Hello To All!

No matter what I read or how hard I try to visualize, my brain can't understand the flow of steam in a one-pipe radiator, nor can I lock in the reason vents are part way up on the radiator.

I've encountered steam radiators where the sections are connected across the top and bottom with push nipples and where only the bottoms are connected. That's confusion number one.

Confusion number two is the path of steam in the unit and why the vent is part way up:

I've read that steam travels up the first section, across the top and displaces the air from the last section out of the vent. To my mind, that would make the radiator heat in a diagonal at best, or only the top and last section at worst. How would the air in the other sections escape?

I've also read that the steam rushes across the bottom via the push nipples & up each section. That makes the air expelling really confusing. Would not each section need a vent at the bottom? (Or maybe even top)

If it's no trouble, could someone explain to this block-head brain of mine the path of steam in a one-pipe and the reason the vent is part way up?

Thanks For Teaching!
Paul

Comments

  • jumper
    jumper Member Posts: 2,246
    Options
    Water is most dense; then air; then steam. So steam condenses at top and condensate washes air down into water which goes down the waterspout. Sometimes vent is installed at top of radiator so that liquid drops in steam push the air right out and tweet a whistle as well. Now you have me confused.
  • leonz
    leonz Member Posts: 1,127
    edited February 2023
    Options
    To understand fully it you should wander over to www.castrads.com.. The first 2 paragraphs on the first page will explain it for you.

    The diagram they provide shows a vent halfway up one of their radiators and shows in the side view that there is a vacuum breaker on the same side in the top plug which allows the radiator to work more efficiently allowing cool air to enter and sealing the radiator when steam enters it to hold the heat in
    longer.

    Credit for the following goes to campbell-sevey inc.

    The vacuum breaker installed in a radiator helps your heating system in in four ways.

    1. improving condensate drainage flow back to the boiler
    2. reduces the possibility of water hammer
    3. minimizes temperature swings and uneven temperature
    4. minimizes steam loss
  • dabrakeman
    dabrakeman Member Posts: 552
    edited February 2023
    Options
    I am sure rate of venting has some influence on this as well. Not sure in the video in the previous discussion what the boiler sizing and radiator vent type situations were.
    PGB1
  • Chris_L
    Chris_L Member Posts: 336
    Options
    leonz said:

    To understand fully it you should wander over to www.castrads.com.. The first 2 paragraphs on the first page will explain it for you.

    The diagram they provide shows a vent halfway up one of their radiators and shows in the side view that there is a vacuum breaker on the same side in the top plug which allows the radiator to work more efficiently allowing cool air to enter and sealing the radiator when steam enters it to hold the heat in
    longer.

    Credit for the following goes to campbell-sevey inc.

    The vacuum breaker installed in a radiator helps your heating system in in four ways.

    1. improving condensate drainage flow back to the boiler
    2. reduces the possibility of water hammer
    3. minimizes temperature swings and uneven temperature
    4. minimizes steam loss

    A vacuum breaker in a one-pipe steam radiator in addition to the vent? Seriously, how many people have that? And why wouldn't a well-working vent accomplish the same thing?
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,922
    Options
    Patrick Linhartds Color book will open anyone's eyes to whats going on. Get a copy. Mad Dog
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,834
    edited March 2023
    Options
    @PGB1 I am going to take a stab at the explanation to understand the answer to this query
    I've read that steam travels up the first section, across the top and displaces the air from the last section out of the vent. To my mind, that would make the radiator heat in a diagonal at best, or only the top and last section at worst. How would the air in the other sections escape?

    I like to think of the radiator as a bucket of air. When you fill the radiator with water, the air gets pushed out. if both the top and the bottom of the sections are push-nippled together then it does not matter how the water gets in there. Water will flow from one section to the other section thru the bottom nipples and the air will flow thru the top nipples until the water completely fills the radiator. Once all the air is out, you can close the vent. There may be some very small pockets of air at the top of each radiator above the height of the push nipple but that is miniscule compared to the amount of water. You can see that in your mind's eye right?

    Now think about what would happen if there were only top nipples on that hot water radiator. As the water entered the left (or right) section and filled that section, the air would leave that section by way of the top of the section. Water going in and air leaving at the same time as that section filled with water. the air would get pushed out by the weight of the heavier water. Once that first section is full of water, the additional water will fill the next section, heavier water will push the air from the second section. This happens over and over again in each section until the radiator is filled with water. Eventually the radiator will be filled with water and the last section will be filled with water as high as the vent opening will allow air to leave the radiator. You can picture that now, right? So there will be a small amount of air left in the last section and that will float to the top after the water stops pushing the air out and water flow stops


    That is how steam works in any container. Just upside down. Since the steam is lighter it will go to the top and the air will find its way out the bottom of the radiator that has bottom only connections. The steam will then pour over to the next section displacing the heavier air to the vent at the end section. It will then pour over to the next then the next until the radiator is full of steam and the steam reaches the vent to close off the air vent. After the steam flow stops all the air finds its way to the bottom of the radiator. During this settling of the air to the bottom, the air has brushed up against the hot steam and hot cast iron, and that air is now very hot. Think of steam as upside down slow motion hot water because it is a fluid just like any other liquid or gas, the heavier stuff will move to the bottom and the lighter stuff will move to the top and once the pressure is equalized it will find its own level.


    As the steam looses its latent heat, the steam condenses into water. The water is heavier than both the steam and the air so it finds its way to toe bottom. It also takes up 1700 times less space in the radiator. This leaves more room for fresh steam to enter the radiator. And as long as there is pressure in the boiler that steam is moving into the radiator to replace the condensed steam that is leaving by becoming water, and that water is leaving the radiator, just like the air left the example top only connection radiator above.
    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics
    PGB1
  • Waher
    Waher Member Posts: 251
    Options
    Chris_L said:

    in a one-pipe steam radiator in addition to the vent? Seriously, how many people have that? And why wouldn't a well-working vent accomplish the same thing?

    Vacuum breakers are necessary on one pipe steam radiators with thermostatic valves.

    They are a nice addition on any one pipe radiator for the previously mentioned reasons while at the same time being yet another thing which would fail compared to a standard plug.

  • Jamie Hall
    Jamie Hall Member Posts: 23,283
    Options
    If it's a thermostatic valve, yes -- but that's the wrong device. It should be a thermostatic vent. There is a difference. A properly functioning vent -- thermostatic or otherwise -- will not hold a vacuum, and is not intended to.

    If the system pressure gets excessive (over 3 psi) the vent mat jam shut. If you are lucky, a sharp rap will open it. If you aren't, you just bought a new vent.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Chris_L
    Chris_L Member Posts: 336
    Options
    Waher said:

    Chris_L said:

    in a one-pipe steam radiator in addition to the vent? Seriously, how many people have that? And why wouldn't a well-working vent accomplish the same thing?

    Vacuum breakers are necessary on one pipe steam radiators with thermostatic valves.

    They are a nice addition on any one pipe radiator for the previously mentioned reasons while at the same time being yet another thing which would fail compared to a standard plug.

    the comment of @leonz wasn't limited to radiators with thermostatic valves. Look at the webpage he mentioned: https://www.castrads.com/uk/resources/how-it-works/one-pipe-steam-radiators/

    The company says its steam radiators come standard with a vacuum breaker, and it illustrates one on a standard one-pipe setup with a normal vent. (Though the text doesn't say anything about it being needed except when a thermostatic valve is used on the vent.)
  • Gordo
    Gordo Member Posts: 857
    edited March 2023
    Options
    @PGB1 :Time-lapse infrared view of a single-pipe steam radiator heating up
    https://youtube.com/shorts/rj7Y9RVyXGg
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
    PGB1
  • Waher
    Waher Member Posts: 251
    Options
    Chris_L said:


    The company says its steam radiators come standard with a vacuum breaker, and it illustrates one on a standard one-pipe setup with a normal vent. (Though the text doesn't say anything about it being needed except when a thermostatic valve is used on the vent.)

    They aren't needed for standard radiator valves installations, but are a "nice to have" "luxury" feature.
  • dabrakeman
    dabrakeman Member Posts: 552
    Options
    Gordo said:

    @PGB1 :Time-lapse infrared view of a single-pipe steam radiator heating up
    https://youtube.com/shorts/rj7Y9RVyXGg

    That is exactly how my steam only radiators fill. Monitoring mine simply by feel progression is bottom to top one section at a time. However, I have mostly two column radiators and there is a circulation in the two radiators where the steam comes in from the bottom but tends to go up one tube before the other per section. Intuitively I would have expected it to be consistent one way or the other (left tube before right tube or back before front or vice versa) but find that it is not. Seems to vary from section to section and from radiator to radiator but always one tube heats slightly before the other in the same section.
  • tocker
    tocker Member Posts: 30
    Options
    Great exchange!  Thanks!
  • PGB1
    PGB1 Member Posts: 77
    edited March 2023
    Options
    Thank You Everyone for your very helpful information, explanations & links. Finally, I think the concept has sunk in- hopefully permanently.

    The illustrations & text you wrote, Edward, are very helpful. If you're not a teacher by profession, you would make a great one.

    Gordo's video is very helpful, too. After watching both videos & studying Edward's work, if I'm visualizing correctly, were the vent installed at the top, the vent would close long before the radiator was full of steam. If it were at the bottom, it would not close because the condensate it too cold.
    Did I get it?

    The discussion of vacuum breakers reminds me of the house in which I grew up. Our steam was, what my father called, a "Zwei en Eins" (Two In One) or "Verwirrt" (Confused). Part of the house was one-pipe and part was two-pipe from a common boiler. Some radiators had vents & vacuum breakers, some had steam traps.

    When I was really young, my job was removing the vacuum breakers to clean the lime off with vinegar. I was also the steam trap cleaner-upper guy.
    I always dreaded opening the horizontal radiators in the ceiling, as I'd end up covered with rust water.

    On the plus side, during "working on the heat" days, I could play in the coal bin with impunity. (Always fun when you're a kid)

    Thank You Again everyone. People hear are very generous with their time to explain and discuss.