Before and After work was done. thanks for the guidance everyone.
tsayles50
tsayles50 Member Posts: 36
Recently had the piping around my boiler fixed. Not pictured are Gorton 1 and 2 air vents for my two main pipes. New CO2 detector. Skimmed the boiler. Blew down the boiler. Demineralizer. New 0-5 PSI gauge.
mattmia2Alan (California Radiant) ForbesMikeAmann
    mattmia2 Member Posts: 17,478
    I'm not sure that original piping was completely awful but I can't see enough of it here. The drop header obviously is better.
  • tsayles50
    I didn't take the best before picture but it was welded copper and only utilized one riser.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,681
    Looks Top Notch..HUGE improvement 👏 Mad Dog 🐕
    tsayles50SuperTech
  • ChrisJ
    ChrisJ Member Posts: 17,519
    Is that header feeding a bullhead tee (two mains fed by one pipe in opposite directions)?
  • JUGHNE
    JUGHNE Member Posts: 11,604
    edited June 2023
    That bullhead tee looks like it was always there. Might be a 2 x 2 x 3.
    Maybe a 3" steam riser to it may have been better.
    But then that would lead to a 3" header....you have to stop somewhere.
    But with tall double drop header and vertical steam riser it should deliver dry steam. Previous postings talked about wet steam.
    The heating season will tell.
    How did the old piping sound?
    What is the boiler model number? Now I see it was a 63-04
    ethicalpaul Member Posts: 8,933
    Your inspector was cool with the drop header? Lucky!
    mattmia2SuperTech
  • tsayles50
    I guess it is. In all my research I didn't come across the phrase bullhead tee. The white header goes in two different directions.
    Does this mean anything specific?
  • tsayles50
    That white main at the top is older probably original, I think it's white from being insulated by asbestos. There were some sounds coming from the system but it wasn't too bad to be honest. My biggest concern with the previous set up was the welded copper pipes breaking in the middle of winter, with the threaded steel I am less concerned about it.
    I also got appropriate main vents, the previous one was super tiny.
    The lack of main venting was probably why your radiator vents were spitting. There was just too much velocity trying to push it all out through the radiator vent.
    tsayles50
  • EzzyT
    EzzyT Member Posts: 1,380
    @tsayles50 thank you for allowing me to do the work on your boiler. Here is a picture of the piping heating up with an infrared camera along with the gorton main vents.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    tsayles50mattmia2SuperTech
    pecmsg Member Posts: 7,284
    I should have recognized your workmanship! :)
  • ChrisJ
    Oh.
    If @EzzyT did the work forget I said anything.
    You can sleep well at night.
    mattmia2SuperTechJUGHNECLamb
  • random12345
    random12345 Member Posts: 504
    My understanding is that ideally there is no tee and having two separate take-offs from the header is best. One going right, the other left in that picture. I'm not sure why this is the case though? Harder to balance the system maybe?
  • tsayles50
    Thank you so much @EzzyT!! you did a great job.
    Probably was piped directly off the original coal boiler and it only had one outlet.
  • clammy
    clammy Member Posts: 3,257
    Luckily you had got Ezzy to straighten it out being most would have left it like it was and given the excuse of well it steams and it,s like that ,now just get it insulated and stay on top of maintaining it properly w yearly maintenance and your good to go for the foreseeable future .
    Peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Mad Dog_2