Bevel steam trap
Has anyone seen these traps before? It appears to be a bevel configuration trap, in a right angle piping. This is an end of line trap, after the last longitudinal branch on a 1916, 2-pipe, vacuum return system. Infrared imaging shows it being 214’ on inlet and outlet, assuming a failed open trap.
thom


Comments
-
Seems to be some raised lettering on the other side of the valve body. Would have been helpful to see.
But looks unique enough that someone who has encountered or seen it before will be able to identify it.0 -
Sadly my phone died after this pic. I will be sending a colleague in to take additional pictures.
My initial concern was that the trap was bent by the piping not being supported adequately, but it does look to be solid.0 -
-
If possible, since that's on the end of a steam main, I'd use an F&T trap. Also, those bushings in the run of the tee before the pipe turns down to the trap are causing a water pocket, which would cause banging. That needs to be corrected when the trap is replaced.Jamie Hall said:Might be easier to replace it with a normal radiator trap...
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
I agree, I missed the concentric bushing until I reviewed the pictures. Most interesting in considering this, this is in an area that does not receive steam... the floor and wall cavity where the pipes exist are warm-to-hot, but the steam does not reach the radiators above. This situation has been so long standing that no-one even asks why there is no heat. Most of our original infrastructure is under concrete or behind brick in the walls.
This immediate area has a 1980s renovation, several abandoned pipes and very little heat.0 -
You need a Steam Guy. Where are you located? We might know someone.......Tommi68 said:I agree, I missed the concentric bushing until I reviewed the pictures. Most interesting in considering this, this is in an area that does not receive steam... the floor and wall cavity where the pipes exist are warm-to-hot, but the steam does not reach the radiators above. This situation has been so long standing that no-one even asks why there is no heat. Most of our original infrastructure is under concrete or behind brick in the walls.
This immediate area has a 1980s renovation, several abandoned pipes and very little heat.Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I am in Toronto, ON.The trap is a Bestobell GMR30
-
-
@Tommi68
I agree with much of the above.
Trying to repair this trap, its location and the angle it is located, not to mention in time you are allowed to do the job is the biggest problem.
Replace it as @Jamie Hall suggests above.1 -
-
Some issues are at play, the pipe seems to sag in places along its run. Some dips and the concentric bushings will need to be addressed. And every other pipe in the building uses F&T at the end of line. I’ll be contacting our mechanical contractor for the rework, they will send a good plumber so I will advocate to replace the bushings for a nipple and reducing coupling.I wasn’t looking for the no heat issue; no one even thinks about this anymore, that’s just how it is. I was doing different work and had a thought to look under some access hatches that I don’t look in more than once each decade. I have been searching for the EOL and drip legs on the 7 steam mains since October and found almost a dozen that have missed any service or trap inspection.0
-
You need a reducing ell, not a reducing coupling. The reduction has to take place in the vertical section or else you would need an eccentric coupling which may be difficult to find.Tommi68 said:Some issues are at play, the pipe seems to sag in places along its run. Some dips and the concentric bushings will need to be addressed. And every other pipe in the building uses F&T at the end of line. I’ll be contacting our mechanical contractor for the rework, they will send a good plumber so I will advocate to replace the bushings for a nipple and reducing coupling.I wasn’t looking for the no heat issue; no one even thinks about this anymore, that’s just how it is. I was doing different work and had a thought to look under some access hatches that I don’t look in more than once each decade. I have been searching for the EOL and drip legs on the 7 steam mains since October and found almost a dozen that have missed any service or trap inspection.
I don’t know if I’d want the job of repiping that. A lot of floor would have to come up.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Nomenclature question: I presume the ‘reducing ell’ is a reducing 90’elbow.You need a reducing ell, not a reducing coupling. The reduction has to take place in the vertical section or else you would need an eccentric coupling which may be difficult to find.0 -
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 19 Recall Announcements