Glycol mixture 70/30 initial fill pressure
JHK
JHK Member Posts: 26
In a glycol piping loop for chilled water or a dry cooler (Liebert) do you still want the highest point under 3-4 psig with the pump off or do you want to keep it at a higher pressure at the highest point?
    Jamie Hall Member Posts: 27,214
    Glycol or not makes little difference. However... be sure that the pressure at the inlet to the pump when the pump is running is also at least 3 to 4 psi.
    pecmsg Member Posts: 7,020
    How many ft to the highest point, top to bottom?
    hot_rod Member Posts: 27,290
    Hopefully not a 70% glycol, 30% glycol mix?
    At least 5 psi pressure at the highest point in the system. 10- 12 psi is a common fill for 1 and 2 story buildings.
  • JHK
    Thanks for the replies, I do appreciate it. The height is 18 feet. It is 70% water.
    18 X .433= 7.8 psi to lift water to the high point. add 5 for 12.8 psi at the fill valve. 12 psi is fine.
    Most expansion tanks and fill valves come preset at 12 psi. But always confirm the tank precharge.
  • JHK
    Ok, thank you.