Pigtail question regarding Gauge on residential one pipe steam
The port off front of boiler has a stem that rises up to a Tee fitting. Off to one side it has a pigtail for the pressuretrol and off the other side of the Tee it goes directly into the 1 to 30psi gauge ( that must be 30 years old). The dial has ever moved to my knowledge and the pressuretrol is on the lowest setting - QUESTION: should the gauge have a pigtail since my service tech has never mentioned it even when he last checked the pigtail, which was fine? I know the tech added some water to the pigtail when he re-installed it
Regards
RTW
Most gauges say on the face that it has an Internal syphon. But mots think for longer gauge life it should be on a pigtail. Use all brass fititings on the pressure trol and gauge and you will have fewer problems.
YES, the front of gauge has " internal syphon gauge" printed on it
Lastly, is there a way my service tech can test the 0 - 30psi gauge when he returns to service/clean boiler after the heating season or is this an overkill request? Regards, RTW
That's overkill. Odds are that the gauge will read something, anyway, if the boiler pressure gets up in the 5 to 10 pound range, at which point you have other things to worry about. Leave it.
Most cheaper gauges that I've seen fall under the +- 3-2-3 category. My guess is the cheap gauges supplied with boilers do as well.
That means the middle 50% is 2% accuracy and below that and above are 3%. It doesn't mean it's not accurate at the extremes, it's simply a little less accurate.
So in the middle 50% of the gauge a 30 PSI gauge is within +-0.6 PSI and at the extremes it's within +-0.9 PSI.
If I did my math correctly.
The liquid filled Yellowjacket gauges I bought are class 1 gauges, so 1% across the entire range.
I think they were close to $80 each for the lowside and highside gauges not including a manifold or anything.
But that's not necessary for a steam boiler. Any cheap 3-2-3 gauge is fine, it would just be nice to have an added low pressure gauge in addition to the required 30 psi gauge.
why?
The system will never run with enough pressure for you to get an accurate reading?
@ChrisJ What? You didn't mention the Magnahelics?
They're 2% across the full scale I believe.
Yes,
But what I meant was it's 2% off across the entire range, as opposed to the 3-2-3 gauges.