Pigtail question regarding Gauge on residential one pipe steam
The port off front of boiler has a stem that rises up to a Tee fitting. Off to one side it has a pigtail for the pressuretrol and off the other side of the Tee it goes directly into the 1 to 30psi gauge ( that must be 30 years old). The dial has ever moved to my knowledge and the pressuretrol is on the lowest setting - QUESTION: should the gauge have a pigtail since my service tech has never mentioned it even when he last checked the pigtail, which was fine? I know the tech added some water to the pigtail when he re-installed it
Regards
RTW
Comments
-
Most gauges say on the face that it has an Internal syphon. But mots think for longer gauge life it should be on a pigtail. Use all brass fititings on the pressure trol and gauge and you will have fewer problems.
0 -
YES, the front of gauge has " internal syphon gauge" printed on it
0 -
-
Lastly, is there a way my service tech can test the 0 - 30psi gauge when he returns to service/clean boiler after the heating season or is this an overkill request? Regards, RTW
0 -
That's overkill. Odds are that the gauge will read something, anyway, if the boiler pressure gets up in the 5 to 10 pound range, at which point you have other things to worry about. Leave it.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Most cheaper gauges that I've seen fall under the +- 3-2-3 category. My guess is the cheap gauges supplied with boilers do as well.
That means the middle 50% is 2% accuracy and below that and above are 3%. It doesn't mean it's not accurate at the extremes, it's simply a little less accurate.
So in the middle 50% of the gauge a 30 PSI gauge is within +-0.6 PSI and at the extremes it's within +-0.9 PSI.
If I did my math correctly.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
The liquid filled Yellowjacket gauges I bought are class 1 gauges, so 1% across the entire range.
I think they were close to $80 each for the lowside and highside gauges not including a manifold or anything.
But that's not necessary for a steam boiler. Any cheap 3-2-3 gauge is fine, it would just be nice to have an added low pressure gauge in addition to the required 30 psi gauge.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
why?
The system will never run with enough pressure for you to get an accurate reading?
0 -
@ChrisJ What? You didn't mention the Magnahelics?
0 -
They're 2% across the full scale I believe.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Yes,
But what I meant was it's 2% off across the entire range, as opposed to the 3-2-3 gauges.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements