Older Weil McLain boiler; fire box corrosion
My name is Matt, I'm new here, and I have screwed up. I am asking for help so I can deal with my situation in a grown-up way.
The screwup is failing to pay proper attention to my Weil McLain steam boiler. I believe it to be an EG or EGH model per the circuit diagram, and a call to the mothership told me it was manufactured in 1992, though they could not confirm the model.
We live in central Michigan.
A helpful technician showed me some years ago how to drain & refill the boiler, and how to pay attention to the water level and check the low-water warning lamp and automatic circuit. He also showed me how to swap a thermocouple, and I came away with the impression that these units are pretty maintenance free.
Fast forward some maintenance-free years to the start of this heating period, when I noticed two things: yellow light coming from one side of the burner box, and more heat in the boiler room in the basement. I found that two of the seven burner tubes had become disconnected -- heavy corrosion on the support end had made this possible.
Gas was coming out of the spigots and was happily burning outside the fire box. I pushed the tubes back on, which made things considerably better, and I've been monitoring it since then to make sure things didn't get worse. I also put a CO alarm near the boiler, which has not complained.
The heat has been working fine all along, too.
Another positive is that I've kept 2+ feet of clear space around the boiler.
I have two goals here:
#1 stay alive and don't damage our house.
#2 get through the heating period so we don't have to make a twelve thousand dollar decision in haste, AND have major surgery with our backs to the wall. It was 0 F this morning. Not a great time for HVAC work.
Saving money is not by itself a driver; we own the house outright and we can afford a new boiler. We care very much about "value," though, so we want to make an informed and unrushed decision.
My plan, which I'm asking you to critique:
(i) Buy a CO monitor and measure in ppm to see how bad a situation I have.
(ii) Get two new burner tubes from Supplyhouse.com.
(iii) Install these new tubes and rig them in such a way that they'll stay put and in proper orientation.
In the spring, get professionals to come in and advise. They will probably recommend a new boiler, but we'll let them explain it.
It might of course be best to call a technician right now. I'm worried about being forced into immediate replacement. Is that something to be concerned about? I don't know the rules, but I know that they can be Draconian when it comes to gas.
Your comments and insights would be appreciated.
I will attempt to attach some pictures -- I took more, but I'm trying not to overload.
Thanks in advance,
Matt
The boiler is leaking. That's what caused the rust/corrosion. Figure on replacing it soon.Make the call now.All Steamed Up, Inc.
Consulting2 -
Get a contractor that will use Steel pipe and iron fittings to put the new boiler together. the Copper risers are a sign of incompetence on the part of the previous installer. Quite possibly the reason for the boiler leaking that caused the problem to begin with.
If you don't install swing joints so the pipes can give a little during expansion when it heats up and contraction when it cools down, something else has to give. The gaskets between the sections are probably leaking steam and causing that burner box to rot away.Edward Young Retired
2 -
Thanks to both of you.
This fits with what I know about the house and its owners:
Built in 1929, by a family with money -- owners of a small local bank.
Sold to a family with little money some time in the fifties, and then sold to my wife and me in 1997.
From electrical to plumbing, just about every piece of later work seemed to have been done shoddily.
For example, in 2010 a wet spot appeared in the wall between the shower and our bedroom.
It was a leak caused by galvanic corrosion where copper was mated directly to galvanized steel. I fixed that myself, and it wasn't fun. Soldering copper pipe in wood-framed walls? Ugh. The plumber took over a week to even give an estimate, so I saw the light. That's on par for me with contractors, even when I get recommendations.
The instructive part is that the pipes stayed tight at least 13 years and maybe much longer. My parents had an incompetent plumber mate dissimilar metals without a dielectric union, and it leaked within two years. We have soft water, and that slows the process. I think™.
Galvanic corrosion is probably exactly what's happening here, but it took three decades to get bad. When you say "risers", that's got to be the 4 inch (?) vertical steam pipes coming from the top of the boiler, correct? They would have to corrode at the joint at the top of the boiler. "The laws of physics are strictly enforced," to quote my former boss. This would create a leak that never leaves a puddle, because there's only steam pressure when there's a flame. That all makes sense to me.
The old company's sticker is still on the boiler. So they're out.
I just got a recommendation for another one. They installed a new boiler at a colleague's house, and he was happy with the work.
I'll have them come out and ask them to assess. If they aren't worried about the copper risers, does that mean I should forget them, too? Steam heat is a little unusual out here, and if HVAC folks are like car mechanics -- where I have some expertise myself -- then Oy Vey on finding a good one.
Thanks again, and I'm glad I found this place.
Best,
Matt0 -
@mattmich
Send a message to @offdutytech he is in Michigan but may not be in your area. He may be able to recommend someone. He does excellent work. Steam pros are scarce in your area1 -
@EBEBRATT-Ed
Thanks. I have done so.
Here is a link to an album showing the full setup, if anyone is interested.
The eight-inch-to-six-inch reduction in the exhaust is a nice touch. The chimney folks explained to me why it was a good idea, and the city inspector signed off on it. What do I know.
https://www.flickr.com/gp/196596407@N06/r274v09v98
Best,
Matt0 -
Not a corrosion issue. Copper has a greater coefficient of thermal expansion than steel pipe. The copper pipes are expanding too much ripping you boiler apart where the sections are joined.mattmich said:Galvanic corrosion is probably exactly what's happening here, but it took three decades to get bad. When you say "risers", that's got to be the 4 inch (?) vertical steam pipes coming from the top of the boiler, correct? They would have to corrode at the joint at the top of the boiler.
You need to read other posts on replacing a steam boiler. When you replace that boiler you need to size it based upon radiator size not heat loss to the house. Need to pipe new boiler as in owners manual, you would be amazed how many problems await if not followed. Hopefully you can use the person recommended by Ebebratt-ED.0
There's been progress. I invite comments; no need to be gentle.
So the old tubes maybe weren't the best anymore... and the new ones don't have much reason to stay in the proper orientation, what with the box so corroded.
So I crimped up some encouragement from 14 gauge copper.
I'll come up with something more solid so I can leave the house with the heat on, I just wanted to see the new tubes in operation.
Here are a couple more pictures of the burner in action.
That last one was with the flash by mistake... it shows the back of the box a bit better.
Any thoughts, assuming I get the new tubes to stay put?
Thanks!
Matt
Brother you are throwing away good money for bad.
Its really unsafe. Really unsafe. You really should turn it off.0 -
@realliveplumber
I appreciate your response. Doesn't mean I like it, but I take it seriously.
>> good money for bad.
I need a new boiler, that is clear. We have money set aside for stuff like that, that's not the issue.
The issue is that it's going to be -4 F on Saturday, and it's 18 now and dropping. This 95-year-old house doesn't have the plumbing to just empty the pipes. My Sawzall would probably work.
I've made contact with a member here, sent him some pictures and we talked last night. He'll try to come out this weekend and start the process. He might be too far away to do the actual install, but it's a start. He didn't know anyone local who's good.
Thankfully the missus is on travel for a week, so that helps, mentally at least. Nobody else on the line.
I have the new tubes mounted in such a way that they will not come off, and they will not rotate. When I push them off the spigots, they spring back, all seven of them.
>> unsafe
I'm not loving this, for sure. And I started this thread by stating I'd screwed up. Low maintenance is one thing, I went no maintenance. No excuse, it's not how I do stuff like cars, but it's what I did here.
I will say that it's safer than it was yesterday. For whatever that is worth. Case in point, I can now touch the outside of the burner box everywhere, comfortably. It was way too hot to touch in the far right corner (in the pictures.) I'm not patting myself on the back here.. it's not good. It's just less bad.
>> turn it off.
There are steps between "turn it off" and "pretend everything is OK." Like only running the heat when someone's home and awake. There's a CO monitor and a fire alarm in the boiler room.
I'm not trying to run this thing another year; I'm trying to buy time so I can get a new boiler, and do it right.
Again, thanks for your feedback. It's weighing on me.
-Matt
I get it, and I wish you well. I just wanted you to be aware. Please be careful.
I know it is not convenient, it really sucks.
We have had customers in a similar situation. We winterized the building. I mean properly winterized it. A 185 cfm tow behind compressor, and blow out all of the piping, including washing machines, icemakers, and humidifiers. We either shut off the water service at the curb and drain the main, or add heat tape, or a 100 watt bulb at the main where it enters the basement. Or both.
A coupe of oil filled radiators in the basement usually allows for threading pipe without getting frostbite.
The owners spent a few nights in a hotel.
It is a pain, but it beats the alternative. And the alternative could be a really bad outcome.
Just offering some ideas to think about.
Hello again. Summer is upon us, and I got luckier than I deserved. No more mishaps with the boiler, and my jerry-rigged burner got us through.
Thanks again to those who gave their opinion and answered my questions.
For my edification — and your entertainment — today I started tearing into the boiler to see if I could learn anything. I still need to find a competent contractor, which is not going to be easy in this area. So whatever I can learn is a bonus.
First up though: Someone tell me there CAN'T be asbestos in this thing… right??? It was banned in 1989, and my boiler has a 1992 serial number according to the manufacturer.This is what the insulation looks like:
and like this:
I'll post more pictures later. But I hope I just didn't do something really stoopid.
-Matt0 -
Where were we?
The fire box is a mess.
[So is the date function on my camera; the battery must have drained. Please ignore.]These pictures are of the boiler itself, from below, and I tried to get the corner where the corrosion was worst. The cast iron looks remarkably good. Whether that means anything, I don't know.
-Matt
Moment of silence. That boiler is dead.
Try the Find a Contractor page of this site to locate a Steam Man who can replace it.
Consulting0 -
Please do not run that boiler again. Yours and your wife's life literally depends on heading everyones warning. This boiler cannot be saved. The firebox is rusted away, and the sections are leaking. That is the entirety of the boiler.
There shouldn't be asbestos in it. Take a sawzall to it and cut out everything and make it a little easier for someone to install a new boiler. I'd even cut out all the copper up to where you find iron.
I can not express how much I want the next picture you post showing us nothing but the stains on the concrete from where this one stood.
» [..] showing us nothing but the stains on the concrete from where this one stood.
Yes, the boiler is toast. Right now I'm trying to understand what else is going on, and I want to learn how to tell future problems when I look at my new one in ten years.
Cuz it looks like it's gonna be mostly me doing the looking.
Here's a look at some of the equipment that I should have been maintaining or at least cleaning over the years.I work at a university lab, funded by the federal government. We have around 600 employees, counting graduate students. Having been here since I was a fresh-faced student myself in the early 90s, I know people. So last Friday I visited the plumbers.
That was pretty much "Who's on First" for 20 minutes…
"You sure it's steam, not water?
"How old is the house?
"Man, I've converted a bunch of these to hot water.. can't think of anyone who does steam around here..Hey Cale! You know anyone who does steam boilers?"
"What for?
"You sure it's not water?
"How old is the house?"and so on. It's slim pickins around here.
-Matt1 -
I found a youtube video titled "Near-Boiler Piping in Steam Heating Systems" by a Dan Holloman, who's written a bunch of books on the subject; his name comes up in the forums a bit. Which one(s) do you recommend I buy?
The video is excellent, at least to my layman's mind. I can alreaydy see a bunch of problems with my installations, starting with the use of copper, and the way the pipes directly out of the boiler set the two streams of steam up for a collision where they come together.Apparently it should look like so — the pointer is from the explanation how you get water problems at that location if the steam went upwards there — but mine looks like the picture below.
To say nothing of the lack of the big valve that can be shut to use water pressure to blow the mud out, which I obviously can't do with my setup.
At least I got the, ah, "insulation" removed around the boiler.0 -
Peerless has been good to me. Boiler should be repiped, in black iron,and in strict compliance with the manufacturer's installation instructions.
Some thoughts.
If you are up for it and have some tools you might be best off doing the install yourself with the guidance of this forum and having a "plumber" finish up the water supply and gas connections.
The correct way to size a boiler is to add up the EDR of all of the radiators, not by doing a heat loss or picking another boiler with the equivalent input or output BTU's. You may find that you can get away with a smaller boiler than you have now.
Many small to midsize boilers only require a single riser. You could probably make your install really easy positioning the new boiler such that you don't need to thread any pipe or perhaps just a single pipe that the big box stores could do for you.
Pay attention to the piping diagram in the boiler manual as they tell you exactly how to pipe it.
When It came time for me to figure out what to do I decided it was not only cheaper to buy all of the tools needed, but afterwards I'd still have all of those tools. That's a very big deal in my book. Tools never go bad and are always useful and hold their value.
The rub is the amount of work involved and of course the risk.
I did mine after work and on weekends and since it was the summer I had plenty of time. This was nice because when I was unsure of something I had plenty of time to figure it out, get help, order parts etc.
2 -
I pretty much came to the same assessment as Chris when my boiler died. I also wasn't getting warm feelings about the local contractors so I did it myself. I got mine running on 10/19/2014, which was also my 40th birthday, so that was a nice present. System still purring along nicely 10 years later.
It is a fair amount of work for sure, can be back breaking, but also mentally therapeutic.
If one is a beer drinker, I've always liked this line from Shawshank Redemption:
" I think a man working outdoors feels more like a man if he can have a bottle of suds. That's only my opinion, sir."
For me it doesn't necessarily have to be outdoor work, but any work qualifies.
Several of us have done our own installs, this site has been invaluable for guidance. I've lost track of who all has done their own steam install from this site. I have done it, @ChrisJ and @ethicalpaul are 3 that I know of, and I'm proud to call them good friends too, thanks to this website. @Erin Holohan Haskell @DanHolohan thanks for that BTW.
3 -
Thanks @KC_Jones.
Welcome, @mattmich! Dan's my dad and he started this forum in 1997. You can find more resources and articles on steam heating systems here. As for books, I recommend The Lost Art of Steam Heating Revisited.
President
HeatingHelp.com1 -
Thanks, everyone.
I appreciate the input. I will try to not dribble out information over lots of posts.
So without trying to be complete, here are some thoughts.
@Erin Holohan Haskell: Thanks for the welcome. The 'revisited' book arrived yesterday and I have begun my education. So far it's making a lot of sense. Grasping the principles is easy; grasping the practical implications will be a bear. Steam speed, heat transfer, effects of pressure — these are all far outside one's usual experience, so it's going to be difficult to develop a quantitative feel for anything.@AdmiralYoda, @KC_Jones: I'm used to doing my own work. Plumbing, electrical, the occasional car repair or a new water heater… so far so good. The number one rule is not to get cocky and to be realistic about risk, and be realistic about what I know and do not know. I have not made up my mind at all how far I want to take this, but I have a little time to decide, and whatever I can learn is all to the good.
@EdTheHeaterMan
» the Copper risers are a sign of incompetence on the part of the previous installer. Quite possibly the reason for the boiler leaking that caused the problem to begin with. If youdon't install swing joints so the pipes can give a little during expansion when it heats up and contraction when it cools down, something else has to give. The gaskets between the sections are probably leaking steam and causing that burner box to rot away.That went right over my head when you wrote it back in January. Having read up about near-boiler piping, it now makes sense and I'm sure you are correct.
I will post again when I have something to report or to ask.
Thanks again to all who responded. Social media have caused a lot of problems, but forums like these, where knowledgeable folk are generously helping others, make it worth while. I do appreciate the support.
-Matt2 -
That copper geasrt can cause boiler sections to separate but there is another piping error. That is a colliding header where the system steam takeoff is between the two boiler outlets, that WILL cause water carryover into the header because the takeoff is between the two boiler outlets. The system steam take off should be after both boiler steam outlets and the connection to the equalizer, that way the steam and any condensate are flowing in the same direction.
This shows the eight way to pipe a boiler -
Bob
3PSI gauge0 -
EDIT: thanks for the ComfortCalc link. Those diagrams are really clear.
» That is a colliding header where the system steam takeoff is between the two boiler outlets,
That's what I wondered after I watched a Youtube video on Near-Boiler Piping in Steam Heating Systems
from, you guessed it, the HeatingHelp channel.
While we're at it, there isn't a Hartford loop either.And the front (South) side of the house is fed from the top of the boiler, as I would expect.. while the rear is plumbed into the condensate return. In other words, it looks to me like the steam has to travel as sketched below…
*********** I'm leaving this image here but it's wrong. See the next post ************** 25 June 2024 -MattI took a bunch of pictures of the boiler structure with all the covers and ducting removed. The fire box is a mess, and it looks to me like there was indeed a steam leak to cause the corrosion, but I don't see it. I would expect galvanic corrosion where the copper is piped in, but I don't see that either.
I'll sift through the picture and post some later for amusement's sake. Next time I have a problem, I'd like to catch it early, so I really want to learn what I can from the wreck. Speaking of wreck — fire box as seen from the rear of the boiler (W), and a top rear view. I don't know if the sealing material was meant to fix a leak or if that's how the segments were put together originally.-Matt
Well.
I was wrong.
It bugged me all day… with the Pressuretrol set to < 4 psig, there was no way the steam could make it through the condensate return.As my former boss liked to say, "The laws of physics are strictly enforced."
Or put another way: "If it can't be right, it's not right." In other words, figure out what's really going on.
Of course, the steam goes once around the basement ceiling, feeding all the radiators and returning the condensate as shown.
Y'all knew all this but were too nice to tell me I was being an idiot.
Won't be the last time I'm sure.
-Matt0 -
I finally made some progress on the boiler teardown.
As @JakeCK put it:
» I can not express how much I want the next picture you post showing us nothing but the stains on the concrete from where this one stood.
I tried the gentle method of unscrewing things, but that only got me so far.
The threaded rods that tie the sections together actually unscrewed quite easily.But I cut the water supply line and used my biggest wrench to unscrew the blowout spigot; no dice. I'll either have to use a torch, or just cut it. I'm assuming cutting is the best way?
Before I get the Sawzall out: What should I measure, preserve, photograph to help the installer?
Should I just take a few more pictures and then remove all the copper back to the threads in the steel piping?
I'd be grateful for any advice.
-Matt0 -
Its scrap metal. Whatever fits your fancy. Whoever installs the new boiler should be following the manufacturers near boiler piping. So not much here is going to need to be preserved or saved. But please cap off that gas line. It is right where the shutoff handle could be easily knocked open. And the last thing you want to do is bump that while cutting and have a spark light off a really nice flame thrower with unlimited fuel in your basement.
Did you find any actual spots on the block that were leaking?
Now that you know this, you'll need to install some serious venting on the end of that main. How long is the main, and what pipe size?
Consulting0 -
Thanks for the feedback, everyone.
I'll answer @JakeCK, @ChrisJ, and @Steamhead in order.» But please cap off that gas line.
That should have been obvious but wasn't. I took care of it last night, thanks.
» Did you find any actual spots on the block that were leaking?
I did not, and it's bugging me. It would seem that there has to be a leak somewhere, due to the corrosion in the fire box. But it has to be a steam leak, not a water leak, since there is never any water on the ground. And I figured I'd be able to see it, but so far, nothing. I expect I'll get the sections apart with a hammer and a chisel and maybe a crow bar, maybe something will show up. This may not be my last steam leak, and I'd like to know how to spot them.
» How long is the main...
I measure 79 ft of horizontal pipe in a square "loop" under the basement ceiling. Give or take a couple feet.
There is one place where the rear of the house is bumped out and a horizontal line is Tee'd off the main, that's another 10 ft before it goes vertical.
» ..and what pipe size?
The steam enters through iron pipe, 2-7/8 inch outer diameter.
By the time it comes out of the asbestos and becomes the condensate return, it's 2-3/8 OD, and I can't tell where the reduction is made.
I only removed the insulation near the boiler, as instructed by a member here, so it's not easy to see. Someone did a thorough job on the insulation.
» you'll need to install some serious venting on the end of that main.
There is a vent on the end of that line, but it was hidden in the earlier pictures.
Here's what it looked like with the insulation still on, not a great shot:Thanks again,
-Matt0 -
It was my opinion before you tore it apart that the corrosion wasn't from the boiler leaking, but I wasn't sure and it's far from my area of expertise. I don't do this for a living.
However, I felt and still feel others who commented knew better overall and the fact is the boiler was very likely at the end of it's life anyway. What's the point in investing in a new burner setup, covers etc for a boiler that's going to start leaking next year, or in a few years at best?
The EG series is a good boiler with a life expectancy of about 30 years.
My first concern with this setup was to get through the winter, which worked out, mostly due to luck.
Now I need new equipment, and I'm not looking to cut corners or to squeeze a few more years out of this old thing. I don't want to go through this again.
For my wife and me, it's not about a low price. Quality comes first. Value, too, we're not made from money.. but cheap is no good if it's "cheap." We can afford a new boiler.
We cannot afford shoddy work.
I now have three leads on local installers, but no real recommendations. It's hearsay and google searches. One thing I can do is show people what I've got, and anyone who doesn't say "OMG the near-boiler piping is wrong" is disqualified. After all, that was everyone's first reaction here.
And after reading a few chapters of the 'Lost art...revisited' book, I now know what they meant.
BTW I just saw the Mikey Pipes youtube clip of the Pyrex-glass-piped McLain boiler. THAT was interesting.
-Matt
Is there a reason you're not up to installing the new one yourself?
Is it not allowed in your area? Do you have doubts you can handle it?
Everything you need to know is right here on this forum.
I'd start by accessing your installed radiation and how long the old boiler used to run. Chances are you can go at least one model smaller. Next, for that size boiler, assuming an EG-40 or EG-45 I'd run a single 3" out into a 3" header. Easy to do and you can probably get away with mostly off the shelf nipples from Supplyhouse.com
Copper below the water line is considered fine by most, preferred by some. My equalizer is even copper but the header and everything else above is black iron / cast iron.
With the google searches, you can check the photos to see if they have photos of any steam boiler work. Would also check their website to see if they very specifically mention steam.
Not that I know them or recommend them, just an example:
If you check their photos, can see tons of steam boiler installs. And then you can judge quality of their work.
The one thing I would strongly recommend you do is figure out the proper sizing on your own. That is another thing that is gotten wrong far too often and it will help you either vet out the contractors, or put them to task with sizing incorrectly.
It's not hard, it does not take too long. If you want we can guide you through it.
That vent is either a Hoffman #5 or #6. It might have been OK for a coal-fired boiler but not for oil or gas.
Start with two Gorton #2 vents there. That should be enough, but you can add more if needed.
Consulting0
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 106 Geothermal
- 982 Plumbing