks for your story. I sure hope the skimming session today will help improve things. The previous Burnham Independence had been doing a fine (at least adequate) job of heating the house in spite of the non-optimal near boiler piping. Here in New England the temp is dropping so I need to get this sorted out soon.

  • dgn
    dgn Member Posts: 40
    edited October 29

    @Jamie Hall "…Do the main and risers to those radiators get hot?"

    Yes, the mains get hot but can't tell about the risers to the rads. This is a typical New England triple-decker so once the risers leave the basement it's all in the walls.

    One basic error is that there's only one pipe coming off the header which splits into 3 mains (see photos). The rads that come off of 2 of the 3 are cold where as the 3rd set of rads do get hot. Understandably the rads don't get got since the short-cycling is not allowing time for the steam to get to them.

    I don't think raising the vaporstat cut-out pressure of 8oz will do much besides add a few seconds to the length of the short cycling. Increasing pressure seems to go against everything I've read in Dan's "Lost Art" book and his lectures.
    BTW, I want to say I've appreciated the deep knowledge you've share in various posts through the years.

    GrallertIronman
  • trivetman
    trivetman Member Posts: 202

    do yourself a favor and pay attention to how he skims it so you can do it yourself. Assuming thats all the problem is, youve likely got a few skimming sessions to go before the problem stops repeating. Itll make your life a lot easier if you don’t have to call for service every time it pops up

  • dgn
    dgn Member Posts: 40

    Oh, I most definitely will watch. I typically watch and ask questions of any repair person. I've learned a lot through the years and have saved plenty of $$$ yet won't do jobs that are over my head and create even worse problems. This skimming session is included in the job so I wasn't going to pass it up. The question is, how much time do I put between this and subsequent skimmings that I do?

  • ChrisJ
    ChrisJ Member Posts: 16,234
    edited October 29
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    LRCCBJ
  • ChrisJ
    ChrisJ Member Posts: 16,234

    @dgn

    Thank you for the pictures of the boiler.

    Would it be possible to get some of various radiators including a few that work, and those that do not? I'd also like to see what vents are on them, if possible.

    Do you have main vents? If it's been mentioned already I apologize, I didn't see it.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Ironman
    Ironman Member Posts: 7,514

    Problems with individual rads is probably due to inoperative or incorrect vents on them.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • dgn
    dgn Member Posts: 40

    There are essentially 3 mains coming off the header. The issue has to do with ALL the rads coming off each of 2 of the mains, not individuals. None of the vents have been changed from the old to the new boiler.

  • dgn
    dgn Member Posts: 40

    Sorry, no rad photos at the moment. Only one of the mains has a vent.

    What I'm wondering that nobody on this thread has mentioned is the auto water feed and condensate line from the header going into a wet return rather than back into the boiler as in the old system. I don't recall ever seeing photos on HH showing this. Is this ok?

  • ethicalpaul
    ethicalpaul Member Posts: 6,433
    edited October 29

    Its fine. Topologically, the wet return is an extension of the bottom of the boiler, it's all the same container of water.

    Water feed into the wet return is even preferable because it can provide a way to flush that line (or part of it), and it warms the feedwater before it hits the boiler (not that it would harm a hot boiler anyway—as long as the boiler wasn't empty)

    I put my (manual) water feed right where the end of the main drops down to the wet return. (which is about 6 feet from my boiler due to the way my main wraps around my basement)

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    dgn
  • KC_Jones
    KC_Jones Member Posts: 5,804

    Since at least one of the mains not heating is one of the ones lacking vents, I'd say you have the problem in hand, just need to fix it. I would guess the main that is heating is the one with main vents, but I really don't know. Venting for balance really starts in the basement with getting the main venting sorted. On a warm start it should take less than 5 minutes to fully heat all the mains and then the radiators should start heating.

    As far as the water feed, that's actually the preferred location by many. Putting it into the wet return allows it to mix with some of the warm condensate so the temperature difference from fresh water to the hot boiling water is less. That said, I don't think it matters too much either way.

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • mattmia2
    mattmia2 Member Posts: 10,754

    Each main needs to be vented somehow. My first thought was that it was water being thrown in to some of the mains by surging but it could be just lack of venting. What happens at the end of the mains?

    How much does the water line move while it is steaming? Is it bouncing?

    ethicalpaul