Connecting taco sr501 and hydrostat 3150
benmoussa3
Member Posts: 2
Hi I have a tankless and circulator 1 on Hydrostat 3150 and another zone on Taco SR501, zone 1 works perfectly, however Zone 2 turns on the Circulator 2 but it doesn't fire the boiler... whoever made this install used the Typical Wiring (Cold Start) and didn't connect 6 (N/O) and 5 (COM)... what should I do in this case? I would like Zone 2 to fire the boiler if thermostat is calling for heat. Thanks
Note: TT on boiler is already used by Zone 1 Thermostat
I wonder if this is the whole of the wiring? But if it is, there's no reason you can't connect 5 and 6 on your zone relay to T-T on the boiler in parallel with any other thermostat or relay (not, however, in parallel with the one already controlling the same relay...)Br. Jamie, osb
Thank you all0
Hey did you ever get this working on your existing equipment? I have the exact same thing that I’m trying to do. Thanks!0
- 15.8K Strictly Steam
Use this one.