Steam pipe insulation! Wondering if this is to close to the boiler exhaust
Options
matt_spear
Member Posts: 2
0
Comments
-
From paper to metal exhaust is about 2 3/4 inches0
-
That should be fine. The Barometric draft control should be straightened up though.
Who ever did your last professional adjustment on the draft control did not get an accurate draft adjustment, and therefore your combustion adjustments can not be correct.
If you did a DIY chimney inspection and put it back that way, the combustion adjustments are now way off.Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0 -
Code requires 6" clearance between single wall flue and combustible materials.0
-
Is Fiberglass insulation Combustable material?pedmec said:Code requires 6" clearance between single wall flue and combustible materials.
Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics1 -
Fiberglass NOEdTheHeaterMan said:
Is Fiberglass insulation Combustable material?pedmec said:Code requires 6" clearance between single wall flue and combustible materials.
The paper YES
0 -
Easy solution
Cut the insulation back 6" from the vent.0
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements