Boiler Replacement
Marij
Member Posts: 5
We are replacing our boiler in the coming months. I asked my installer about recent HH recommendations for installation including using at least two risers, increasing the riser size, and piping a drop header. His reply was that he would follow all manufacturer’s recommendations and not make changes to our near boiler piping. Not sure if I should or how I would push for any of these HH recommendations. Very few steam installers in my area. I would appreciate hearing from the HH community on this topic.
Three photos added above.0
I'm wondering if there is encapsulated asbestos on the old header. If not, I'd try to find a way to use it.All Steamed Up, Inc.
Consulting0 -
A bit unusual -- I'd bet that the present boiler is a replacement for a previous one. I'd leave the near boiler piping be, just as is, to the extent possible. It would be rather fun to know just what is under the higher "header"... but I wouldn't disturb the insulation if I didn't have to.Br. Jamie, osb
Also, a second bid (significantly higher) described two proposals with std and better. The “better” option included “piping upgraded from basic specifications”; dropped header design; cleaning solution/chemical cap; upgraded pressure control and gauges; electronic and float cutoffs; king valves; mud leg blow down capability; removable/cleanable returns; new vents; and viewable skim port. I would love to know if I should include some of these upgrades. Thanks!0
@Marij if you can afford the upgrades and are planning on staying in the house a while i vote yes to the upgrades2
Usually both tappings are preferred for production of dry steam and better performance of the system over all . The dryer the steam the better your system will perform and using both tappings almost guarantees your boiler is producing the driest steam it can and the existing velocity out of the boiler will be extremely low ,aside from the risers ,the header size that is also very important . I also see what seems to be a hot water loop . A much better alternative would be to use a Weil McLean w a tankless coil and pipe as a separate closed loop hydronic system in the long run there will be much less issues w mud and sediment and the use of a fairly inexpensive low maintenance wet rotor circulator can be used instead of the correct pump for a open loop which would be a fairly expensive 3 piece brass body circulator which requires some maintenance.Unless your bidding contractor has done a edr on your existing radiator to ensure that the correct size boiler is installed and to verify the existing one was sized properly .
As for myself only under 120 btu uses one riser and that would only apply top tapping w a min of 3 inch tapping everything above generally are piped using both risers ,as for a drop header I generally will install where it’s serves it purpose and allows me meet the recommended 24 inch header height and or makes it easier to connect to existing mains . Generally real steam guys do the edr and don’t size replacement boiler off the existing it s not the way it’s done at least by myself and the few who I would recommend and there are not many .
Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
The insulation really needs to be removed but from the looks of it it should be repipe with a new header using both tapping . There’s some thing funky going on w the large steam drum and the if any drip off it .
Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Thanks all!@109A_5, we noticed dark soot accumulating under the back corner. Burner tubes in that area are rusty and C02 level high. Boiler is 33 years old.@clammy - 261 calculated EDR (plus hot water loop). The hot water loop heats2-story addition with baseboard and have had to replace pump once or twice in past 25 years or so. Your thoughts very helpful. I am just unsure on how to raise some of these considerations with our installer.0
Adding new photo showing higher”header” now that old boiler out and i
insulation cut off. 0 -
From the looks of it I would repipe the header and not use what’s there and just start over w completely new near boiler piping using both riser and a proper equalizer . I would still suggest a tankless for the baseboard loop .
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating2 -
I agree...Stockham...they made great Valves for many years. Last used them in the Early 1990s. Still in business...says Made in 'Bama...Maybe.. Mad Dog 🐕1
- 87.2K THE MAIN WALL
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 75 Pipe Deterioration
- 6.4K Radiant Heating
- 15.6K Strictly Steam
