gas valve
heatandair
heatandair Member Posts: 5
I had a call today for no heat The gas valve on a Goodman Furnace that was installed backwards it ran for almost a year. I reversed the valve and everthing is fine. My question is why did it run when it was backwards.
  • heatandair
    I don't do a lot of gas
  • Tim McElwain
    Tim McElwain Member Posts: 4,658
    What was the Make and model of the valve?
    pecmsg Member Posts: 6,895
    In backwards from the factory?
    EdTheHeaterMan Member Posts: 11,762
    edited November 2022
    If the pressure regulator section of the valve was not causing a problem, the solenoid portion would still open and close. I guess the regulator finally engaged and caused the flow restriction.
    I had a Firo-matic valve cause me hours of aggravation on a new oil burner installation. Went well into the night with operation for one cycle then no operation on the next. I blew out the fuel line and even changed out the fuel line with new copper tubing. Finally I reversed the Firo-matic and everything worked. Why did the oil flow on some cycles and not flow on other cycles? It was not a check valve but there must be a reason there is an arrow on that valve.
    Of course, I instaled the valve, so it had to be installed in the proper direction. NOT!
    pecmsg
  • HomerJSmith
    HomerJSmith Member Posts: 2,745
    Misteaks, happen!
  • Tim McElwain
    Was it a single seated valve OR A REDUNDANT VALVE?