Furnace won’t start when powered by generator.
Jeanf
Jeanf Member Posts: 1
edited October 2022 in Gas Heating
I have a York Propane furnace. Runs perfectly when powered by the grid. Will not start when powered by generator. I adjusted the generator to 120V 60HZ to no better result. Generator oscillates between 59.9 to 60.1. Is that enough to cause the problem?
  • WMno57
    WMno57 Member Posts: 1,408
    I think your Hz is fine. I think the problem is your igniter requires a different type of neutral - ground bonding than your generator is currently set up for. Not hard to change, but lets think this through.
    Are you currently without heat? I remember a thread from a couple years ago describing this issue. I will find it.
    How do you have your furnace and generator connected?
    STEVEusaPA
    109A_5 Member Posts: 3,444
    edited October 2022
    Hello @Jean,
    If the possible neutral - ground bonding issue does not help remedy your problem maybe read this post.
    https://forum.heatinghelp.com/discussion/comment/1172856#Comment_1172856
    WMno57
    pecmsg Member Posts: 6,770
    How is this generator connected to the furnace?
    mattmia2 Member Posts: 15,591
    Where in the cycle does it fail?
    Jamie Hall Member Posts: 26,835
    Excellent reference, @WMno57 -- thank you. And, in passing I might add that it presents one of the best (if subtle) arguments for connecting your "portable" generator through a transfer switch and your main box, or a lockout system on your main circuit board if you are going cheap, rather than the common "just put the boiler power feed on a plug and plug it into the generator" back lot approach.
    PC7060
  • HomerJSmith
    HomerJSmith Member Posts: 2,710
    edited October 2022
    Sometimes a problem can occur because the generator has a high THD (total harmonic distortion) of the 60 hz sine wave. The THD of the utility is around 2% and a generator can be as high at 12%. Timing circuits that rely upon the HZ can be affected. You may need a line conditioner.