pex expansion when heated
mikedo
Member Posts: 297
does heat pex expand like copper when heated. I'm worried about noise when used in a baseboard system if the pex is strapped tightly
Pex expands 1.1" per 100 feet per 10 degree rise
Copper expands .125" per 100 feet per 10 degree rise
Almost 9 times as much. FostaPex was some awesome stuff, but has been discontinued. There are other brands of pex-al-pex (a layer of aluminum sandwiched between 2 layers of plastic) which would serve a very similar purpose in reducing thermal expansion.
PAP expands .3" per 100 feet per 10 degree rise2 -
thanks0
What happens inside a slab, with all those little sharpish edges against the pex ?
Currently in building maintenance.0 -
Nothing. The pex encased in concrete doesn't move. However, it needs to be sleeved as it exits or enters the slab for the reason you're thinking ofDave Carpentier said:What happens inside a slab, with all those little sharpish edges against the pex ?You can have it good, fast or cheap. Pick two0 -
Hmm, I'll have to check if we used sleeves. There's metal guide things that turned the pipes up 90deg. Im not sure if they went all the way around the pipes though.
If the PEX is totally restrained in the slab it will squish. It won't like it, but it will. Unlike copper, the forces aren't great enough to crack the slab.Br. Jamie, osb
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam