Connecting taco sr501 and hydrostat 3150
![benmoussa3](https://secure.gravatar.com/avatar/ead38cf7d2dd43b455b994c41779dce5/?default=https%3A%2F%2Fvanillicon.com%2F8ab269a27ebaaa3b528423c24d1ec823_200.png&rating=g&size=200)
benmoussa3
Member Posts: 2
Hi I have a tankless and circulator 1 on Hydrostat 3150 and another zone on Taco SR501, zone 1 works perfectly, however Zone 2 turns on the Circulator 2 but it doesn't fire the boiler... whoever made this install used the Typical Wiring (Cold Start) and didn't connect 6 (N/O) and 5 (COM)... what should I do in this case? I would like Zone 2 to fire the boiler if thermostat is calling for heat. Thanks
Note: TT on boiler is already used by Zone 1 Thermostat
![](https://us.v-cdn.net/5021738/uploads/editor/rp/o1vaqkeu6y5u.jpg)
![](https://us.v-cdn.net/5021738/uploads/editor/5u/3kzhfildkqsx.jpg)
![](https://us.v-cdn.net/5021738/uploads/editor/f0/nkm89ssmiosp.jpg)
Note: TT on boiler is already used by Zone 1 Thermostat
![](https://us.v-cdn.net/5021738/uploads/editor/rp/o1vaqkeu6y5u.jpg)
![](https://us.v-cdn.net/5021738/uploads/editor/5u/3kzhfildkqsx.jpg)
![](https://us.v-cdn.net/5021738/uploads/editor/f0/nkm89ssmiosp.jpg)
0
Comments
-
I wonder if this is the whole of the wiring? But if it is, there's no reason you can't connect 5 and 6 on your zone relay to T-T on the boiler in parallel with any other thermostat or relay (not, however, in parallel with the one already controlling the same relay...)Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If you want the reverse function of 3150 to operate with both zones, wire per middle diagram, if you just want zone 2 to bring on burner, run power from #4 terminal of 501 to ZR on 3150To learn more about this professional, click here to visit their ad in Find A Contractor.1
-
-
Thank you all0
-
Hey did you ever get this working on your existing equipment? I have the exact same thing that I’m trying to do. Thanks!0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 932 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements