Vent Testing and Repair
As I mentioned in the discussion "Gorton Air Vent Quality", I had so many vent failures that I found it necessary to not only pre test Vents before installation but to repair the existing failed vents because the high number of replacement vent failures. First, I will explain the components of steam vents. Second, how they operate. Third, Requirements
for their proper operation. Finally, Testing typical failures and repair.
Components:
Each vent regardless of type has:
1] Input opening
2] Case or Housing
3] Seat with air port
4] Pin/head and float
5] Thermal element
6] Output opening
[See Vent Diagram]
The operation:
1] Low Temperature position:
The thermal element which is attached to the case, is in a contracted position and the pin
or head attached to it is not blocking air from passing out of the seat air port. The
amount of air entering the input and leaving the radiator is determined by the output
opening size. This opening can be fixed, interchangeable or adjustable.
2] Closed position:
The steam and or heated air entering the input will heat up the case and the thermal
element attached to it. This transfer of heat will cause some of the steam to condensate
and flow back through the input opening. The case and thermal element will heat up to
a higher temperature. The thermal element will expand forcing the pin / head into the
seat with enough force to close the air port and preventing steam from escaping. In the
case of a bellows system, the expansion and force is determined by it’s volume and the
amount of and type of chemical [usually alcohol] contained in it. In the case of a bi
metal system, the expansion is determined by it’s length and the closing force is
determined by it’s thickness and with.
Requirements:
1] A vent when attached to a mains pipe or radiator must pass cold air within a specified
pressure level without and below closing temperature without closing. In most cases this
should not be more than 3 psi. The closing temperature is normally 140F and is close
to the case temperature. Within 4 to 5 degrees.
2] The thermal element must be positioned so that when the closing temperature is
reached it’s expansion distance is equal to the closing distance which is the difference between the low temperature position and the closed position of the pin / head. The case temperature with steam present is determined by the ambient temperature, the temperature transfer coefficient of the vent, the transfer of heat between the input opening and the radiator or pipe and the steam temperature [212F to 218.5F between 0 and 2psi]. The proper closing distance cannot be determined accurately unless the tolerance or deviation of the pin / head dimensions is known.
3] The movement of the pin / head into the seat should be with little friction
Test Setup: [See Test setup and options]
1] Induction Cooktop: heat source
2] Induction adapter plate: non iron heating
3] Pressure cooker 1930 15 Qt: Steam generator
4] Pressure release valve: protection
5] Siphon SS 1/4" with loop: protection
6] Gauge 3 psi 1/4": Monitor pressure levels
7] Tee 1/4 SS: Connections
8] Valve ball SS 1/4": Steam flow control
9] Adapter M/F SS: 1/4" to 1/2 or 1/4" to 3/4" or 1/4" to 1/8:
10] Elbow 90 SS: 1/4 to 1/2, 1/4 to 3/4"
11] Coupler SS 1/4"
12] Type K thermocouple and meter: monitor case temperature
Using this test set up each Vent type can have its shut off case temperature which is
close to the thermal element temperature by throttling the valve and watching the
gauge needle fluctuate with steam turbulence passing through the tee to the vent and
looking at what temperature the turbulence stops. The shut off temperature can also be
determined if the vent closes too fast to monitor the temperature by turning off the
pressure cooker after the vent closes, and wait to see at what temperature the vent opens.
This can even be a negative temperature as the pressure cooker cools it makes a vacuum.
This setup can determine the Shut off temperature of any vent and if mains vents would pass or fail in the field. It will not determine pass or fail for radiator vents which are
apparently affected by the connection to the cast iron radiator. Pass or fail for radiator
vents were determined by their operation when connected to actual radiators. I have
obtained a small radiator for this purpose in the future. Must determine how to connect it
to the pressure cooker.
Common Failures:
1] Will not Pass air:
For out off box [OB] vents that do not pass cold air the cause is the pin / head is
stuck in a position blocking the seat hole. Members of this site have mentioned that
Gorton #2 vents will not rattle when this occurs. For in service vents foreign substance
blocking the seat hole. [See G#2 OB]
2] Will not close:
For OB vents that will not close the cause is the expansion distance or force created
by the thermal element is not long or great enough respectively for the pin / head to
reach the closing position or force
3] Will not stay close during the steam cycle:
For OB vents, the vent is closing partly do to pressure not just temperature and will
open as the case temperature and pressure drops
Test and Repair: Gorton vents
I do not at this time whish to go into details as to how the units were unsealed
[Un soldered] and resealed. Here is a summary of the repair procedure:
1] Open unit on hot plate. Examine head and post position in bi metallic strip. If the
head and float are dislodged, replace it in strip hole. For in service vents clean heads
and seat holes with CLR.
2] Measure the closing distance using the bottom of case as reference. Mark the float
bottoms so that you measure from the same location. Example: Low temp = 0.76",
Closed position = 0.92", Closing distance = 0.16"
3] Attach sensor to bi mettallic strip and freeze the vent to determine the fall out
temperature. Example: 53F was measured.
4] Heat the vent and determine the closing temperature of strip. 162F was measured.
5] Cool vent strip to 85F and adjust the strip to close at 140F. A change of Low temp
position from 0.76 " to 0.83" was made. The vent was heated to verify 140f closing.
6] Cool unit to determine new fall out temperature. 30F was measured.
7] Seal vent and rest for leaks, closing pressure and closing temperature.
Conclusions:
I was able to repair 18 of 32 Gorton radiator vents. 3 could not be repaired because of
physical damage and soldering issues. Some were in service so their was corrosion issues that were not reversible. All were purchased within the last 5 months.
1] All OB Gorton vents that closed when turned upside down and would not close when
when they reached 160F case temperature or at all, have closing distances that are
greater than the expansion distance.
2] All OB Gorton vents that had head float fall outs, were due to closing distances that are
3] There is no way to know the correct closing distance without knowing the head / float
tolerance. However, If you repair enough vents you can guess the distance consistently.
4] The G#2 vent I referred to was sent as a replacement for a OB failed vent.
I would like to thank the members of heatinghelp for their information on steam heating. You saved me a lot of time money and more important, reputation.
WaherFishin_RoddelcrossvCaptain Who
  • ARobertson13
    ARobertson13 Member Posts: 149
    I would like to add in reference to the Gorton G#2 vents and shipping handling issues causing dislodged floats, this is not the case. If you have vents with "fall out" temperatures of 53 degrees, the floats can be dislodged standing still as it was when I cooled one down.
    ethicalpaul Member Posts: 8,920
    edited March 2024
    Nice. I LOVE that pressure cooker test rig!!
    While you had those Gorton #2s open, did you ever happen to see if the "float" actually "floats"? I found in their #1, it sinks like a stone.
    Long Beach Eddelcrossv
  • ARobertson13
    I already closed that vent. I have one that I opened last year. The test that was done by some one on the internet was not proper. The correct way to test the float is to open the vent mark off the closed position.
    Then immerse the entire vent in a glass beaker of water and see if it rises to the closed position.
    edited March 2024
    Thanks! Tell me if you think my test was proper if you would. I daresay this "float" ain't gonna rise no matter what.
    https://youtu.be/XXevhGi02q4
    BobC
  • ARobertson13
    I just remembered that I did a test on a G#1and it did not float. As for the G#2 Archemede's principal states that if a body weighs less than the volume of water it displaces it will float. I have this float Head assembly at 2.69 oz and the water it displaces at 2.35 oz max so it cannot float.
    ethicalpaulLong Beach Ed
  • RTW
    RTW Member Posts: 285
    Not sure if this is the right thread to ask this question, but if the main vents / radiator vents off the shelf function properly, does boiling them in a white vinegar solution for three to five minutes ( as mentioned before on this site) every 2 or 3 years help for function and longevity? That is assuming you have good water and a well-maintained steam heating system & installed boiler, or just forget about it?
  • ChrisJ
    ChrisJ Member Posts: 17,477
    Even with bad water as long as the boiler is piped correctly and producing dry steam there shouldn't be a reason to soak them.  The only thing they should ever see is distilled water which doesn't have minerals.
    Jamie Hall Member Posts: 27,498
    The main vent on the system Cedric powers is a Gorton #2installed about 20 years ago, augmenting a Hoffman 75 installed around 95 years ago. Neither one has needed any maintenance...
  • ARobertson13
    Chrisj and Jamie Hall are correct. If you look at my post where I discuss common failures: 1] Will not pass air. I separate [OB] out of Box from in service conditions. I should point out that other members have reference a blue foreign substance in both #1 and #2 Gorton vents that clearly did not come from any heating system. I omitted this from my post. See picture This blue film some believe to be solder flux is not present at the 1/2" input and is present on one side of the float. I did not use any heat to open this vent last year Nov 2022 to insure that I did no heat damage.
    Waherethicalpaul
  • ARobertson13
    Also, I use CLR not vinegar
  • TKPK
    TKPK Member Posts: 74
    did you happen to document the closing and opening temperatures of Gorton 1 & 2s.
    I cannot find the spec and would be interested to know.
    Assume 1-2 oz of pressure / vacuum
  • ARobertson13
    TKPK, Sorry for the slow response. I forgot about this discussion. If you go to the supply House site and look up the vent in question, they mention the basic specifications: 140F to 240F. This is not why I chose 140F. If you have a vent on the mains that opens well below 140F, It probably will not open within the cycle off time. This will reduce the steam transit velocity to that of an unvented mains. For the radiator vents, a closing temperature far above 140F will result in a vent that will not close when the radiator is filled with steam. I just finished testing 12 radiator vents #4, #5, #6 and Ds. [I have 85 vents radiator, fast and master in my building and had to finish a project started last season] 10 of them had a closing temperature of around 170F and none of them closed when steam from the radiator entered them. They just passed steam. I opened them cleaned and made adjustments to the bimetal strips and all but one closed. I will go into a more detailed explanation as to why this happens in the future. I do not think that people in the steam community are testing these vents. Just putting them in and the residents just assume that is how things are and tolerate it.
    ethicalpaulTKPK
  • ChrisJ
    I'm confused, how could a device that closes at 170f pass 212f steam?
  • ARobertson13
    Chrisj,
    It can't. This has to do with understanding on what goes on in a radiator, mains and vents. I will explain this at a later date.
  • ARobertson13
    Correction, I should have stated that it can. Here is why: see diagram
    1] When steam enters a vent or any closed metallic container, the temperature of the steam is determined by the pressure in the container
    2] The steam will make contact with the walls of the container or case and transfer heat to the case resulting in condensation and an increase in the case temperature and indirectly the expansive element [bimetalic strip, bellows or cylinder]. The temperature of the case and expansive element is determined by the thermal conductivity of the metal case, case thickness, steam temperature and air temperature. I have measured a 3 to 5 degree difference between the case and expansive element.
    3] The case temperature must reach a level that will heat the expansive element enough to make the head or pin contact with the seat opening and do so with enough force to keep it closed under pressure [negative or positive]. This is determined by the coefficient of expansion and mass [or thickness and length] of the expansive element.
    So the steam can be at 212F or 216F and the vent will fail to close because the expansive element is not hot enough or will not stay hot enough. I have tested vents with cylinders that would cycle open and close because the cylinder or bellows would close, lose heat through case convection, then open letting in more steam heating up the cylinder causing it to close. This would happen anywhere from 2 minutes to every 25 seconds.
    Long Beach Edwz25
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,843
    edited February 2025
    This is a fact that few understand or consider. Vents, even when closed under steam, do "breathe". Some brands more than others. This causes loss of steam and lowers boiler water. Customers complain that vents hiss and this is often normal cycling.
    I find Gorton valves waste more steam than Hoffmans. Perhaps the imprecise adjustment of their bi-metallic strip vs. a more immediate closing alcohol sylphon in others. Most valves are designed to close at fairly low temperatures, but they still tend to cycle in some systems.
    I'm sure this varies on room and condensate temperature, radiator configuration and steam quality.
    Captain Who
  • ARobertson13
    My point is this: Vents that do not close when steam enters them are of no use to me or any contractor that is maintaining or balancing a steam system. They cause overheating. As for those vents that cycle, the pinging noise they make are annoying to residents. I purchased about 20 vents #4, #5 and #6 this heating season. Not one of them would close below a case temperature of 165F. I had to open and adjust all of them because I dare not install them in my clients residents apartment. What do I have to do, Manufacture my own vent. It looks like that is the solution. The manufactures will keep selling these non closing vents if we keep buying them.
    You confuse me on a couple points.
    First, vents that do not close to steam do not cause overheating—they cause loss of water, even worse. But they do not cause overheating—the radiator is full of steam either way.
    Second, I'm not sure why you believe that vents should close at a case temperature of 165F. Shouldn't they close at like 200, when the vent gets steam in it?
    I think if your units' radiators are getting too hot even with a #4 on them you might consider enclosing them
  • ARobertson13
    ethicalpaul, Did i say vents should close at 165F? No. I said the ones that I got during the last heating season did not. As a matter of fact, vents that do not close at around 140F will not close in most radiators at pressures below 1.5 psi. If you read the comments that I made earlier, you would not be confused. As I explained to another member, you have to understand what is going on inside radiators, mains and vents. If a vent is closed, the amount of steam entering a radiator is determined by the amount of steam that is condensed by the radiator and this along with the radiators material, thickness and outside air temperature, determines the radiators surface temperature. If a vent is passing steam, more steam is entering and just like a pipe passing steam, the temperature of the surface would be higher than if the vent is closed.
    Long Beach EdCaptain Who
    Sorry but I am still confused by what you're saying, that's OK!