Steam pipe insulation! Wondering if this is to close to the boiler exhaust

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • matt_spear
    matt_spear Member Posts: 2
    From paper to metal exhaust is about 2 3/4 inches 
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,609
    edited December 2022
    That should be fine. The Barometric draft control should be straightened up though.
    Who ever did your last professional adjustment on the draft control did not get an accurate draft adjustment, and therefore your combustion adjustments can not be correct.

    If you did a DIY chimney inspection and put it back that way, the combustion adjustments are now way off.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • pedmec
    pedmec Member Posts: 1,220
    Code requires 6" clearance between single wall flue and combustible materials.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,609
    pedmec said:

    Code requires 6" clearance between single wall flue and combustible materials.

    Is Fiberglass insulation Combustable material?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ethicalpaul
  • pecmsg
    pecmsg Member Posts: 6,196

    Is Fiberglass insulation Combustable material?
    Fiberglass NO
    The paper YES

  • pecmsg
    pecmsg Member Posts: 6,196
    Easy solution
    Cut the insulation back 6" from the vent.