Is there a more accurate Pressuretrol?
Bodycount
Member Posts: 43
I have this style / model Honeywell Pressuretrol.
If I engage the adjustment screw approximately 1 turn or less so it doesn’t pull out, the pressure will reach 4.5 psi.
If I disengage the screw so it’s at its lowest setting (basically deactivated) it will reach 1.5 psi.
The diff is at 1.
I’d like to replace the unit with a more accurate unit so I can keep it at 0.5-1 psi.
Thanks in advance.
Tom.
0
Comments
-
-
Hello @Bodycount,
As @mattmia2 stated a Vaporstat 16 Oz and less, is probably the most common addition. If you are tripping out with pressure you may want to add a delay timer too. Also Dwyer makes a variety of low pressure switching devices.
I played with my Pressuretrol a bit since I read some folks just removed the spring, but that may have created erratic cycling, so I did this, an easy modification. Come to find out, in my case the EDR is greater than the boiler rating so my system never makes pressure more than a few inches of water column. So my Pressuretrol is just a safety device.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System2 -
As it ideally should be!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements