Testing digital manifold

Good morning, I just bought a used testo 557. How can I pressure test it? I don’t think it would be good to submerge in water like my old dial gauges.

Thanks in advance.

Comments

  • Ironman
    Ironman Member Posts: 7,547

    Do you have an electronic leak detector?

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • ChrisJ
    ChrisJ Member Posts: 16,315

    I'd think a reasonably quick test would be to pull a vacuum on it and valve it off and wait to see if it climbs.

    I know that doesn't guarantee it won't leak under positive pressure but it's probably a safe bet.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • bignozzle
    bignozzle Member Posts: 31

    no,don’t have electronic leak detector.

  • mattmia2
    mattmia2 Member Posts: 10,924

    Or better yet pressurize it with nitrogen and see if it holds.

  • bignozzle
    bignozzle Member Posts: 31

    I installed a vcrt on the high pressure side and put caps on the other ports. I pressurized to 300 psi. I shut valve on vcrt. I took the knobs off and put bubble leak detector around the valve stems and caps. No bubbles. I did 10 minute test and it lost .4 psi. Not sure where the pressure went.

  • ratio
    ratio Member Posts: 3,789

    Internal, either the transducer connection or the transducer itself.

    Or, just temperature equalization. 10 minutes isn't very long.

  • mattmia2
    mattmia2 Member Posts: 10,924

    Wait another 10 minutes, temp changes could account for .4 psi at 300 psi. If it keeps going down as you wait longer there is a leak, if it stabilizes or fluctuates up and down it is just error in the equipment or expansion and contraction.

  • bignozzle
    bignozzle Member Posts: 31

    I don’t think it’s expansion or contraction because the nitrogen bottle and the gauge were in my garage for a couple of days before.

    Thanks for the input.

  • ChrisJ
    ChrisJ Member Posts: 16,315

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 10,924

    .1% isn't a lot of electronics to drift either. give it an hour or 2, if it keeps going down there is a leak. the temp of the nitrogen changes when you change the pressure on it too although it should get cooler when you lower the pressure from the tank pressure.