Is the damper supposed to be there?
andresloaiza
Member Posts: 3
in Oil Heating
If you mean the barometric draft regulator (swinging disc), yes.All Steamed Up, Inc.
Consulting1 -
I haven’t seen any other boiler with it so close. Right out of the combustion chamber0
Do you have other pictures? I’m curious what the piping looks like.andresloaiza said:
Agree it should be moved to the horizontal run. There's no way a combustion test is getting done without picking up free air from the regulator.
In the current location, the barometric draft regulator will work fine. However I also see a problem with getting proper combustion test results. It's easy enough to move it to the horizontal section of the vent connector
We have a few like that- if you tip your analyzer probe down so it's below the barometric, you'll get good readings.
The only drawback I see is that on some boilers, more noise will escape if the barometric is that close.All Steamed Up, Inc.
Consulting1 -
i would worry more about that near boiler piping than that damper location. bullhead tee on the equalizer and undersize. doesn't look like 1-1/2 as required by manufacturer unless pic is deceiving0
- 117 Geothermal