Before and After work was done. thanks for the guidance everyone.
I'm not sure that original piping was completely awful but I can't see enough of it here. The drop header obviously is better.0
Is that header feeding a bullhead tee (two mains fed by one pipe in opposite directions)?
That bullhead tee looks like it was always there. Might be a 2 x 2 x 3.
Maybe a 3" steam riser to it may have been better.
But then that would lead to a 3" header....you have to stop somewhere.
But with tall double drop header and vertical steam riser it should deliver dry steam. Previous postings talked about wet steam.
The heating season will tell.
How did the old piping sound?
What is the boiler model number? Now I see it was a 63-040 -
Your inspector was cool with the drop header? Lucky!
That white main at the top is older probably original, I think it's white from being insulated by asbestos. There were some sounds coming from the system but it wasn't too bad to be honest. My biggest concern with the previous set up was the welded copper pipes breaking in the middle of winter, with the threaded steel I am less concerned about it.JUGHNE said:That bullhead tee looks like it was always there. Might be a 2 x 2 x 3.
I also got appropriate main vents, the previous one was super tiny.0 -
@tsayles50 thank you for allowing me to do the work on your boiler. Here is a picture of the piping heating up with an infrared camera along with the gorton main vents.
3 -
My understanding is that ideally there is no tee and having two separate take-offs from the header is best. One going right, the other left in that picture. I'm not sure why this is the case though? Harder to balance the system maybe?0
Thank you so much @EzzyT!! you did a great job.EzzyT said:@tsayles50 thank you for allowing me to do the work on your boiler. Here is a picture of the piping heating up with an infrared camera along with the gorton main vents.
Probably was piped directly off the original coal boiler and it only had one outlet.0
Luckily you had got Ezzy to straighten it out being most would have left it like it was and given the excuse of well it steams and it,s like that ,now just get it insulated and stay on top of maintaining it properly w yearly maintenance and your good to go for the foreseeable future .
Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1
