Intermittent AC locked rotor condition-- resolved
Comments
-
Have you had any power "blinks"?
Do you have a time delay for restart?
This is often a feature in t-stats.
It provides up to a 5 minute delay to restart AC.
Gives time for pressures to equalize.0 -
That unit should have a 5 minute delay built into the PCB.
@DJohanson I assume the unit was tested in low stage?
Is it wired as a legacy setup or as communicating?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
If the voltage is up to spec (not low) and the wire is the correct size and the connections clean and tight then you may need a hard start kit (relay and start capacitor0
-
Do you have a meter to capture (min/max) starting amps to verify the code?0
-
Thanks for your fast response to our AC issue. To your questions, we have experienced some power blinks (Duke Energy) but the lockout issues haven't occurred at those times. (We had installed a whole-house surge protector, BTW.) The Honeywell thermostat does have a 5 minute start delay and is wired "legacy". The tech tested operation during low stage including line voltage and the L1-L2 terminal connections (original installer didn't connect the high stage and we've found that we don't need it.) I'll speak with the tech regarding measuring start current and a hard start kit. Again, I appreciate your suggestions and questions!0
-
IDK about your AC in particular, but some multi stage equipment is designed to start in high stage and then step down to lower stages.
Maybe the high stage start is needed.0 -
The OP's equipment always starts in low stage by design.JUGHNE said:IDK about your AC in particular, but some multi stage equipment is designed to start in high stage and then step down to lower stages.
Maybe the high stage start is needed.
It's a Copeland Ultratech.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
You feel the HVAC equipment is alarming out on a spike that's shorter than a typical DMM can detect?mattmia2 said:
You will need more than the average DMM/clamp meter to measure this, a DMM only samples a few times a second so it doesn't do a great job of capturing peak transients.HVACNUT said:Do you have a meter to capture (min/max) starting amps to verify the code?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
It certainly could be. An analog circuit driving an io pin set to interrupt could detect a very short transient.
I guess we need to know what exactly triggers that code.0 -
mattmia2 said:
It certainly could be. An analog circuit driving an io pin set to interrupt could detect a very short transient.
I guess we need to know what exactly triggers that code.
That's the best I've got from them.
They don't tell you anything useful.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
A list of operating information would help. Superheat, discharge temperature, sub cooling. Minimum on, minimum off.0
-
mattmia2 said:
Do you have a meter to capture (min/max) starting amps to verify the code?
You will need more than the average DMM/clamp meter to measure this, a DMM only samples a few times a second so it doesn't do a great job of capturing peak transients.
If I really need it, I break out the 179.0 -
I've had a 179 since 2002, but I don't have an amp clamp for it.HVACNUT said:mattmia2 said:
You will need more than the average DMM/clamp meter to measure this, a DMM only samples a few times a second so it doesn't do a great job of capturing peak transients.HVACNUT said:Do you have a meter to capture (min/max) starting amps to verify the code?
My pos Fluke 17B which is not true RMS can capture min/max amps. I use it on every maintenance and it hasn't failed me yet.
If I really need it, I break out the 179.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
The manufacturer most likely wants around 6-8 degrees of subcooling and 7-9 for superheat in low stage, going from memory.pecmsg said:A list of operating information would help. Superheat, discharge temperature, sub cooling. Minimum on, minimum off.
What the OP actually has, along with the type of metering device and lineset length and evaporator location, would be nice to know.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
If it is somehow detecting the compressor failed to start within a minute then that is a long enough period for min/max on a dmm to capture.ChrisJ said:mattmia2 said:It certainly could be. An analog circuit driving an io pin set to interrupt could detect a very short transient.
I guess we need to know what exactly triggers that code.
That's the best I've got from them.
They don't tell you anything useful.
The next step would be to look at the schematic and maybe the control itself and see what it has connections to that it uses to decide the compressor didn't start. Does it have a way to measure line voltage? Does it have a way to measure current? Is it only connected to pressure switches and some thermistors and is inferring that the compressor didn't start by what it is reading from those senseors?0 -
I've never been able to find one.mattmia2 said:
If it is somehow detecting the compressor failed to start within a minute then that is a long enough period for min/max on a dmm to capture.ChrisJ said:mattmia2 said:It certainly could be. An analog circuit driving an io pin set to interrupt could detect a very short transient.
I guess we need to know what exactly triggers that code.
That's the best I've got from them.
They don't tell you anything useful.
The next step would be to look at the schematic and maybe the control itself and see what it has connections to that it uses to decide the compressor didn't start. Does it have a way to measure line voltage? Does it have a way to measure current? Is it only connected to pressure switches and some thermistors and is inferring that the compressor didn't start by what it is reading from those senseors?
The PCB used is made by Emerson / Copeland, not by Goodman / Amana and the diagram shown can't be trusted. At least it couldn't back in 2017 when I metered out the board to wire in a condenser fan control on mine. And even that was only a crude diagram showing where the fan, compressor etc wire into the board.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
ChrisJ said:mattmia2 said:My pos Fluke 17B which is not true RMS can capture min/max amps. I use it on every maintenance and it hasn't failed me yet.
Do you have a meter to capture (min/max) starting amps to verify the code?
You will need more than the average DMM/clamp meter to measure this, a DMM only samples a few times a second so it doesn't do a great job of capturing peak transients.
If I really need it, I break out the 179.0 -
ChrisJ..... lineset is 20' long, evap coil is ~3' higher than condenser. Txv metering. Downflow furnace installed with ample supply and return ducting. At 93F outside temp on low stage, 325psi and 142psi, SH at 8 and SC at 2. Typical run times that day were at least 1 hour. I did notice a current loop on the control board which likely measures the compressor current, if that helps any.0
-
Separate subject but SC should be 6-8 from what I recall, so the system is a tad undercharged.DJohanson said:ChrisJ..... lineset is 20' long, evap coil is ~3' higher than condenser. Txv metering. Downflow furnace installed with ample supply and return ducting. At 93F outside temp on low stage, 325psi and 142psi, SH at 8 and SC at 2. Typical run times that day were at least 1 hour. I did notice a current loop on the control board which likely measures the compressor current, if that helps any.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
-
heatandair said:Talk to your electrician about the surge protector, sometime changes in amp draw when it changes stages will cause problems1
-
Locked rotor condition again; called the technician to investigate. While testing the compressor windings, found a loose spade connector on circuit board powering the condenser fan. Not sure why this wouldn't trigger a high pressure lockout instead of "locked rotor" but it's now trouble free for past 2 weeks. Thanks everyone for your comments!3
-
-
Hi! I have the same problem on an Amana 2-stage. Has yours stayed trouble-free from this problem??
Thanks for your help! Nick0 -
Did you ever figure out the problem on your unit?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Maybe the pressure switch isn't interlocked with a time delay correctly and when the pressure falls because the compressor shut off it resets and tries to restart the compressor before it has equalized so the compressor then fails to start.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements