Furnace won’t start when powered by generator.
Jeanf
Member Posts: 1
I have a York Propane furnace. Runs perfectly when powered by the grid. Will not start when powered by generator. I adjusted the generator to 120V 60HZ to no better result. Generator oscillates between 59.9 to 60.1. Is that enough to cause the problem?
0
Comments
-
I think your Hz is fine. I think the problem is your igniter requires a different type of neutral - ground bonding than your generator is currently set up for. Not hard to change, but lets think this through.
Are you currently without heat? I remember a thread from a couple years ago describing this issue. I will find it.
How do you have your furnace and generator connected?
1 -
-
Hello @Jean,
If the possible neutral - ground bonding issue does not help remedy your problem maybe read this post.
https://forum.heatinghelp.com/discussion/comment/1172856#Comment_1172856
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
How is this generator connected to the furnace?Jeanf said:I have a York Propane furnace. Runs perfectly when powered by the grid. Will not start when powered by generator. I adjusted the generator to 120V 60HZ to no better result. Generator oscillates between 59.9 to 60.1. Is that enough to cause the problem?
0 -
Where in the cycle does it fail?0
-
Excellent reference, @WMno57 -- thank you. And, in passing I might add that it presents one of the best (if subtle) arguments for connecting your "portable" generator through a transfer switch and your main box, or a lockout system on your main circuit board if you are going cheap, rather than the common "just put the boiler power feed on a plug and plug it into the generator" back lot approach.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Sometimes a problem can occur because the generator has a high THD (total harmonic distortion) of the 60 hz sine wave. The THD of the utility is around 2% and a generator can be as high at 12%. Timing circuits that rely upon the HZ can be affected. You may need a line conditioner.0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements