Testing digital manifold

Good morning, I just bought a used testo 557. How can I pressure test it? I don’t think it would be good to submerge in water like my old dial gauges.

Thanks in advance.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Ironman
    Ironman Member Posts: 7,698

    Do you have an electronic leak detector?

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • ChrisJ
    ChrisJ Member Posts: 16,565

    I'd think a reasonably quick test would be to pull a vacuum on it and valve it off and wait to see if it climbs.

    I know that doesn't guarantee it won't leak under positive pressure but it's probably a safe bet.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • bignozzle
    bignozzle Member Posts: 31

    no,don’t have electronic leak detector.

  • mattmia2
    mattmia2 Member Posts: 12,244

    Or better yet pressurize it with nitrogen and see if it holds.

  • bignozzle
    bignozzle Member Posts: 31

    I installed a vcrt on the high pressure side and put caps on the other ports. I pressurized to 300 psi. I shut valve on vcrt. I took the knobs off and put bubble leak detector around the valve stems and caps. No bubbles. I did 10 minute test and it lost .4 psi. Not sure where the pressure went.

  • ratio
    ratio Member Posts: 3,950

    Internal, either the transducer connection or the transducer itself.

    Or, just temperature equalization. 10 minutes isn't very long.

  • mattmia2
    mattmia2 Member Posts: 12,244

    Wait another 10 minutes, temp changes could account for .4 psi at 300 psi. If it keeps going down as you wait longer there is a leak, if it stabilizes or fluctuates up and down it is just error in the equipment or expansion and contraction.

  • bignozzle
    bignozzle Member Posts: 31

    I don’t think it’s expansion or contraction because the nitrogen bottle and the gauge were in my garage for a couple of days before.

    Thanks for the input.

  • ChrisJ
    ChrisJ Member Posts: 16,565

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 12,244

    .1% isn't a lot of electronics to drift either. give it an hour or 2, if it keeps going down there is a leak. the temp of the nitrogen changes when you change the pressure on it too although it should get cooler when you lower the pressure from the tank pressure.