Lineset in new construction
        
            Options        
            
        
 
            
                
                    bdbsenji                
                
                    Member Posts: 1                
            
                        
            
                    I am in the planning phase of new construction for a basement walk out home that is on a significant slope.  I will be using multiple mini splits and would like to place them next to a wall at the lowest point of the property.  This wall will essentially be a concrete wall (foundation). How should I approach  getting the linesets through the wall.  Have the linesets “set” before the foundation pour or drill holes through the foundation at a later time?  I really don’t want to have them run vertically on the outside of the foundation.                
                0                
            Comments
- 
            Install PVC sleeves in the forms before the concrete is poured. You’ll need at least a three inch diameter sleeve for each line set. You can probably get two line sets through a four inch sleeve depending upon the size of the tubing of the line set.Bob Boan
 You can choose to do what you want, but you cannot choose the consequences.2
- 
            If it's being poured, nothing beats the convenience of a sleeve already in the wall when you're ready to pull in the linesets. The next most convenient thing is to hire someone else to drill them.Once I actually bought a **** wet drill & 4½" core bit for a one-off job. Total cost was under $300, and I have the drill for home use now, too! 0
- 
            How long until the spam link gets added?0
- 
            ratio said:How long until the spam link gets added?  https://www.youtube.com/watch?v=wlx94yQ_3hA https://www.youtube.com/watch?v=wlx94yQ_3hA
 C'mon... I should at least get an LOL from @ratio
 Edward Young Retired After you make that expensive repair and you still have the same problem, What will you check next? 2
- 
            I tugged mini lines through a 2" PVC conduit once (tight). We had long radius ells at the ends. Needed some 2x4 leverage to do it (got super tight at the end) but it worked. Next time it will be 3" PVC0
- 
            Use talc to lube the Armaflex™. I learned that from the beer guy, watching him pull in the lines to the taps.0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements