Connecting taco sr501 and hydrostat 3150
Options
benmoussa3
Member Posts: 2
Hi I have a tankless and circulator 1 on Hydrostat 3150 and another zone on Taco SR501, zone 1 works perfectly, however Zone 2 turns on the Circulator 2 but it doesn't fire the boiler... whoever made this install used the Typical Wiring (Cold Start) and didn't connect 6 (N/O) and 5 (COM)... what should I do in this case? I would like Zone 2 to fire the boiler if thermostat is calling for heat. Thanks
Note: TT on boiler is already used by Zone 1 Thermostat
Note: TT on boiler is already used by Zone 1 Thermostat
0
Comments
-
I wonder if this is the whole of the wiring? But if it is, there's no reason you can't connect 5 and 6 on your zone relay to T-T on the boiler in parallel with any other thermostat or relay (not, however, in parallel with the one already controlling the same relay...)Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If you want the reverse function of 3150 to operate with both zones, wire per middle diagram, if you just want zone 2 to bring on burner, run power from #4 terminal of 501 to ZR on 3150To learn more about this professional, click here to visit their ad in Find A Contractor.1
-
-
Thank you all0
-
Hey did you ever get this working on your existing equipment? I have the exact same thing that I’m trying to do. Thanks!0
Categories
- All Categories
- 85.6K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
- 18 Recall Announcements