pex expansion when heated
mikedo
mikedo Member Posts: 302
does heat pex expand like copper when heated. I'm worried about noise when used in a baseboard system if the pex is strapped tightly
  • kcopp
    kcopp Member Posts: 4,710
    Yes it does. In fact about 4 times as much. There is a product the Viega makes "Fostapex" that has a lower expansion rate.
    STEVEusaPAmattmia2Intplm.
  • GroundUp
    GroundUp Member Posts: 2,536
    Pex expands 1.1" per 100 feet per 10 degree rise
    Copper expands .125" per 100 feet per 10 degree rise
    Almost 9 times as much. FostaPex was some awesome stuff, but has been discontinued. There are other brands of pex-al-pex (a layer of aluminum sandwiched between 2 layers of plastic) which would serve a very similar purpose in reducing thermal expansion.
    PAP expands .3" per 100 feet per 10 degree rise
    CLambZman
    Jamie Hall Member Posts: 27,616
    As noted, it will expand. If you don't allow for the expansion --bends, joints, it will give you much grief.
  • mikedo
    thanks
  • Dave Carpentier
    Dave Carpentier Member Posts: 640
    What happens inside a slab, with all those little sharpish edges against the pex ?
  • Canucker
    Canucker Member Posts: 723
    Nothing. The pex encased in concrete doesn't move. However, it needs to be sleeved as it exits or enters the slab for the reason you're thinking of
    You can have it good, fast or cheap. Pick two
  • Dave Carpentier
    Hmm, I'll have to check if we used sleeves. There's metal guide things that turned the pipes up 90deg. Im not sure if they went all the way around the pipes though.
    If the PEX is totally restrained in the slab it will squish. It won't like it, but it will. Unlike copper, the forces aren't great enough to crack the slab.