Steam pipe insulation! Wondering if this is to close to the boiler exhaust
  • matt_spear
    matt_spear Member Posts: 2
    From paper to metal exhaust is about 2 3/4 inches
    EdTheHeaterMan Member Posts: 11,539
    edited December 2022
    That should be fine. The Barometric draft control should be straightened up though.
    Who ever did your last professional adjustment on the draft control did not get an accurate draft adjustment, and therefore your combustion adjustments can not be correct.
    If you did a DIY chimney inspection and put it back that way, the combustion adjustments are now way off.
  • pedmec
    pedmec Member Posts: 1,238
    Code requires 6" clearance between single wall flue and combustible materials.
    Is Fiberglass insulation Combustable material?
    pecmsg Member Posts: 6,750
    Fiberglass NO
    The paper YES
    Easy solution
    Cut the insulation back 6" from the vent.