Drop Header Steam build (I wanna do it properly)
2»
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,827
    It will work.
    Subdural
    mattmia2 Member Posts: 16,379
    Subdural said:
    @KC_Jones anything i can do with this situation? larger near boiler pipes? Or is it close enough with proper near boiler pipes that it would work?
    vaporstat
  • Subdural
    Subdural Member Posts: 35
    @mattmia2 the unit has an attached honeywell PA404A/B Pressuretrol controller - yet seems like a different language being spoken in how that is to be configured...
    The right model vaporstat can be set to control the pressure to keep it under 1 psig or even 1/2 psig.
    Subdural
    ethicalpaul Member Posts: 8,607
    You'll get an idea of how it is working regarding the sizing issue…if you find it is cycling a lot during a call for heat, ensure your main venting is good, and minimize any setback (I'd say no more than 3 degrees). Steam works better with minimal setback anyway.
    STEAM DOCTOR
  • ChrisJ
    ChrisJ Member Posts: 17,271
    Paul,
    While I admit I cheat in several ways, my steam system has no issues with a 10 degree setback.
    I'd tend to say as far as efficiency, it probably does better with a large setback than maintaining temperature. But I leave it on 1 temperature because we're all awake / home at different times.