Is there a more accurate Pressuretrol?

Bodycount
Member Posts: 39

I have this style / model Honeywell Pressuretrol.
If I engage the adjustment screw approximately 1 turn or less so it doesn’t pull out, the pressure will reach 4.5 psi.
If I disengage the screw so it’s at its lowest setting (basically deactivated) it will reach 1.5 psi.
The diff is at 1.
I’d like to replace the unit with a more accurate unit so I can keep it at 0.5-1 psi.
Thanks in advance.
Tom.
0
Comments
-
-
Hello @Bodycount,
As @mattmia2 stated a Vaporstat 16 Oz and less, is probably the most common addition. If you are tripping out with pressure you may want to add a delay timer too. Also Dwyer makes a variety of low pressure switching devices.
I played with my Pressuretrol a bit since I read some folks just removed the spring, but that may have created erratic cycling, so I did this, an easy modification. Come to find out, in my case the EDR is greater than the boiler rating so my system never makes pressure more than a few inches of water column. So my Pressuretrol is just a safety device.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System2 -
Categories
- All Categories
- 84.3K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 44 Chimneys & Flues
- 1.8K Domestic Hot Water
- 4.8K Gas Heating
- 120 Geothermal
- 156 Indoor-Air Quality
- 3K Oil Heating
- 57 Pipe Deterioration
- 794 Plumbing
- 5.4K Radiant Heating
- 370 Solar
- 14.1K Strictly Steam
- 3.1K Thermostats and Controls
- 54 Water Quality
- 39 Industry Classes
- 80 Job Opportunities
- 22 Recall Announcements