Glycol mixture 70/30 initial fill pressure
JHK
Member Posts: 19
In a glycol piping loop for chilled water or a dry cooler (Liebert) do you still want the highest point under 3-4 psig with the pump off or do you want to keep it at a higher pressure at the highest point?
0
Comments
-
Glycol or not makes little difference. However... be sure that the pressure at the inlet to the pump when the pump is running is also at least 3 to 4 psi.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
How many ft to the highest point, top to bottom?0
-
Hopefully not a 70% glycol, 30% glycol mix?
At least 5 psi pressure at the highest point in the system. 10- 12 psi is a common fill for 1 and 2 story buildings.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks for the replies, I do appreciate it. The height is 18 feet. It is 70% water.0
-
18 X .433= 7.8 psi to lift water to the high point. add 5 for 12.8 psi at the fill valve. 12 psi is fine.
Most expansion tanks and fill valves come preset at 12 psi. But always confirm the tank precharge.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Ok, thank you.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements