Older Weil McLain boiler; fire box corrosion
Comments
-
There's been a little progress here and there.
I'm not disengaging, I just don't want to drip and drab small bits of information and waste everyone's time.
Let me go in order.@ChrisJ
» Is there a reason you're not up to installing the new one yourself?
I've tackled "pro" jobs before, and while I've generally been successful, they've all been serious time sinks. Sometimes DIY is best, like window replacement or when I laid a natural slate floor in the kitchen. Electrical work is somewhat straightforward, and household plumbing jobs, too. Just slow.
The chimney repair I farmed out, dto. the floor refinishing — and I'm glad I did. 25 years and looks as good as then. The trick is finding the RIGHT professional. I'll come to that.
This boiler job is up there. There is the weight, there is the zero experience — case in point: Holohan says the main vent should be 15" back from the downward elbow ("revisited", p. 133). I did find the explanation, picture and all, p. 188. Just reading through all the material takes time. "Takes" time, not "wastes" time. It's actually an interesting subject.But my vent is 5" from the elbow. Do I have to move it? Do I just add a longer nipple? That's what I would do, but a pro knows this stuff, and I'm guessing.
I haven't excluded DIY but I'd much rather pay the money and keep the three weeks of vacation I'd have to invest. "Know thyself" — I get OCD on stuff.
The only reason it's even an option is you-all. I do appreciate the help and support.
-Matt
0 -
@dko and @GGross:
Thanks for pointing out the contractors you did — I'm in East Lansing; that's quite the distance.
The upside of DIY is of course that I'll become educated in the process; I expect I'll do a lot of my own maintenance and troubleshooting in any case.Plus there's that pesky day job I still have ;)
-Matt
0 -
» That vent is either a Hoffman #5 or #6. It might have been OK for a coal-fired boiler but not for oil or gas.
Good eye, I suppose — I haven't checked for the marks on the vent.
But you nailed it: this house used to be heated with coal. Which in 1929 was to be expected.0 -
» The one thing I would strongly recommend you do is figure out the proper sizing on your own.
I've been working on that.
It's less straightforward than I thought, but I'm probably close.
First up, here are my radiators: I have one oddball one, of which I'll dig up a picture from when I had it sandblasted and then painted it in the garage.
But all the others are "American Radiator" and "CORTO Patented 1921." Pictures below.
Using the "Standard Column Radiators" table on p.120 of the "revisisted" book, I get an EDR of 675 or 600 square feet — using the "as installed x 1.5" oro the "as originally installed, x1.33" methods. respectively. See the attached spreadsheet if you're so inclined.
That's of course not quite right; my radiators look different.
I found a 1922 AR Corto catalog — in these pages, of course — but the radiators are not quite the same. They look different and the sizes aren't right. haven't done the math with them yet.From threads here as well as the book, I'm getting 240 x EDR, giving me 162,000 or 143,000 BTU/hr.
Or maybe not. P. 126 reads "Convert this to MBH (thousands of Btu per hour) by multiplying by 240."That's where the wheels come off a bit. The prefix M means Mega = 10^6.
The text SAYS thousands.
And the number itself is already ~150,000 BTU/hour, with no kilo- or Mega-, and it matches the catalog description of, helpfully "BTU" — no time given. Since BTU is a unit of energy, that doesn't make much sense, since we're interested in power….I can only conclude that the /hour is assumed, and it's a kind of shorthand.
Anyway, I'll stop this post here with a couple of radiator pictures. If anyone has a reliable conversion for these, I'm all ears.
-Matt
0 -
Today, one of my plumber friends at work came through with a plumber's name and number. I chatted with the gentleman over the phone a bit. It went okay.
Good: from mentioning the "Dan Hollohan" book, he knew what I was talking about and said he had and had read the book, but not the 'revisited' version. I asked him about a recent boiler job, and he said, a couple months ago.. when I dug a little more, meaning STEAM boiler, then he said it had been a couple years, which when I say it means, like 2019.
Not so good: As a Litmus test, I showed him a picture of my boiler with the copper piping, from above in the thread. He was not bothered by the copper piping, nor by the opposing pipes — he called it, "deadheading", which I believe is the proper term. This was considered a No-No by the members here as well as in the book, so it gives me pause.
Here I am, with eight hours of book reading and fifteen hours on the internet — am I now a youtube-certified™ steam fitter? Should I disagree with a professional?On the other hand, I can't ignore what I've learned, especially when it makes sense to me.
I'm inclined to ask my new friend — who works for a good-sized firm; they do work for my employer — for an estimate. It would allow me to pick his brain a bit about replacement boiler sizing, and if that sounds good….
Just looking at the main as it goes around the basement, it looks just like the book says it should, with the 45 degree angle as the steam pipes branch off and good insulation everywhere.
I just measured the overall drop in the main — it's 12 inches, and as I wrote above, the total length is about 80 feet — so for a parallel-flow system we need 1 inch per ten feet, and that's about what we have, given that the condensate return slopes a little more at the very end. So whoever did this originally musta read a book, too.
So I'm thinking this is not that complicated a job, because the basics are presumably OK. I've not had problems with spitting vents, or radiators not getting hot.
The old boiler would run on a really cold day for 30-40 minutes on and 1 hour off. I kept book on this one Saturday in January when it was in the single digits.For good measure, I wrote a request for a steam expert on the "FRIEND'S of Michigan Steam Engine & Threshers Club Group." [apostrophe included]… but I haven't gotten anything back beyond a couple of thumbs up ;)
I'll stop here. Any thoughts will be appreciated.
-Matt0 -
Well, regarding the radiators, you have the later and much more common Corto version which followed standardized dimensions and ratings. The earlier ones were unique. Use the chart for any standard large-tube type you can find such as the National "Aero", U.S. Radiator "Capitol", Weil-McLain "Cameo", Burnham "Fero" etc. All these charts appear in @DanHolohan 's book "E.D.R.".
Maybe give the guy who read the original Lost Art book a try. There might just not be a lot of steam in your area, which would explain why it's been a while for him. Or try some of the local supply houses to see if they know someone.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
» Or try some of the local supply houses to see if they know someone.
…and that was exactly my plan for this week.
There's a wholesale only place where I've gotten parts on a friend's account...they should know someone.
0 -
M means Mega = 10^6. "BTU" — no time given. Since BTU is a unit of energy, that doesn't make much sense, since we're interested in power…. I can only conclude that the /hour is assumed, and it's a kind of shorthand.
You may be an electronic engineer. BEE-tu is British Thermal Units and pre-dates wide use of the Metric system or strict units. "M" is Roman for 1000. If you mean a Million (as for pipeline gas prices) you multiply "M"s: 1 million Btu is 1 "MMBtu".
"per hour" because what else would it be? Days are long but minutes are short when feeding a coal fire.
If you do Joules, a BTU is 1055J. Also 1.0551 kJ (kilojoules), 0.2931 W⋅h (watt hours), 252.2 cal (calories),
0.2522 kcal (kilocalories). Or the heat of burning a single wooden kitchen match (roughly).The name "British Thermal Unit" was probably invented in the US.
Wikipedia mentions the Roman/Metric conflict in passing.
0 -
radiator pictures. If anyone has a reliable conversion
Generally, for natural convection heatsinks/radiators, not featuring extreme fin size/shape, it is adequate to take the gross overall dimensions and find similars. Especially since your rads are very conventional.
0 -
@JakeCK
» I can not express how much I want the next picture you post showing us nothing but the stains on the concrete from where this one stood.There's been progress in that direction.
I got the middle sections upstairs in the garage, might get help for the heavier pieces.0 -
@Steamhead
» you have the later and much more common Corto version which followed standardized dimensions and ratings.
I got the E.D.R. book last Thursday, and that allowed me to fill in the gaps in the calculation.
There are three types of radiators in the house; the Corto's with five columns and 20" and 38" height, respectively, and then one radiator made up of four sections of the "Wall Radiator" type, also bey American.
That let me calculate the total in-use radiation as 375 square feet.
What's missing from the original installation is this:
- One radiator in the kitchen, with the line capped off after a run of 5 ft.
- One radiator in the attic, 50 square feet, valved off and verified to be cold when the heat is on.
- One radiator in my office, that used to be an 8x16' sleeping porch with windows all around.. a massive 19 sections of a 20" high radiator, for another 51 square ft. I moved that thing to the garage when I renovated the room, and the line is valved off. It took four big guys to carry it…
I went around the basement and followed the main and all the branches as far as I could. I'm confident I'm not missing anything. So what size boiler do I need?I'm inclined to go with the in-use radiators and the standard 1.33 factor. I know that Holohan recommends a factor of 1.5 to make up for the unused lines, but at low steam pressure, I don't see how that can use up significant amounts of steam — it's got nowhere to go, which is eloquently described in the chapter "It's all in the venting."
The math, then: 375 x 1.33 is 499; multplied by 240 gives 119,668 or 120 MBTU/hour.
[Thanks to @PRR for sorting out the units for me.]In an earlier post, I wrote how my old boiler would run 30 minutes, then cycle off for an hour, then come on again — on the coldest day of the year. That may be an indication that the system is oversized for the heat load.
This 1929 2000 sq ft house is now pretty well insulated — retrofitted, of course, by previous owners and by me — and it would not be surprising if there is now too much radiation. It wasn't until recently that I realized that they are modular and can be changed, and I don't think I want to mess with it now.How much heating efficiency am I giving up by sizing this way? Should I try to make a reduction of radiation part of the job? We have one thermostat in the house, in the first-floor living room, and we keep it at 67 degrees. It doesn't get too warm in any room, nor particularly cold. As my wife is fond of saying, "it's fine the way it is."
What size boiler should I buy?
-Matt
0 -
I have a recommended plumber coming tomorrow morning.
My idea is to have him look at the system and tell me what he wants to do, and why, and take notes.I have some specific ideas for proper piping, and to get the main vent moved away from the down elbow, to have everything as close to the manufacturer's instructions and "best practice" rules. I think I'd like a drop header.
I talked to a second gentleman on the phone, and while he saw no problem with my colliding header either ("That's how it's done") but he otherwise seemed to know what he was talking about. As a bonus, he installed a boiler in an appartment building two months ago.
He asked about the number of burner tubes on my old boiler (7) and put the size at 150 MBTU/hour ("it's at least 15 per tube, but usually 20") and made the off-hand suggestion of installing 120 MBTU/h ("they're usually oversized.")
I may disagree with the methodology but the answer was the same I got going through the steps. I didn't go into it over the phone.
After tomorrow, I'll schedule a visit for the second guy, and depending on the proposals, think about going to the "steam show" at the county fair grounds next weekend. From the pictures, these guys are all 80 years old, though.-Matt
0 -
You want to include the disconnected/valved off/missing radiators. The piping was sized to support them so the pick-up factor might be too high if you just go by what's still hooked up.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
I would add up all of the radiators and then go around and figure out the EDR of the steam piping which will actually get hot (air can get out) and account for whatever insulation you have installed, or are going to install.
I would also do a manual J on the house and see how the actual loss on the coldest nights compares with the installed radiation.
I'd then make a judgement on what size boiler I wanted.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I gotta ask this — it's so obvious that nobody ever spells it out: When sizing a boiler by EDR, the BTU number is the OUTPUT figure and more specifically, the IBR number.
Meaning: Installed EDR x 1.33 x 240 = IBR Rating.
YES?0 -
Minor update. I've had a 'corporate' guy come by Monday; he'll send me a proposal. Wants to do another McLain, which is fine by me, and has agreed to do the piping to manufacturer's specs. He was sizing the boiler by "old boiler - 1" and wasn't really interested in EDR. But in general he did seem to know his stuff and was the proper age, but of course when it comes time to do the job, he'll send a couple younger guys. Which is understandable but I like to know up front who I'm dealing with. Haven't had a proposal yet.
The second gentleman came Monday evening; he's on his own and brings in help as needed. Same thing with the boiler sizing, though when I showed him my calculations, he was receptive. But on the proposal it says "all piping in copper" which does not give me the warm fuzzies. We did talk about that, or at least I did.
This morning I called a second corporate firm. They have a guy, and he can come by to look at my situation… in early September. Heating season starts in October, so that's cutting it way too close.
And then I called a fourth person, and I'm feeling good about him. Has the full set of Holohan books, and a Dead Men sticker on his truck. He's the first person who wants to size the boiler to the EDR. He's even close, not a ten minute drive from my house. I'll see him on Monday.-Matt
0 -
The DOE rating is the boiler's actual output.
The IBR rating you're looking at already takes the 33% into consideration. They're suggesting you need 36,000 btu/h for piping losses which in my opinion is, a bit much.
Personally, I feel you should take your EDR * 240 and then add your piping losses, add an extra 10-15% to that and then choose a boiler going by the DOE rating.
My own system has 392sqft and I'm using an EG-40. For my size system or similar I absolutely would not go bigger than an EG-45 under any circumstances.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
-
» The DOE rating is the boiler's actual output.
» The IBR rating you're looking at already takes the 33% into consideration.Thanks. I didn't realize that, and now I'm glad I asked.
There are plenty of things in this business that people "just" know so they're easy to miss in the writeups or discussions.» My own system has 392sqft and I'm using an EG-40. For my size system or similar I absolutely would not go bigger than an EG-45 under any circumstances.
The gentleman who'll come by on Monday said EG-45 off the top of his head when I told him my EDR numbers. That sounds bang-on to me, though I've had some indecent thoughts I'll write about in the next post.
How many different "boilers" does Weil McLain actually make?
If I look at the spec sheets, it seems pretty obvious that from the EG-30 to the EG-55, we have three different boiler configurations and six different-sized burners.Is that true?
I read the thread about the two-sizes-too-big boiler that @SteamGirl had to have replaced; it was an EG-55 instead of an EG-45. For those who didn't read her thread, the installer went with the larger boiler, and problems ensued, including high energy bills. As remediation, "downfiring" was proposed and adamantly opposed by the knowledgeable people here. It never came up that an EG-55 to -50 cexchange might just be a burner swap. Is it?
The resolution of the thread was a replacement of the unit to the proper EG-45, and the problems disappeared.
-Matt
[EDIT: Forgot to add the graphics]
0 -
I may have missed it,
What's your total installed EDR?
I'm far from an expert, but as far as I know an EG-30 and 35 are the same boiler, 40 and 45 are the same etc. The differences between a 40 and 45 is the drafthood and an extra burner tube.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
When reading the "oversized boiler" thread, I was directed to this article:
https://www.heatinghelp.com/systems-help-center/taking-another-look-at-steam-boiler-sizing-methods/which got me thinking.
The first thing that occurred to me is that I can calculate my the EDR of my piping simply by calculating the area from the length and the outside diameter of the pipes.
Dan Hollohan states in his article on insulating steam pipes that "The 1.33 pickup factor assumes insulated pipes." I'm not sure that's correct. Taking my house as an example, as originally installed I have 476 sq ft of radiator surface, and 141 sq ft of piping, for a "pickup factor" of 1.30, calculated as (476+141)/476.
I'm assuming 10 ft of piping for going to the second floor, and 20 to go to the attic.All my pipes are insulated, even the vertical ones in the wall — I've come up against them personally on several occasions — and that insulation effectively lowers the load.
Finally, I can estimate the load on the capped runs by assuming a maximum steam pressure of 3 PSI, which will compress the air in the pipes to 0.8 times the initial volume, leaving 0.2 of the dead volume to be heated by steam. It can't go any farther, as described in the chapter on venting.If I knew how much to reduce the EDR to account for the insulation, I could do a really accurate calculation from these factors.
And once I have that number, I will probably wind up between the numbers for an EG-40 and an EG-45, and I would be sorely tempted to try the lower-rated boiler and make up for it as described in Dave Bunnell's article linked above: "[..] the radiators rarely if ever heat all the way across because the thermostat is satisfied long before the system is completely filled with steam. This then begs the question….. Why are we sizing steam boilers to completely fill the system with steam?"A big difference between me and a professional is that I can make small adjustments over time. A pro leaves the job and moves on to the next one. I wouldn't be into any experiments either, if I risked call-backs.
In line with my last post: I'll only try the experiment with the smaller boiler if I can "upsize" by changing the burner. An actual boiler swap is not in the cards.
-Matt
0 -
@ChrisJ
» What's your total installed EDR?As orginally installed, 476 square feet + 141 square feet of piping, ignoring the near-boiler stuff.
As we now run it, 345 sq ft — I just discovered yesterday, when checking the radiator shutoff valves, that the one in the downstairs hallway (30 sq ft) was actually disconnected from the piping, and not by me. We've never used it, because the dining room radiator is five feet from it, and I wasn't even aware. Beautiful system, it just worked ;)
0 -
I wouldn't include capped pipes, they're not going to heat if your system is sized reasonable and vented well.
But what happened to all of these radiators?
Why are they gone?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
@ChrisJ
» But what happened to all of these radiators?There are 14 branches off the main. Of these, 10 are still active.
The "canceled" radiators are:
- one unit in the kitchen under the window. Never saw it; it was gone by 1997, branch is capped.
- a radiator in the attic, 50 square ft, valved off.
- a radiator in my upstairs office/sleeping porch, removed during a down-to-the studs renovation. 51 sq ft.
- the hallway radiator, removed and not properly reinstalled during floor refinishing. 30 sq. ft.None of these are missed due to the much improved insulation.
-Matt0 -
In other Michigan News:
I'm finally getting somewhere. Contractor #3 showed up yesterday and toured the place. He was the first person to be truly intererested in my radiators, and he clearly had lots of experience. I learned a lot of things, assuming they're all correct in the first place, an that I understood him right.In no particular order:
Knockdown radiators often leak after a decade or so; factory-assembled and -tested models last longer.
A McLain will last 20 years, a Burnham will last 30. The difference is push nipples on the latter.
[I might believe that. My old boiler clearly relied on something similar to on O ring to remain sealed. At 32 years I ain't complaining]He'll rent a 'stair walker' to get the new boiler down the stairs.
My pipes are in good shape, and the system looks built right.
He'll not unscrew the old elbows but shatter the cast iron with a sledge hammer and a helper with a second hammer bracing the other side.I need proper venting on the main, and then use adjustable vents on the radiators. They're old, replace them all.
I thought all that sounded good, until he got to the part where he has time to do it in October. Last year, I turned the heat on September 30th; the latest is the end of October. If that's the "plan" in July, that scares me.
So I'm on the fence here; on the one hand, the guy clearly knows his business — he could rattle off vent models and boilers off the top off his head — but the timeline, and how easily it could slip, is a problem.
But read on.
-Matt
0 -
I have mentioned that three contractors who came to bid on the job… that doesn't count the "other" large local firm that does boilers; they could send their guy out to take a look .. in early September. No thanks.
Contractor #1 came through with a proposal today. He's with a large firm, and he's indicated he's willing to work with me on the details. I'll spell it out below.Contractor #2 sent a quote quickly. I know we're not supposed to discuss numbers here, but I think it's OK to day I wasn't too pleased when he quoted one number during the visit, and went up nearly three grand overnight. But it was kind of where I expected it; roughly twice the cost of a boiler if I bought it. Which sounds about right to me. It takes a lot of investment before someone is ready to do a job like this.
The deal breaker here is "piping will be done in copper" like we hadn't even spoken the day before.Proposal #1 was, surprisingly, approximately the same amount as #2, it just took a week to get it.
It reads, "Installation of 1-Burnham model PIN6NI-HEZ pacakage steam boiler, 175 MBH input. Provided with low water cutoff and damper. Near boiler piping will be replaced. Boiler will be delivered unassembled and will be built on site. Pricing will also include permit cost, removal and disposal of old unit."It's light on details, but I think the price is fair, I like that it's a Burnham, and I really like that there's a company behind it with a deep bench and an on-call policy. I'm not always home, and Madame is happier with a number to call.
I had a brief exchange with the gentleman and he thought going down one size in the boiler would not be a problem. This Burnham (6 sections) is almost an exact replacement of the capacity of my EG-50 (5 sections, 7 burner tubes). I'll be better off with a smaller unit.
My question to the experts: Does that sound right? Should I push for a pre-assembled unit? Should I go with a SteamMax rather than the old Independence unit?
Should I specify the near-boiler piping kit that Burnham sells? Should I push for a drop header? I'm not worried about a few hundred dollars extra, or a couple grand, if that's what it takes for a first-rate job.
On timing, he said that "quickest he could get the boiler is the last week of August; installing takes 3-4 days, could be done that week of first week in September." That sounds reasonable.
I'm inclined to go with these guys.
Thanks as always for the interest and the support.
-Matt0 -
A side note, but it may be of interest:
Last night, after the "I can do it in October" business, I got sufficiently worried to think again about doing the job myself. I'd rather pay a few grand extra, so long as I know it's done right. But not that late in the game.
Anyway, after searching on Youtube a bit, I found a gentleman in New York [BobsPluminbVideos] who cuts old cast-iron fittings with carbide Sawzall blades, then peels them off the threads of the remaining plumbing. I thought that looked hopeless for an amateur, but then I remembered my copper piping and figured I could do the sensitive cuts slowly and by hand.
First I cut the old two-inch copper tube off its cast-iron reducer. I used a strap so it wouldn't get away from me.
Then I cut the remaining stub out of the cast iron, slightly damaging the threads. I think it should be OK; the only issue being that we know have effectivelly reduced the main to [EDIT: The inner diameter of the copper pipe is 2-1/4 inches, not two.]On the other hand, it worked OK for 30 years, so if I were doing the job, I'd probably just order an EG-40 and figure out how to connect to it. I'm glad that it looks like I won't have to. The professionals will, I hope, cut the reducer out and use the whole 2-1/2 inches… I think the pipe looks pretty clean, for having been installed 95 years ago.
1 -
For what it's worth I chose a WM after cutting a rotted Burnham out of my basement that had rotted out twice in 8 years according to the records on the boiler (I had just bought the house).
Now I'm not saying that boiler wasn't abused but it certainly left a bad taste in my mouth. Not literally.
Now I'm also not around these things all the time. I only have my own experience and the ones I see rotted out on this forum.
But for me....WM or Peerless.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
2 -
From what I've read, it's a matter of water chemistry. Here in Michigan, we have water, water, everywhere, and it's soft… our water heater, even though I never changed the anode, lasted 25 years, just for an example.
So if guy #3 tells me he puts them in and they last 30 years, I kinda believe him.
I found a Burnham video showing the assembly of a large boiler.
This looks righteous.0 -
What happened with guy number four who had Dan's books and understood what EDR is?
0 -
That was guy #3 and he can get to it around Christmas…
0 -
hi Matt! I lived within 90 minutes of you for 45 years but now I live in Nj, which I consider to be the residential steam capital of the US.
Here’s some miscellaneous input for you, I just read your thread for the first time.
- In your first message you said someone taught you to drain your boiler. What did they teach you?
- Measure your radiators, get the total and then forget all that BTU math I saw you trying to do—just compare that value to “net sq ft of steam” which is provided by all manufacturers on their boilers. That number is already too big so if you are between two boilers in size, 100% pick the smaller one. Don’t measure your pipe. Don’t include removed radiators.
- Yes you may very well already know more than any current HVAC contractor in your area about steam.
- Based on what I just read above, buy a boiler from a local supply house and install it yourself. You have plenty of time to install it (they all come with instructions that your contractors probably have never read). You have time to buy any tools, learn to use them, install it wrong, figure out what you did wrong, fix that, pull a permit, get it inspected, fix whatever irrelevant minor things the inspector finds and fix that. Or you can let months pass waiting for contractor number 3 who we aren’t even sure knows what he’s doing.
- Buy a Peerless (my preference) or a WM
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
-
back ordered until September though 😅
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Even if its backordered couldn't he get a copy of the installation instructions and start getting all of the near boiler piping correct? That way by the time it does arrive he can just plop it in place?
0 -
» back ordered until September though 😅
Ya I noticed that, too. So quickly we can go from all-the-time-in-the-world to hair-on-fire.
Were it just me, I'd risk it and plumb in an EG=40 myself.But it ain't, and having a good-sized company with a call-in policy is great for those times when I'm on travel and the missus has to deal with a failure. That's a big part of it right there.
They've already agreed to go from an Independence 6-section to a 5-section model, good for 358 sq ft EDR, so I am going to go that route. I was pleasantly surprised by the pricing, the money is in the checking account, and every time I pull on a short, my shoulder reminds me that it didn't like hauling the old boiler sections out of the basement. I'm not fifty any more ;)
I will try to pursuade them to change two things: (i) to buy the packaged boiler, since the IN5I will actually fit through all doors, at 21 inches wide. And (ii) to install a drop header, or at least just buy the Burnham piping kit and install it.
Once it's installed and working like it did with the old one, I'll swap out all the old radiator vents and set the system up properly.I might add that this is not the ONLY thing that needs fixin' at my house, plus there's that pesky day job that keeps making demands on my time…
-Matt
0 -
Based on my time here I wouldn’t buy an Independence but that’s admittedly anecdotal
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
yes and learn the manual and call around to local supply houses to find a Peerless or WM in stock
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 431 Carbon Monoxide Awareness
- 127 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements