Optimizing a New System

Options
Hi All,
I recently had my Burnham Jublee replaced with a MegaSteam 513. When it runs, prior to the Cycle Guard (CG450-1560) cutting it off, it never builds more than ~0.25 psi. My Jublee would cycle off at just less than 1.0 psi. The MegaSteam burner is being fired at 1.0 GPH, it is rated at 1.35 GPH, should the nozzle be increased to the next larger size? Is the Cycle Guard forcing the system to shut off to frequently?

Comments

  • pecmsg
    pecmsg Member Posts: 4,847
    Options
    Why is the water level dropping?
  • Jamie Hall
    Jamie Hall Member Posts: 23,289
    Options
    Hopefully the Cyclegard is just doing its thing. You don't want to build more pressure than what you have -- sounds like the system is running pretty well.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,204
    edited January 2023
    Options
    If all the radiators are heating, you have sufficient steam pressure for distribution. Ideally, the pressuretrol should never have to shut off the burner on a properly sized boiler.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,525
    Options
    @MyNameIsMike

    Don't worry about the pressure unless you're not getting heat. The lower the pressure you run the better.
    MyNameIsMike
  • JUGHNE
    JUGHNE Member Posts: 11,061
    Options
    Does the water level actually drop or is the Cyclegard just doing it's shut down for testing?
    pecmsg
  • MyNameIsMike
    MyNameIsMike Member Posts: 6
    Options
    Hi pecmsg,
    I assume that it is boiling off. When the 15 minute cycle guard kicks in the water level slowly comes back, within the 60 shutoff time.
  • MyNameIsMike
    MyNameIsMike Member Posts: 6
    Options
    Hi Jamie Hall,
    The cycle guard is only triggering on time, not low water.
  • MyNameIsMike
    MyNameIsMike Member Posts: 6
    Options

    If all the radiators are heating, you have sufficient steam pressure for distribution. Ideally, the pressuretrol should never have to shut off the burner on a properly sized boiler.

    My radiators are getting hot.
  • MyNameIsMike
    MyNameIsMike Member Posts: 6
    Options
    JUGHNE said:

    Does the water level actually drop or is the Cyclegard just doing it's shut down for testing?

    The water level in the sight glass does drop by over an inch.