Navien NCB-240/130H and Nest Thermostat Issue
I have a three zone system. Zone 1 with 4th Gen Nest Learning thermostat works fine. Other two zones have Nest Thermostat cconnected. As soon as I add thermostat to base, heat turns on and stays on. I have three wires connecting thermostat to Navien. C to C, R to R and W to W. Can someone explain what is going on and how to fix this?
Thank you
    Jamie Hall Member Posts: 26,705
    Probably what looks like R, C, and W wires at the thermostat aren't R, C, and W wires in the basement….
    SuperTechEdTheHeaterMan
  • dlotito
    dlotito Member Posts: 5
    I pulled the cover off the Navien and see the zone controller outputs. They are marked R, W and C. I confirmed the wiring matches the thermostat.
  • dlotito
    This is the zone controller. I had the installer come back and add a third wire to the C output of each zone. I just didn't snap an "after" picture.
  • SuperTech
    SuperTech Member Posts: 2,633
    Check the installation instructions, perhaps it's a setting? Do you have a multimeter? That would really help with figuring this out. Is there any splices in the wiring?
    Navien with a Nest thermostat....two of my least favorite things combined together. Seems like a recipe for a lot of problems.
    Ironman
    EdTheHeaterMan Member Posts: 11,500
    You and @pecmsg secretly love that thermostat. Just afraid to admit it
    SuperTech
    pecmsg Member Posts: 6,710
    There still Garbage……………only good as Hockey Pucks and skeet shoot!
    SuperTechIronman
    What about this idea
    Old system wiring to old zone valves looked like this:
    New wiring to the Navien boiler is actually this
    When it should look line this
    Double check the wiring from the thermostat to the boiler control as @Jamie Hall suggested. There may be one of the thermostat wires crossed. that will make things go wrong fast.
    If you are absoutel sure that there are no crossed wires, and you get the same problem, then just for 💩 & giggles connect all three thermostats in the basement where you can see all three thermostat wires from end to end. If it works that way, then there is a compromised wire in the walls somewhere.
    And while you are checking wiring, really check. Don't assume anything. Remember that there may be crossed splices in the wiring. Remember that there may be broken wires. Remember that electricity is colour blind.
    If you twist R and W together at the thermostat. the circ. pump and boiler should fire. If they don't, problem. If you put a multimeter between R and C, you should have 24 VAC. If you don't, problem.
    SuperTech
  • dlotito
    So, from the picture above that says. "The one that works", it looks like you want me to swap the C and W wires between the Navien and the thermostat. Correct?
    edited October 2024
    Not Exactly… that can get you in trouble.
    • We want the R on the thermostat to really be connected to the R on the Navien
    • We want the W on the thermostat to really be connected to the W on the Navien
    • We want the C on the thermostat to really be connected to the C on the Navien
    It might be that simple, but don't just start swapping any wires. Know that you have a wire that is the same on both ends. Don't assume that there are no splices in the wall somewhere. If you suspect that there is a problem do the test I mentioned above. Remove the base plate of all three thermostats from the wall and connect all three thermostats in the basement where you can see both ends of the thermostat wire right in front of you.
    Swapping a W and a C may cause the R to get connected to C in the Navien control to short out the transformer on the control system. If you do that then the Factory Installed Smoke may be released from the control transformer. …and that can be expensive.
  • dlotito
    I can physically see the entire wire from the finished basement thermostat running to the Navien. I am sure that there are no splices. If one of the wires are broken, I don't think I would see this behavior. I'm not sure what to do next.
  • SuperTech
    Next thing to do is get a multimeter or hire a service tech who has one and can figure it out for you.
    edited October 2024
    So, you are sure about the wire in the basement…
    What about the other two thermostats?
    If you are not sure what to do next, I have an idea. What if you removed the other two thermostats from the wall. sub base and all. Connect short pieces of thermostat wire (about 6 feet long) to the Navien zone control locations. Now connect the other end of the thermostat wire to the sub base of the two thermostats you took off the wall two sentences ago. Now put the thermostats on the sub bases and see what happens.
    This test will require you to actually do something other than stare at the problem. It will require some 6 foot pieces of 3 conductor thermostat wire and a screw driver. You may need to use a wire cutter and a wire stripper.
    After you actually try this, let me know what you find.
    Hope this information is helpful
