Is there a more accurate Pressuretrol?
Bodycount
Bodycount Member Posts: 43
edited September 2022 in Strictly Steam
I have this style / model Honeywell Pressuretrol.
If I engage the adjustment screw approximately 1 turn or less so it doesn’t pull out, the pressure will reach 4.5 psi.
If I disengage the screw so it’s at its lowest setting (basically deactivated) it will reach 1.5 psi.
The diff is at 1.
I’d like to replace the unit with a more accurate unit so I can keep it at 0.5-1 psi.
Thanks in advance.
Tom.
    mattmia2 Member Posts: 16,637
    Vaporstat. Put it in series with the pressuretrol so the pressuretrol acts as a backup.
    Bodycount
    109A_5 Member Posts: 3,950
    Hello @Bodycount,
    As @mattmia2 stated a Vaporstat 16 Oz and less, is probably the most common addition. If you are tripping out with pressure you may want to add a delay timer too. Also Dwyer makes a variety of low pressure switching devices.
    I played with my Pressuretrol a bit since I read some folks just removed the spring, but that may have created erratic cycling, so I did this, an easy modification. Come to find out, in my case the EDR is greater than the boiler rating so my system never makes pressure more than a few inches of water column. So my Pressuretrol is just a safety device.
    BodycountEdTheHeaterMan
    ethicalpaul Member Posts: 8,716
    As it ideally should be!