Testing digital manifold
Good morning, I just bought a used testo 557. How can I pressure test it? I don’t think it would be good to submerge in water like my old dial gauges.
Thanks in advance.
Comments
-
Do you have an electronic leak detector?
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I'd think a reasonably quick test would be to pull a vacuum on it and valve it off and wait to see if it climbs.
I know that doesn't guarantee it won't leak under positive pressure but it's probably a safe bet.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
no,don’t have electronic leak detector.
0 -
Or better yet pressurize it with nitrogen and see if it holds.
0 -
I installed a vcrt on the high pressure side and put caps on the other ports. I pressurized to 300 psi. I shut valve on vcrt. I took the knobs off and put bubble leak detector around the valve stems and caps. No bubbles. I did 10 minute test and it lost .4 psi. Not sure where the pressure went.
0 -
Internal, either the transducer connection or the transducer itself.
Or, just temperature equalization. 10 minutes isn't very long.
0 -
Wait another 10 minutes, temp changes could account for .4 psi at 300 psi. If it keeps going down as you wait longer there is a leak, if it stabilizes or fluctuates up and down it is just error in the equipment or expansion and contraction.
0 -
I don’t think it’s expansion or contraction because the nitrogen bottle and the gauge were in my garage for a couple of days before.
Thanks for the input.
0 -
Hoses expanding?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
.1% isn't a lot of electronics to drift either. give it an hour or 2, if it keeps going down there is a leak. the temp of the nitrogen changes when you change the pressure on it too although it should get cooler when you lower the pressure from the tank pressure.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements