Gas hot water boiler
Mplumbermd1
Member Posts: 1
in Gas Heating
I recently replaced my oil fired hot water boiler with a gas fired hot water boiler. My problem is that I have 2 line voltage thermostats and my new boiler is set up for liw voltage (24 volts). To replace the thermostats will involve breaking open walls and ceilings, I’d rather not do that. Is there a way I can still use my live voltage (110 volts) thermostats with this new system? Any help would be greatly appreciated. Thanks
Wireless thermostats.Bob Boan
Disconnect your line voltage stat and take it off the wall. Splice a short piece of low voltage cable to the line voltage cable and reconnect it to the thermostat (or better yet to a new low voltage stat) and mount the thermostat on the wall. Find the line voltage cable at the boiler and splice some low voltage cable to it and connect it to the boiler where the low voltage thermostat would connect.
MAKE ABSOLUTLY SURE YOU HAVE THE RIGHT CABLE AND THAT NO OTHER LINE VOLTAGE OR CONTROLS ARE WIRED TO IT.
you should ring out the cable with an ohm meter to make sure you have the right cable. if in doubt call an electrician0 -
There are many ways of getting a new 18/8 cable pulled with little if any damage!
Many of the new thermostats need a common wire. So you may need 3 conductors
If possible pull some new 24v wire
maybe some 5 conductor for AC option down the roadBob "hot rod" Rohr
Or leave the line voltage thermostats and use them to control a relay or relays in the basement. They control the coil, and the 24 VAC boiler circuit through the normally open contacts.Br. Jamie, osb