Is the damper supposed to be there?

Options
andresloaiza
andresloaiza Member Posts: 3

Comments

  • Steamhead
    Steamhead Member Posts: 16,844
    Options
    If you mean the barometric draft regulator (swinging disc), yes.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    andresloaiza
  • andresloaiza
    andresloaiza Member Posts: 3
    Options
    I haven’t seen any other boiler with it so close. Right out of the combustion chamber 
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Options
    It would be better on the horizontal piece of flue pipe.

    There was an error rendering this rich post.

    HVACNUTkcopp
  • pecmsg
    pecmsg Member Posts: 4,861
    Options

    Do you have other pictures? I’m curious what the piping looks like. 
  • HVACNUT
    HVACNUT Member Posts: 5,841
    Options
    Agree it should be moved to the horizontal run. There's no way a combustion test is getting done without picking up free air from the regulator. 

  • andresloaiza
    andresloaiza Member Posts: 3
    Options

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,852
    edited May 2022
    Options
    In the current location, the barometric draft regulator will work fine. However I also see a problem with getting proper combustion test results. It's easy enough to move it to the horizontal section of the vent connector

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Steamhead
    Steamhead Member Posts: 16,844
    Options
    We have a few like that- if you tip your analyzer probe down so it's below the barometric, you'll get good readings.

    The only drawback I see is that on some boilers, more noise will escape if the barometric is that close.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    EdTheHeaterMan
  • pedmec
    pedmec Member Posts: 976
    Options
    i would worry more about that near boiler piping than that damper location. bullhead tee on the equalizer and undersize. doesn't look like 1-1/2 as required by manufacturer unless pic is deceiving