Multiple Pressure Reliefs

seanbeck1
seanbeck1 Member Posts: 23

Looking for some advice on this system. It has been designed with pressure relief valves @ the boilers and the expansion tanks. I’m doubting if the ones @ the expansion tanks are required.

The PRVs on the boiler are integral and match the input rating of the boiler.

IMG_2009.jpeg

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • pecmsg
    pecmsg Member Posts: 6,043

    where do they show a second PRV

  • seanbeck1
    seanbeck1 Member Posts: 23
    edited September 2024

    Shows one on each boiler, and one on each expansion tank (bottom right corner).

    It’s the symbol next to where it says ‘to floor drain’.

  • mattmia2
    mattmia2 Member Posts: 12,662

    Might be some commercial code thing about pressure vessels.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,733

    The ones on the boilers are all you need

  • ratio
    ratio Member Posts: 3,978

    Are you piping this now? You might be able to get a letter from the engineer saying they're not needed. That would satisfy our inspectors around here, but I dunno about yours.

  • seanbeck1
    seanbeck1 Member Posts: 23

    Yes in the process of piping.

    I am going to add the additional PRV’s @ the expansion tanks. It can take weeks here to get an answer from an engineer. I can always remove afterwards.

    I just wanted to check and see if I was right about them not being needed/overkill.

  • ratio
    ratio Member Posts: 3,978

    I don't think they would hurt anything, so I probably wouldn't bother taking them out once they're installed.

    Sometimes, adding "delay of project" to the subject line will get them hopping—but sometimes there's nothing you can do to get them to move faster. In this case, since you've presumably already included the extra valves in your cost, I suppose they have no interest in answering speedily.

  • pecmsg
    pecmsg Member Posts: 6,043

    On each boiler YES!

    If the expansion tanks can be isolated, then the LAHJ MAY require them!

  • seanbeck1
    seanbeck1 Member Posts: 23

    Noted.

    Yes technically the Exp tanks can be isolated. Although we always put lockshield valves on expansion tanks, and advise the building owner to lock them open.

  • pecmsg
    pecmsg Member Posts: 6,043

    Then there required!

  • Jamie Hall
    Jamie Hall Member Posts: 25,999

    You beat me to it. If there is a possibility that the PRVs at the boilers may be isolated from the rest of the system (not just the expansion tanks but the system as a whole) then I, at least, would have required them.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,128

    In NYC, some boiler inspectors require an additional relief valve, same rating as boiler IF expansion tank has an isolation valve to the system. Over a fixed BTU...Mad Dog

    HVACNUT
  • HVACNUT
    HVACNUT Member Posts: 6,755

    So if there's a manual shut off valve to the expansion tank, a boiler rated pressure relief valve is sometimes required at the expansion tank? That's what the OP's drawing is showing. Looks like actual taps in the expansion tanks. I've never seen such an animal, but I work on small stuff.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,424

    I'm wondering where this job is located??? Since the diagram is redacted, it must be a TOP SECRET location, like the NSA, CIA or Secret Service building

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Member Posts: 25,040

    if the boiler with PRVs attached is isolated from the system where expansion come from to require a system relief valve?

    I suppose a failed fill valve could increase pressure

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream